    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    Modbus Publisher

    User help
    2
    2
    1.5k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • J
      josefran
      last edited by

      Hi,

      Has anyone used Modbus Publisher?
      I created two Modbus Publisher with the same port and different slaves:

      upload-6bf02e2c-af15-483b-ac62-93f361e63f94

      But I have only communication with one of the slaves:

      upload-086288f3-5844-4a81-9a23-facb5e49fd8a

      Why does this happen?

      1 Reply Last reply Reply Quote 0
      • JoelHaggarJ
        JoelHaggar
        last edited by

        I just did a little test on this and it looks like you can only have one slaveID per port. There may also be a bug that prevents ports other than 502 being used. We'll look into that a bit more and get back to you.

        1 Reply Last reply Reply Quote 0