Thanks Jared, you guys are awesome!
Great response time, much appreciated.
Thanks Jared, you guys are awesome!
Great response time, much appreciated.
So it's a standard Modbus response:
05 ACKNOWLEDGE
The slave has accepted the request
and is processing it, but a long duration
of time will be required to do so. This
response is returned to prevent a
timeout error from occurring in the
master. The master can next issue a
Poll Program Complete message to
determine if processing is completed
Hi,
I have a Modbus RTU Data source, and are getting the following error from most of the 5 Slaves on the BUS, but only from register 0:
Urgent 'Modbus RS485': Cool Room Temperature — Modbus RS485: Acknowledge
The slaves only have two registers being polled, 0 and 1.
Update period: 30 seconds
Timeout: 1000ms
Contiguous batches only
The event lasts only 0 millseconds
Has anyone seen this before?
Hayden
@joeamiraglia Thanks Joe. I am used to V3, which pulled its default values from the env.properties file. V5 must have it's default values embedded somewhere else then.
Hi,
This has to be a silly question, but every line in my V5 mango.properties file appears to be commented out:
# The port at which Mango Automation will listen for browser connections
#web.port=8080
# The host interface to which Mango Automation will bind and listen for new connections
# 0.0.0.0 is the special interface that will force a bind to all available interfaces
#web.host=0.0.0.0
Whereas the "Clean" mango.properties file in the Mango Docs doesn't even have hashtags for comments:
The port at which Mango Automation will listen for browser connections
web.port=8080
The host interface to which Mango Automation will bind and listen for new connections
0.0.0.0 is the special interface that will force a bind to all available interfaces
web.host=0.0.0.0
Can I assume that it is ignoring the hashtags?
If you save the event detector before setting the reset limit, it lets you then set the reset limit.
Hi,
5.1.2
When creating a high limit event detector, when setting the Reset duration, the widget goes back to event detector. Then when I try again, is gets all messed up, half showing, unusable.
Chrome and Firefox.
Hayden
@terrypacker Thanks, I will set them up using meta points as you suggest.
@MattFox Hi Matt, the application is a cold room used as a grow room.
The room has set-points for alarms and also automation to turn off grow lights, when the temp gets to high.
But we need to disable all the alarms and automation when they have the doors open for loading/unloading, using an easy method.
I might try to setup the Event Handlers using external context points (maybe a virtual binary point,or physical switch) and scripts, if disabling the event handlers by a user is not possible.
...or just create another user with superadmin privileges.
Thanks anyway for looking at it...
Hi,
I can't see how to give users permissions to Enable/disable event handlers, that have been created by admin.
I gave access to the Event Handlers menu item, which is there, but I can't see any options in the actual individual event handlers, which are not visible.
Does anyone know?
(V3)