    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website
    R
    • Profile
    • Following 0
    • Followers 0
    • Topics 6
    • Posts 15
    • Best 4
    • Controversial 0
    • Groups 0

    rob987

    @rob987

    4
    Reputation
    609
    Profile views
    15
    Posts
    0
    Followers
    0
    Following
    Joined Last Online
    Location Australia

    rob987 Unfollow Follow

    Best posts made by rob987

    • Modbus TCP no recipient found for response

      Hi,

      I am using Mango 3.5.6 modbus tcp to poll a solaredge inverter, and I have bursts of "No recipient" errors. For example on the 26th march, there were 240 errors, over 9 bursts. The times seem to be random, with minutes or hours between errors.

      When I first added the inverter I set the poll time to 1 second and the errors were in the thousands, but I have reduced it to the hundreds by extending the poll time to 2 seconds, and the timeout to 1500mS. This seems a long time for an TCP modbus request timeout.

      2019/03/22-21:06:35,347 1553252795347 data source started
      2019/03/22-21:06:35,389 O 000100000006010300530002
      2019/03/22-21:06:36,390 O 000100000006010300530002
      2019/03/22-21:06:36,473 I 00010000000701030400000000
      2019/03/22-21:06:36,473 O 0002000000060103005d0003
      2019/03/22-21:06:36,553 I 00010000000701030400000000
      2019/03/22-21:06:37,342 I 00020000000901030600697e020000
      2019/03/22-21:06:37,342 O 000300000006010300ce0001
      2019/03/22-21:06:37,423 I 000300000005010302fd9b
      2019/03/22-21:06:37,423 O 000400000006010300d20001
      2019/03/22-21:06:37,685 I 0004000000050103020000
      2019/03/22-21:06:37,685 O 000500000006010300e20002
      2019/03/22-21:06:38,129 I 0005000000070103040040b993
      2019/03/22-21:06:38,129 O 000600000006010300ea0002
      2019/03/22-21:06:38,996 I 0006000000070103040043a19f
      2019/03/22-21:06:38,997 O 000700000006010300f20001
      2019/03/22-21:06:39,400 I 0007000000050103020000
      2019/03/22-21:06:41,388 O 000800000006010300530002
      2019/03/22-21:06:42,003 I 00080000000701030400000000
      2019/03/22-21:06:42,004 O 0009000000060103005d0003
      2019/03/22-21:06:42,084 I 00090000000901030600697e020000
      2019/03/22-21:06:42,085 O 000a00000006010300ce0001
      2019/03/22-21:06:42,629 I 000a00000005010302fd9a
      2019/03/22-21:06:42,629 O 000b00000006010300d20001
      2019/03/22-21:06:43,356 I 000b000000050103020000
      2019/03/22-21:06:43,356 O 000c00000006010300e20002
      2019/03/22-21:06:44,356 O 000c00000006010300e20002
      2019/03/22-21:06:44,526 I 000c000000070103040040b993
      2019/03/22-21:06:44,526 O 000d00000006010300ea0002
      2019/03/22-21:06:44,607 I 000c000000070103040040b993
      2019/03/22-21:06:44,709 I 000d000000070103040043a1a0
      2019/03/22-21:06:44,709 O 000e00000006010300f20001
      2019/03/22-21:06:44,810 I 000e000000050103020000
      2019/03/22-21:06:45,387 O 000f00000006010300530002
      2019/03/22-21:06:46,364 I 000f0000000701030400000000
      2019/03/22-21:06:46,364 O 0010000000060103005d0003
      2019/03/22-21:06:46,445 I 00100000000901030600697e020000
      2019/03/22-21:06:46,445 O 001100000006010300ce0001
      2019/03/22-21:06:47,312 I 001100000005010302fd97
      2019/03/22-21:06:47,313 O 001200000006010300d20001
      2019/03/22-21:06:47,413 I 0012000000050103020000
      2019/03/22-21:06:47,414 O 001300000006010300e20002
      2019/03/22-21:06:48,261 I 0013000000070103040040b993
      2019/03/22-21:06:48,261 O 001400000006010300ea0002
      2019/03/22-21:06:49,262 O 001400000006010300ea0002
      2019/03/22-21:06:49,351 I 0014000000070103040043a1a1
      2019/03/22-21:06:49,351 O 001500000006010300f20001
      2019/03/22-21:06:50,352 O 001500000006010300f20001
      2019/03/22-21:06:50,945 I 0014000000070103040043a1a1
      2019/03/22-21:06:51,048 I 0015000000050103020000
      
      

      I logged the IO when I first added the inverter, and noticed there are two I or O lines together.

      The time between the errors appears to be random

      26/3/2019	 5:47:48 AM	'SE5K': com.serotonin.modbus4j.exception.ModbusTransportException: java.net.SocketTimeoutException: connect timed out 
      26/3/2019	 9:39:24 AM	'SE5K': Exception from modbus master: No recipient was found waiting for response for key com.serotonin.modbus4j.ip.xa.XaWaitingRoomKeyFactory$XaWaitingRoomKey@93a5 
      26/3/2019	 9:39:26 AM	'SE5K': Exception from modbus master: No recipient was found waiting for response for key com.serotonin.modbus4j.ip.xa.XaWaitingRoomKeyFactory$XaWaitingRoomKey@93a6 
      26/3/2019	 10:09:57 AM	'SE5K': Exception from modbus master: No recipient was found waiting for response for key com.serotonin.modbus4j.ip.xa.XaWaitingRoomKeyFactory$XaWaitingRoomKey@ac78 
      26/3/2019	 10:10:02 AM	'SE5K': Exception from modbus master: No recipient was found waiting for response for key com.serotonin.modbus4j.ip.xa.XaWaitingRoomKeyFactory$XaWaitingRoomKey@ac7d 
      26/3/2019	 10:10:15 AM	'SE5K': Exception from modbus master: No recipient was found waiting for response for key com.serotonin.modbus4j.ip.xa.XaWaitingRoomKeyFactory$XaWaitingRoomKey@ac84 
      26/3/2019	 10:10:21 AM	'SE5K': Exception from modbus master: No recipient was found waiting for response for key com.serotonin.modbus4j.ip.xa.XaWaitingRoomKeyFactory$XaWaitingRoomKey@ac8c 
      26/3/2019	 10:10:28 AM	'SE5K': Exception from modbus master: No recipient was found waiting for response for key com.serotonin.modbus4j.ip.xa.XaWaitingRoomKeyFactory$XaWaitingRoomKey@ac92 
      26/3/2019	 10:10:34 AM	'SE5K': Exception from modbus master: No recipient was found waiting for response for key com.serotonin.modbus4j.ip.xa.XaWaitingRoomKeyFactory$XaWaitingRoomKey@ac96 
      26/3/2019	 10:10:53 AM	'SE5K': Exception from modbus master: No recipient was found waiting for response for key com.serotonin.modbus4j.ip.xa.XaWaitingRoomKeyFactory$XaWaitingRoomKey@aca1 
      26/3/2019	 10:11:01 AM	'SE5K': Exception from modbus master: No recipient was found waiting for response for key com.serotonin.modbus4j.ip.xa.XaWaitingRoomKeyFactory$XaWaitingRoomKey@aca8 
      
      

      Mango is also polling an Automation Direct Click PLC via modbus, and has never reported any errors.
      From the system status page

      SE5K previous sequential successful polls 	1
      SE5K last poll duration 			                        531
      SE5K poll success percentage 			        99.24194567277321
      ClickPLC previous sequential successful polls 	-1
      ClickPLC last poll duration 			               63
      ClickPLC poll success percentage 		      100
      
      

      I take it the poll duration is milliseconds? Mango can ping the inverter in 0.6mS

      robert@mango:/opt/mango/logs$ ping se5k
      PING SE5K.nixtec.net (10.11.21.253) 56(84) bytes of data.
      64 bytes from SE5K.nixtec.net (10.11.21.253): icmp_seq=1 ttl=62 time=0.672 ms
      64 bytes from SE5K.nixtec.net (10.11.21.253): icmp_seq=2 ttl=62 time=0.640 ms
      64 bytes from SE5K.nixtec.net (10.11.21.253): icmp_seq=3 ttl=62 time=0.628 ms
      
      

      Only 9 points are being polled in the inverter, (summary from device export)

      HOLDING_REGISTER	TWO_BYTE_INT_SIGNED	1	84
      HOLDING_REGISTER	TWO_BYTE_INT_UNSIGNED	1	83
      HOLDING_REGISTER	TWO_BYTE_INT_SIGNED	1	206
      HOLDING_REGISTER	TWO_BYTE_INT_SIGNED	1	210
      HOLDING_REGISTER	FOUR_BYTE_INT_UNSIGNED	1	226
      HOLDING_REGISTER	FOUR_BYTE_INT_UNSIGNED	1	234
      HOLDING_REGISTER	TWO_BYTE_INT_SIGNED	1	242
      HOLDING_REGISTER	FOUR_BYTE_INT_UNSIGNED	1	93
      HOLDING_REGISTER	TWO_BYTE_INT_UNSIGNED	1	95
      
      

      So my question is, is the problem / fault with Mango, or the Solaredge inverter?

      Thanks

      posted in Mango Automation general Discussion
      R
      rob987
    • RE: MQTT datapoint parsing help.

      Hi,
      Tried the date format yyyy-MM-dd'T'HH:mm:ss.SSS and the error changed to

      Error during read topic: "tele/tasmota_E14FF4/SENSOR" datapoint: "MQTT_NAS - Mealies_Temperature" payload: "{"Time":"2021-01-13T13:26:48","DS18B20":{"Id":"01192718DE3D","Temperature":28.1},"TempUnit":"C"}" exception: "Text '2021-01-13T13:26:48' could not be parsed at index 19"
      

      I have the Sensor temperature, and WiFi signal strength working now. ( Just using JSON, and not JSON + Timestamp, as I cannot find a parsing string that works )

      Mango is subscribed to two topics, STATE and SENSOR.

      The steps I took were

      1. Connect to MQTT Broker and get a copy of the raw data ( Also checks connection from Mango PC )
      robert@mango:~$ mosquitto_sub  -h 192.168.220.208 -p 1883 -u robert -P XXXXX -t tele/#
      
      Client mosqsub/22329-mango received PUBLISH (d0, q0, r0, m0, 'tele/tasmota_E14FF4/STATE', ... (274 bytes))
      tele/tasmota_E14FF4/STATE {"Time":"2021-01-13T10:46:48","Uptime":"4T17:22:27","UptimeSec":408147,"Heap":25,"SleepMode":"Dynamic","Sleep":50,"LoadAvg":19,"MqttCount":3,"Wifi":{"AP":1,"SSId":"NixNet","BSSId":"E4:8D:8C:3F:D7:A1","Channel":1,"RSSI":92,"Signal":-54,"LinkCount":1,"Downtime":"0T00:00:03"}}
      Client mosqsub/22329-mango received PUBLISH (d0, q0, r0, m0, 'tele/tasmota_E14FF4/SENSOR', ... (96 bytes))
      tele/tasmota_E14FF4/SENSOR {"Time":"2021-01-13T10:46:48","DS18B20":{"Id":"01192718DE3D","Temperature":26.6},"TempUnit":"C"}
      

      Check the Subscribed Data at https://jsonformatter.org/json-parser You can paste the received data string in, and get a readable JSON document.

      tele/tasmota_E14FF4/STATE

      object{9}
      	Time : 2021-01-13T10:46:48
      	Uptime : 4T17:22:27
      	UptimeSec : 408147
      	Heap : 25
      	SleepMode : Dynamic
      	Sleep : 50
      	LoadAvg : 19
      	MqttCount : 3
      	Wifi {8}
      		AP : 1
      		SSId : NixNet
      		BSSId : E4:8D:8C:3F:D7:A1
      		Channel : 1
      		RSSI : 92
      		Signal : -54
      		LinkCount : 1
      		Downtime : 0T00:00:03
      

      And
      tele/tasmota_E14FF4/SENSOR

      object {3}
          Time : 2021-01-13T10:46:48
          DS18B20 {2}
              Id : 01192718DE3D
              Temperature : 26.6
          TempUnit : C
      

      Here are the working MQTT Datapoint setups
      Wifi_Signal.png

      And Temperature
      Temperature_MQTT.png

      And The correct values shown on the datasource page
      DataSource_MQTT.png

      If anyone has some ideas on how to parse the Time (JSON + Timestamp) let me know

      Thanks

      posted in User help
      R
      rob987
    • RE: Modbus TCP no recipient found for response

      Hi,
      Thanks for all the input. 247 errors yesterday (27/03/2019) on a cloudy rainy day, so the inverter does not rest :-),
      and devote more time to comms.

      The inverter is on a wired ethernet connection, with mango and the inverter on the wired LAN.

      I had "Contiguous batches only" ticked, as the inverter would not answer back when I first added it. I have now ticked it and reduced the max read registers to 50. The This is giving me 2 requests.

      2019/03/28-08:33:28,568 O 00230000000601030053000d
      2019/03/28-08:33:28,833 I 00230000001d01031a22e2ffff1384fffe2494ffff91d8fffedac6fffe006aeaf70000
      2019/03/28-08:33:28,834 O 002400000006010300ce0025
      2019/03/28-08:33:28,914 I 00240000004d01034a033b012300f7011f00000388012c011d01440000fe93ffb7ff73ff6a0000de17db9ee036de71fffe004162a600191f070015cec0001e39760044aaeb002c0006001e72c40005fcb80000
      
      

      What is the ,nnn after the date-time in the above log (2019/03/28-08:33:28,568). Is it mS timestamp of Java sending and receiving?

      Is there any way to have a poll period associated with a point.? The 2nd longer read is for kWh values, and could be read every 15 minutes. This might allow the instant power values to be read more frequently.

      I am using mango to read, and publish the values to a Click PLC, as I cannot get the Click to talk to the inverter. I used wireshark on the line, and I see the PLC send 3 SYN requests, and the inverter does not reply. I suspect it may be "to fast" for the inverter.

      No errors for 30 minutes, so maybe solved, but not fixed !!!!!!
      Thanks

      posted in Mango Automation general Discussion
      R
      rob987
    • RE: Modbus TCP no recipient found for response

      Hi,
      Just reporting that no errors in the last 24 hours,
      I have the TCP with keepalive set, Comms was very unreliable with a new connection for each request.
      Now the forest of errors has disappeared, I notice I get a "Connect timeout" twice a day, about an hour after sunset, and an hour before sunrise. I suspect a quick fix for a leaky system, as the inverter reboots twice a day.

      The inverter only accepts one modbus connection at a time, so a second device is not an option.

      The instant power value swings very quickly, as clouds move accross the sky, and the fastest update time I can get allows he PLC to adjust the load on 2 x hot water system elements via SSRs. The kWh value is only really used to display "daily usage" of 15 - 30 kWh. It could be read every 15 - 30 minutes.

      I have a support request open with solaredge, and have sent then the wireshark logs of a working modpoll connection from a PC, and a PLC connection showing only 3 x SYN request. I will sent them my findings from this, but I will ask for a "stress test" on the next inverter I purchase.

      Thanks for all your help

      posted in Mango Automation general Discussion
      R
      rob987

    Latest posts made by rob987

    • RE: MQTT datapoint parsing help.

      Hi,
      Tried the date format yyyy-MM-dd'T'HH:mm:ss.SSS and the error changed to

      Error during read topic: "tele/tasmota_E14FF4/SENSOR" datapoint: "MQTT_NAS - Mealies_Temperature" payload: "{"Time":"2021-01-13T13:26:48","DS18B20":{"Id":"01192718DE3D","Temperature":28.1},"TempUnit":"C"}" exception: "Text '2021-01-13T13:26:48' could not be parsed at index 19"
      

      I have the Sensor temperature, and WiFi signal strength working now. ( Just using JSON, and not JSON + Timestamp, as I cannot find a parsing string that works )

      Mango is subscribed to two topics, STATE and SENSOR.

      The steps I took were

      1. Connect to MQTT Broker and get a copy of the raw data ( Also checks connection from Mango PC )
      robert@mango:~$ mosquitto_sub  -h 192.168.220.208 -p 1883 -u robert -P XXXXX -t tele/#
      
      Client mosqsub/22329-mango received PUBLISH (d0, q0, r0, m0, 'tele/tasmota_E14FF4/STATE', ... (274 bytes))
      tele/tasmota_E14FF4/STATE {"Time":"2021-01-13T10:46:48","Uptime":"4T17:22:27","UptimeSec":408147,"Heap":25,"SleepMode":"Dynamic","Sleep":50,"LoadAvg":19,"MqttCount":3,"Wifi":{"AP":1,"SSId":"NixNet","BSSId":"E4:8D:8C:3F:D7:A1","Channel":1,"RSSI":92,"Signal":-54,"LinkCount":1,"Downtime":"0T00:00:03"}}
      Client mosqsub/22329-mango received PUBLISH (d0, q0, r0, m0, 'tele/tasmota_E14FF4/SENSOR', ... (96 bytes))
      tele/tasmota_E14FF4/SENSOR {"Time":"2021-01-13T10:46:48","DS18B20":{"Id":"01192718DE3D","Temperature":26.6},"TempUnit":"C"}
      

      Check the Subscribed Data at https://jsonformatter.org/json-parser You can paste the received data string in, and get a readable JSON document.

      tele/tasmota_E14FF4/STATE

      object{9}
      	Time : 2021-01-13T10:46:48
      	Uptime : 4T17:22:27
      	UptimeSec : 408147
      	Heap : 25
      	SleepMode : Dynamic
      	Sleep : 50
      	LoadAvg : 19
      	MqttCount : 3
      	Wifi {8}
      		AP : 1
      		SSId : NixNet
      		BSSId : E4:8D:8C:3F:D7:A1
      		Channel : 1
      		RSSI : 92
      		Signal : -54
      		LinkCount : 1
      		Downtime : 0T00:00:03
      

      And
      tele/tasmota_E14FF4/SENSOR

      object {3}
          Time : 2021-01-13T10:46:48
          DS18B20 {2}
              Id : 01192718DE3D
              Temperature : 26.6
          TempUnit : C
      

      Here are the working MQTT Datapoint setups
      Wifi_Signal.png

      And Temperature
      Temperature_MQTT.png

      And The correct values shown on the datasource page
      DataSource_MQTT.png

      If anyone has some ideas on how to parse the Time (JSON + Timestamp) let me know

      Thanks

      posted in User help
      R
      rob987
    • RE: MQTT datapoint parsing help.

      I have been trying different patters, and have a new error which is confusing me.
      The Date could not be parsed, then the message ends with
      :ISO resolved to 2021-01-12T16:46:47 of type java.time.format.Parsed"

      ERROR 2021-01-12T16:46:47,246 (com.infiniteautomation.m2m2.mqtt.client.MqttClientDataSourceRT.messageArrived:375) - Error during read topic: "tele/tasmota_E14FF4/SENSOR" datapoint: "MQTT_NAS - Mealies_Temperature" payload: "{"Time":"2021-01-12T16:46:47","DS18B20":{"Id":"01192718DE3D","Temperature":26.6},"TempUnit":"C"}" exception: "Text '2021-01-12T16:46:47' could not be parsed: Unable to obtain Instant from TemporalAccessor: {},ISO resolved to 2021-01-12T16:46:47 of type java.time.format.Parsed" 
      

      MQTT_Point.png

      posted in User help
      R
      rob987
    • MQTT datapoint parsing help.

      Hi,
      I need some pointers on getting MQTT data into mango.
      I have configured the MQTT Broker OK, and am receiving data,
      but I cannot work out how to parse it.

      INFO  2021-01-11T17:13:09,026 (com.serotonin.m2m2.rt.RuntimeManagerImpl.stopDataSourceShutdown:447) - Data source 'MQTT_NAS' stopped 
      INFO  2021-01-11T17:13:11,949 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initializeDataSourceStartup:408) - Data source MQTT_NAS took 2ms to start 
      WARN  2021-01-11T17:16:46,079 (com.infiniteautomation.m2m2.mqtt.client.MqttClientDataSourceRT.messageArrived:355) - Unknown topic "tele/tasmota_E14FF4/STATE" payload: "{"Time":"2021-01-11T17:16:45","Uptime":"2T23:52:24","UptimeSec":258744,"Heap":26,"SleepMode":"Dynamic","Sleep":50,"LoadAvg":19,"MqttCount":3,"Wifi":{"AP":1,"SSId":"NixNet","BSSId":"E4:8D:8C:3F:D7:A1","Channel":1,"RSSI":80,"Signal":-60,"LinkCount":1,"Downtime":"0T00:00:03"}}" 
      ERROR 2021-01-11T17:16:46,121 (com.infiniteautomation.m2m2.mqtt.client.MqttClientDataSourceRT.messageArrived:375) - Error during read topic: "tele/tasmota_E14FF4/SENSOR" datapoint: "MQTT_NAS - Mealies_Temperature" payload: "{"Time":"2021-01-11T17:16:45","DS18B20":{"Id":"01192718DE3D","Temperature":25.6},"TempUnit":"C"}" exception: "Text '2021-01-11T17:16:45' could not be parsed at index 0" 
      
      

      I have a json timestamp pattern of "yyyy'-'MM'-'dd'T'HH':'mm':'ss"
      Also, the temperature value is NaN :-(

      Thanks

      posted in User help
      R
      rob987
    • RE: An error occurred while logging in - Connection error

      Hi All,
      Well its the next morning here in Australia, and I am at home waiting for the corona virus to get me, so I clicked on the link for my mango install, and firefox did the security warning for a self signed certificate again - strange, then
      then the login worked, and up came the screen.
      ![alt text](0_1585524922854_Mango_Screen.png image url)

      Anyway, any thoughts on what magic happened overnight ?

      Thanks

      posted in User help
      R
      rob987
    • An error occurred while logging in - Connection error

      Hi,
      I have had mango running for about 18 months, log in once a week or so and check the solar data it
      records, and emails me. Last login, I updated, an now a week later, I realise i cannot log in.

      The login screen comes up, but fails with "An error occurred while logging in - Connection error"

      System:

      $ uname -a
      Linux mango 4.9.0-12-amd64 #1 SMP Debian 4.9.210-1 (2020-01-20) x86_64 GNU/Linux
      

      Java:
      I noticed the java install advice has changed to openjdk, so I upgraded, but no luck.

      $ java --version
      openjdk 14 2020-03-17
      OpenJDK Runtime Environment AdoptOpenJDK (build 14+36)
      OpenJDK 64-Bit Server VM AdoptOpenJDK (build 14+36, mixed mode, sharing)
      

      mango:
      ma.log only has INFO data logged
      Starting Mango 3.7.5 with Schema Version: 29

      all the processes seem to be running OK

      $ netstat -antp
      Active Internet connections (servers and established)
      Proto Recv-Q Send-Q Local Address           Foreign Address         State       PID/Program name    
      tcp        0      0 0.0.0.0:22              0.0.0.0:*               LISTEN      454/sshd            
      tcp        0      0 127.0.0.1:631           0.0.0.0:*               LISTEN      422/cupsd           
      tcp        0    196 192.168.220.80:22       192.168.220.103:56870   ESTABLISHED 610/sshd: robert [p 
      tcp6       0      0 :::8080                 :::*                    LISTEN      2125/java           
      tcp6       0      0 :::22                   :::*                    LISTEN      454/sshd            
      tcp6       0      0 ::1:631                 :::*                    LISTEN      422/cupsd           
      tcp6       0      0 :::8443                 :::*                    LISTEN      2125/java           
      tcp6       0      0 :::5502                 :::*                    LISTEN      2125/java           
      tcp6       0      0 192.168.220.80:45056    192.168.220.75:502      ESTABLISHED 2125/java           
      tcp6       0      0 192.168.220.80:5502     192.168.220.75:2902     ESTABLISHED 2125/java           
      tcp6       0      0 192.168.220.80:43566    10.11.21.253:502        ESTABLISHED 2125/java           
      tcp6       0      0 192.168.220.80:8443     192.168.220.103:53812   TIME_WAIT   -                   
      tcp6       0      0 192.168.220.80:8443     192.168.220.103:53946   TIME_WAIT   -
      

      I think the two "TIME_WAIT" lines are my login attempt.

      Where can I look for errors / logs that might help resolve the issue.

      Thanks

      posted in User help
      R
      rob987
    • RE: Modbus 32 bit ints are not correct

      Hi all,
      Well, at least I have won the dummy of the week award this week :-)
      The DINTs have swapped words, so when you read from the correct address and swap the words, all is good.
      I "fixed" the publisher by creating a second publisher on same port number, and modbus address 2.
      I did have SINT and DINT data combined in the one publisher, and the PLC was making 2 read requests.
      The DINT values are now increasing as expected.

      Thanks all

      posted in Mango Automation general Discussion
      R
      rob987
    • RE: Modbus 32 bit ints are not correct

      Another problem discovered. I am reading 3 x 32 bit values from an inverter via modbus, and publish them for the PLC to read. The values in mango seems correct, but are not being updated to the publisher. The PLC read is showing success, and the value in the register is being overwritten, but is is not the same as the value in Mango.

      0_1554622881993_Exported_Energy.png

      M_Exported_Energy has a value of 444315 in Mango, but the PLC shows 4390912. This value has not changed all day, so "Export Today" shows as zero.

      I checked logIO in the publisher, files are created, but no data is logged

      -rw-r--r-- 1 root root 0 Apr 7 17:09 processLog.ModbusIpPublisherRT-1.log
      -rw-r--r-- 1 root root 0 Apr 7 17:09 processLog.ModbusProcessImageSendThread-1.log
      @mango:/opt/mango/logs$

      How do I debug the publisher?

      posted in Mango Automation general Discussion
      R
      rob987
    • Modbus 32 bit ints are not correct

      Hi,
      I have a problem reading 32 bit unsigned ints from a PLC. The smaller values are correct, but larger values are not.
      I have done the point locater read using all the available 4 byte int types, with no luck. The data is good when read with modpoll, and agrees with the PLC data.

      The larger values are Watt hour values from power meters, and the PLC stores the midnight values, to show the current days usage.

      $ modpoll -m tcp -a 1 -r 16401 -c 18 -t 4:int -1 192.168.220.75
      modpoll 3.4 - FieldTalk(tm) Modbus(R) Master Simulator
      Copyright (c) 2002-2013 proconX Pty Ltd
      Visit http://www.modbusdriver.com for Modbus libraries and tools.
      
      Protocol configuration: MODBUS/TCP
      Slave configuration...: address = 1, start reference = 16401, count = 18
      Communication.........: 192.168.220.75, port 502, t/o 1.00 s, poll rate 1000 ms
      Data type.............: 32-bit integer, output (holding) register table
      
      -- Polling slave...
      [16401]: 712312
      [16403]: 0
      [16405]: 7787370
      [16407]: 4738731
      [16409]: 7431320
      [16411]: 1011237
      [16413]: 710242
      [16415]: 4390912
      [16417]: 4552479
      [16419]: 7269753
      [16421]: 11488
      [16423]: 6472
      [16425]: 12772
      [16427]: 6717
      [16429]: 2070
      [16431]: 0
      [16433]: 8466
      [16435]: 4306
      
      

      The above modpoll values are correct.
      The point locator test returns the following values -

      0_1554615288841_Screenshot from 2019-04-07 15-32-18.png

      Note, one of the zero values is correct, and the other is 655360

      In space separated text,

      Click PLC Modpoll Read Point Locator
      Register Type MB Address Name Value Value Address Value Address
      DD9 INT2 416401 Pool_Energy 712314 712314 [16401] 1029992 16399
      DD10 INT2 416403 Spare 0 0 [16403] 655360 16401
      DD11 INT2 416405 CP3_Import_Energy_MidN 7787370 7787370 [16405] 54122 16403
      DD12 INT2 416407 CP3_Export_Energy_MidN 4738731 4738731 [16407] 7753387 16405
      DD13 INT2 416409 H1_Energy_MidN 7431320 7431320 [16409] 4744344 16407
      DD14 INT2 416411 H2_Energy_MidN 1011237 1011237 [16411] 7433765 16409
      DD15 INT2 416413 Pool_Energy_MidN 710242 710242 [16413] 1037922 16411
      DD16 INT2 416415 SE5K_M_Export_Energy_Mid 4390912 4390912 [16415] 655360 16413
      DD17 INT2 416417 SE5K_M_Import_Energy_Mid 4552479 4552479 [16417] 4421407 16415
      DD18 INT2 416419 SE5K_I_Energy_MidN 7269753 7269753 [16419] 4582777 16417
      DD19 INT2 416421 CP3_Import_Today 11487 11487 [16421] 7220448 16419
      DD20 INT2 416423 CP3_Export_Today 5942 5942 [16423] 5942 16421
      DD21 INT2 416425 H1_Energy_Today 11989 11989 [16425] 11989 16423
      DD22 INT2 416427 H2_Energy_Today 6650 6650 [16427] 6650 16425
      DD23 INT2 416429 Pool_Energy_Today 2070 2070 [16429] 2070 16427
      DD24 INT2 416431 SE5K_M_Exp_Energy_Today 0 0 [16431] 0 16429
      DD25 INT2 416433 SE5K_M_Imp_Energy_Today 7242 7242 [16433] 7242 16431
      DD26 INT2 416435 SE5K_I_Energy_Today 4306 4306 [16435] 4306 16433

      Any suggestions on how to resolve ?

      Thanks

      posted in Mango Automation general Discussion
      R
      rob987
    • RE: Modbus TCP no recipient found for response

      Hi,
      Just reporting that no errors in the last 24 hours,
      I have the TCP with keepalive set, Comms was very unreliable with a new connection for each request.
      Now the forest of errors has disappeared, I notice I get a "Connect timeout" twice a day, about an hour after sunset, and an hour before sunrise. I suspect a quick fix for a leaky system, as the inverter reboots twice a day.

      The inverter only accepts one modbus connection at a time, so a second device is not an option.

      The instant power value swings very quickly, as clouds move accross the sky, and the fastest update time I can get allows he PLC to adjust the load on 2 x hot water system elements via SSRs. The kWh value is only really used to display "daily usage" of 15 - 30 kWh. It could be read every 15 - 30 minutes.

      I have a support request open with solaredge, and have sent then the wireshark logs of a working modpoll connection from a PC, and a PLC connection showing only 3 x SYN request. I will sent them my findings from this, but I will ask for a "stress test" on the next inverter I purchase.

      Thanks for all your help

      posted in Mango Automation general Discussion
      R
      rob987
    • RE: Modbus TCP no recipient found for response

      Hi,
      Thanks for all the input. 247 errors yesterday (27/03/2019) on a cloudy rainy day, so the inverter does not rest :-),
      and devote more time to comms.

      The inverter is on a wired ethernet connection, with mango and the inverter on the wired LAN.

      I had "Contiguous batches only" ticked, as the inverter would not answer back when I first added it. I have now ticked it and reduced the max read registers to 50. The This is giving me 2 requests.

      2019/03/28-08:33:28,568 O 00230000000601030053000d
      2019/03/28-08:33:28,833 I 00230000001d01031a22e2ffff1384fffe2494ffff91d8fffedac6fffe006aeaf70000
      2019/03/28-08:33:28,834 O 002400000006010300ce0025
      2019/03/28-08:33:28,914 I 00240000004d01034a033b012300f7011f00000388012c011d01440000fe93ffb7ff73ff6a0000de17db9ee036de71fffe004162a600191f070015cec0001e39760044aaeb002c0006001e72c40005fcb80000
      
      

      What is the ,nnn after the date-time in the above log (2019/03/28-08:33:28,568). Is it mS timestamp of Java sending and receiving?

      Is there any way to have a poll period associated with a point.? The 2nd longer read is for kWh values, and could be read every 15 minutes. This might allow the instant power values to be read more frequently.

      I am using mango to read, and publish the values to a Click PLC, as I cannot get the Click to talk to the inverter. I used wireshark on the line, and I see the PLC send 3 SYN requests, and the inverter does not reply. I suspect it may be "to fast" for the inverter.

      No errors for 30 minutes, so maybe solved, but not fixed !!!!!!
      Thanks

      posted in Mango Automation general Discussion