    Modbus module evaluation
    6 Posts 2 Posters 4.4k Views 1 Watching
    • B Offline
      boris
      hi there !
      I'm playing with m2m2 + modbus (so no license for core/modbus) and I don't manage to use more than one modbus point.
      I'm doing the following:
      • create a modbus data source
      • tests: module scan, read data, point locator test
      • create a point (coil status) - name: y11
      everything seems to work ; but then, if I add a 2nd point (name: m11), I get "illegal data value" alarms for that point, while the 1st one (y11) is working OK.
      it's not a problem with the point config itself since if I first define m11 then y11, the illegal data value is now for y11 while m11 is working.
      tried with 1.1.0 as well as 1.2.0rc.
      is that a limitation of the trial mode ?
        No, there is no such limitation in the module trial mode.
        Can you provide an export of the points? Also, when you test them with the data source tools, what values do you get back?
        • B Offline
          boris
          thanks for the quick reply...
          here's the export (with the data source as well).
          this m2m2 instance is only for tests and this specific data source + 2 points, so no problem if you want me to do some tests / brake things.
          forgot to mention that to iron out a problem with the modbus device itself (Delta electronics/IFD9506) I tried reading the coils with libmodbus (on linux) as well as Delta's own software and everything is OK.
          Edit:
          1/ results of the read data test / coil / 2050 + 10:
          2050 ==> false
          2051 ==> true
          2052 ==> false
          2053 ==> false
          2054 ==> true
          2055 ==> false
          2056 ==> false
          2057 ==> true
          2058 ==> true
          2059 ==> false
          2/ results of point locator for coil 2059
          Result: false
          Attachment: download link
            For fun, try checking "Contiguous batches only" and saving the data source.
            • B Offline
              boris
              it seems it fixed it, no new alarm for 10 minutes.
              I thought about that option when reading the changelog of 1.2.0rc, but 1.1.0 had the same problem so I dismissed it.
              thanks - I will continue testing... ; feel free to ask if you want me to test that setup again with in case you patch something.