    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    Modbus RTU datasource configuration

    Scheduled Pinned Locked Moved Mango Automation general Discussion
    13 Posts 3 Posters 4.0k Views 3 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • phildunlapP Offline
      phildunlap
      last edited by phildunlap

      You could try increasing the timeout from 500ms to 5000ms. It's also worth noting that Mango Modbus offsets are 0 indexed, so if the device only responds to reads on valid registers and there are invalid registers around where you are reading, you may want to try the offset +/- 1.

      Another possibility is that there is a register that needs to be written periodically for the device to respond. I've seen that before, but not on serial devices. You could investigate that route by either searching the documentation for anything like that or monitoring what sort of output the proprietary program is doing. It's also possible their protocol begins with a preamble that isn't Modbus at all. Presumably that would be in the manual.

      One thing that strikes me is the "1 bit start." I don't see any way to configure the start bits in the underlying serial port implementation we use (and I don't see anyone complaining about that in my googling, either). I plugged a USB to serial converter into my Windows machine and checked its settings with the 'mode' command. Oddly nothing there about start bits either. You could launch the proprietary program, begin communication and collect mode output for the serial port from the command prompt, then do the same thing with Mango and compare differences. On Linux that would be with the stty commands (and in the stty help I also don't see a way to set start bits). That should let you see if the issue is caused by serial port settings.

      Also I wonder if you have LEDs on the USB to Serial converter, and you can visually tell that the device is not responding to Mango.

      1 Reply Last reply Reply Quote 0
      • E Offline
        etantonio
        last edited by

        Hy,
        it is not possible to use mode during activity on COM8 ,
        so this is the output of mode command when software is stopped
        0_1538381283472_Mode1.png

        and also, using a serial port sniffer during "Aurora communication" activity,
        I've the following results, it seems that are bad CRC but it is working correctly and led blinks green and red on usb-rs485 converter.

        No result also using offset +/-1

        *-----------------------------------------------
        [01/10/2018 10:14:11]
        Modbus Request (COM8)
        Address: 4
        Function: 70 (0x46)
        Checksum: 26122(BAD)

        [01/10/2018 10:14:11]
        Modbus Response (COM8)
        Address: 0
        Function: 6 (0x06) - Write Single Register
        Address: 9028
        Value: 45023
        Checksum: 54017(BAD)

        [01/10/2018 10:14:11]
        Modbus Request (COM8)
        Address: 4
        Function: 78 (0x4e)
        Checksum: 3520(BAD)

        [01/10/2018 10:14:11]
        Modbus Response (COM8)
        Address: 0
        Function: 6 (0x06) - Write Single Register
        Address: 9
        Value: 40990
        Checksum: 2310(BAD)

        1 Reply Last reply Reply Quote 0
        • CraigWebC Offline
          CraigWeb
          last edited by

          I’ve had issues before where one program takes over the port. Try useing a different port for mango and move the usb Converter

          1 Reply Last reply Reply Quote 0
          • E Offline
            etantonio
            last edited by etantonio

            Also changing usb port it is always assigned COM8,
            I think that Aurora Power One implement a proprietary Modbus RTU,

            http://www.drhack.it/images/PDF/AuroraCommunicationProtocol_4_2.pdf

            somewhere I found this information about how to get current and voltage from the inverter

            0x01(ADDRESS) + 0x03 (FUNCTIONALITY) + 0x17,0x00,0x20,0x20,0x20,0x20 (RICHIESTA TENSIONE) + CRC
            0x01(ADDRESS) + 0x03 (FUNCTIONALITY) + 0x19,0x00,0x20,0x20,0x20,0x20 (RICHIESTA CORRENTE) + CRC

            but I'm not sure about how to use such info in mango

            http://www.curtronics.com/Solar/AuroraData.html

            1 Reply Last reply Reply Quote 0
            • CraigWebC Offline
              CraigWeb
              last edited by

              @etantonio said in Modbus RTU datasource configuration:

              Aurora Power-one

              that might explain the existence of this http://www.eborx.com/download/en/powerone/accessories/pvi-rs485-modbus-converter/pvi-rs485-modbus-en.pdf
              I could not find anything about modbus on the aurora power-one manual that I found online.

              1 Reply Last reply Reply Quote 0
              • E Offline
                etantonio
                last edited by

                yes,
                you are right,
                it is a converter from "rs485 aurora" to modbus rtu, so it seems there's no way to work with mango without this object

                1 Reply Last reply Reply Quote 0
                • phildunlapP Offline
                  phildunlap
                  last edited by

                  Good sleuthing!

                  You can definitely do this through Mango still, it just takes a different approach and another few steps. The Serial Data Source can certainly send out "rs485 aurora" and a script can decode it. If you only need a small subset of the possible accessible information and already have the means to record the serial communication it's not that much more work to replay that communication and decode the result. There's a lot of information in this somewhat old thread: https://forum.infiniteautomation.com/topic/2517/chinese-brand-psu_monitoring-rs485-and-mango

                  But the TLDR is that you can set up a serial data source with command / response points and parse the results in a script, and you can have the serial data source be configured to use hex so that you can simply replay the bytes you've recorded to request information. You can send the reads from a script so that it's polling, or use a Point Link if you need to iterate through a whole polling conversation instead of a more Modbus style batch read.

                  1 Reply Last reply Reply Quote 0
                  • E Offline
                    etantonio
                    last edited by

                    Please excuse me,
                    the requirement is changed and i didn't check this,
                    yes, we need the average of point values of last minute, no more the sum.
                    So you think that this could be a good solution?
                    Data surce pools each second and data point computes average of last minute points

                    Regarding database storing I've checked directly on the db that just one data point is stored each minute so I don't care about cached data showed in the datapoint history.
                    Thanks,
                    Antonio

                    1 Reply Last reply Reply Quote 0
                    • phildunlapP Offline
                      phildunlap
                      last edited by

                      I'm not not sure of the question. It sounds like you're asking if the interval logging 'average' option is a good way to log an interval average. If so: yes, that's it's purpose.

                      E 1 Reply Last reply Reply Quote 0
                      • E Offline
                        etantonio @phildunlap
                        last edited by

                        @phildunlap sorry, I'm working on several pc and this question was related to another post

                        https://forum.infiniteautomation.com/topic/3795/sum-each-minute-of-parameter-each-second-value

                        I don't know maybe my distraction or a cross-session problem. Thanks, Antonio