Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
Priority Array
-
Hi
I'm new to BACNet. I wrote a small controller to expose some BACNet objects and some properies. But when I try to write a value to a property using CAS BACNet Explorer using priority other than 'undefined' it's giving an error. Will you be able to give me a working example with priority arrays.thanks
sb -
What's the error?
-
... and what object type are you trying to write to?
-
I'm writing to analogoutput type of objects.
When I write thru the CAS BACNet explorer with priority of 1 it says write access denied and on the java log I could see the listener method "allowPropertyWrite" was called but not the "propertyWritten" method. But when I write with undefined priority both methods are being called.this is how I'm definiing the object properties:
ao0.setProperty(PropertyIdentifier.objectName, new CharacterString(wp.getName()));
ao0.setProperty(PropertyIdentifier.presentValue, new Real(1)); ao0.setProperty(PropertyIdentifier.outOfService, new Boolean(false));
ao0.setProperty(PropertyIdentifier.units, EngineeringUnits.percent);
ao0.setProperty(PropertyIdentifier.description, new CharacterString("31233232132"));
ao0.setProperty(PropertyIdentifier.timeDelay, new UnsignedInteger(90));
ao0.setProperty(PropertyIdentifier.priorityArray, new PriorityArray());
ao0.setProperty(PropertyIdentifier.relinquishDefault, new Real(0));thanks for your immediate response.
SB -
Priority array handling and commandable values had not been implemented. I have added that now, but you'll need to check out the latest source and build into a jar with ANT.
-
Thanks. it worked.
-
Cool. Note that there are a couple limitations in the implementation.
- The min on/off times for binaries (priority 6) are not coded.
- The timing stuff around access doors is also not done.