    Modbus4J Modbus RTU master
    24 Posts 3 Posters 39.0k Views 2 Watching
    • amer jamilA Offline
      amer jamil
      Currently I am working with the Schneider Power Logic electrical device. I want to read the data from the device and show the value in my system. So far, I discover J2mod, Jamod and Modbus4Java library. I used all modbus4java to connect and get the device's data.
      Actually I still confuse whether I suppose to create Master side or Slave side. Based on my understanding, the device will be Slave and my system will be Master (1st question).
      Below is the setting AT MY DEVICE. It indicate that the device in slave mode and its protocol is Modbus RTU. So, I need to create a master apps to communicate with it right which is using the ModbusRTU protocol right ? (2nd question)
      Mode: Slave
      Protocol: Modbus RTU
      Address: 1
      Baud Rate: 38400
      Parity: None
      Below is the code of my apps act as the Master and using the ModbusRTU protocol
      public static void main(String[] args) throws ModbusTransportException, ErrorResponseException {
      ModbusFactory factory = new ModbusFactory();
      SerialParameters params = new SerialParameters();
      params.setCommPortId("COM6");
      params.setBaudRate(9600);
      params.setDataBits(8);
      params.setStopBits(1);
      params.setParity(0);
      ModbusMaster master = factory.createRtuMaster(params);
      master.setTimeout(1000);
      master.setRetries(0);
      long start = System.currentTimeMillis();
      try {
          master.init();
      } catch (Exception e) {
          System.out.println( "Modbus Master Init Error: " + e.getMessage());
            return;
      try {
          System.out.println("Reg. 1001 Value:" + master.getValue(1, RegisterRange.HOLDING_REGISTER, 3110, DataType.FOUR_BYTE_FLOAT_SWAPPED));
      finally {
          master.destroy();
      System.out.println("Time elapsed: " + (System.currentTimeMillis() - start) + "ms"); }
      This is the code that I get from the sample code provide by the Modbus4Java page. The other thing that concern me is the value of params.setCommPortId("COM6"); What other value than "COM6" that I can put there. Because basically it receive a String value. So am I able to put any String value to it ? And what is the function of this particular setCommPortID. (3rd question)
      Looking at the sample code provide by the Modbus4Java page, it does not put the IP address of the device. But in my case, my device got an IP address. And the IP address only use in the Slave apps only. How should my system recognize the IP address of the device ? (4th question).
      And after I run this code snippet, I got an error:
      Native lib Version = RXTX-2.1-7
      Java lib Version = RXTX-2.1-7
      Modbus Master Init Error: com.serotonin.io.serial.SerialPortException: gnu.io.NoSuchPortException
      Please, please and please help me. I been stuck with this almost a month. Really hope someone out there will be able to help me. Thank you in advance for any kind of help and suggestion.
      • hussamH Offline
        hussam
        4th question:if you get a ip address, you should use the modbus tcp/ip,not the modbus rtu(it base one serial com).
        3rd question: you should put the serial com name(seem like com1,com2 it is a string value).
        about the Native lib Version = RXTX-2.1-7 error? please update to the newest mango, it have moved to jssc replace rxtx.
        finally, acutally,if you use the mango 2.5.2 version,it have two module ,modbas serial and modbus tcp, it can easy connect to Schneider Power Logic electrical device.
        amer jamilA 1 Reply Last reply Reply Quote 0
          amer jamil @hussam
          @hussam Hi hussam. Thank you for the reply. Is Modbus4j and Mango 2.5.2 is the different library ? About the serial com name, I still confuse about the value. Can you explain more ?
          • hussamH Offline
            hussam
            Modbus4j is a jar lib which be used by modbus module, and the modbus run base one mango, 2.5.2 also is ok,but Modbus4j can't run alone bucause it need some jar.
            and the serial com name, if you have windows system,you can find some serial com like com1,com2, this is a string value.
              amer jamil @hussam
              @hussam I downloaded the mango 2.5.2. But it just like another software that you can use to interact with the electrical device. How should I integrate the mango with my system ?
              • jeremyhJ Offline
                jeremyh
                What is your end goal? What are you trying to accomplish? What system are you trying to get your power meter data into?
                  amer jamil @jeremyh
                  @jeremyh Hi Jeremy. My goal is to read the data in the Schneider Power Login meter. The value going to be store in the database. My system going to show the meter value. Its like the real time data. The system going to take the meter reading every 5 second and show the value in the system. My system using the Java Language and Spring framework.
                  Below is the example of my system interface.
                  • jeremyhJ Offline
                    jeremyh
                    To answer your question your PC would be the master and the power meter the slave. You would need to set a Slave ID in your power meter though with Modbus TCP sometimes this is not implemented and IP addresses are used instead of slave IDs.
                    Sometimes the server/client model is used in which case the power meter is your server, as it is serving the data (via a Modbus TCP Server), and the PC becomes the client.
                    How far along are you in your application?
                    It seems to me that it would be easier to make such a dashboard using the graphical views module of Mango, a DGLux dashboard (which would be the easiest, if your users dont mind running Flash) or a web interface using the API (maybe the hardest, but most future-proof).
                    Otherwise you will have to reinvent the wheel, there is a lot of stuff under the hood of mango to make sure it keeps working.
                      amer jamil @jeremyh
                      @jeremyh For me, it interface is not a problem. The problem right now is that, I am not able to read the data from the power meter. I also have done the TCP master. Below is the latest code that I try
                      	IpParameters params = new IpParameters();
                      	params.setHost("10.168.168.197");
                      	params.setPort(502);
                      	params.setEncapsulated(false);
                      	ModbusMaster master = factory.createTcpMaster(params, true);
                      	// master.setRetries(4);
                      	master.setTimeout(2000);
                      	try {
                      		master.init();
                      		ModbusLocator locator = new ModbusLocator(1, RegisterRange.HOLDING_REGISTER, 43111, DataType.TWO_BYTE_BCD);
                      		System.out.println("value: "+master.getValue(locator));
                      	finally {
                      		master.destroy();
                      	System.out.println("Took: " + (System.currentTimeMillis() - start) + "ms");
                      and the output of the coding is :
                      value: 8000
                      Took: 78ms
                      while there is no 8000 value at the power meter. Thank you.
                      • jeremyhJ Offline
                        jeremyh
                        From looking at the documentation for your power meter it appears that register 43111 is the second half of a four-byte float (which starts at register 43110) so you might just be reading the last two bytes. You should try reading from 43110 with DataType set to four byte float. If that doesn't give you the correct result try again from 43109 because some manufacturers start counting from 0 not 1.
                          amer jamil @jeremyh
                          @jeremyh actually some of my senior said that I suppose to add 40001 from its original register due to modbus protocol. I want to read the data from the register 3110 actually. In the documentation, the 3110 refer to the Frequency (Hz). That is my I get the 43111 register.
                          But I also try the 43110 and 43109 as you ask me to, but both the result is value: -4.5918E-41
                          • jeremyhJ Offline
                            jeremyh
                            Try using 3110 and and 3109 in your Java code then. Modbus4J is pretty 'smart' and probably makes such an adjustment for you.
                            You might like to get a modbus scanning application and run it on your PC to verify that the data is where you think it is, Mango has such a tool built in so if you have already installed Mango I would suggest using that. Just set up a Modbus TCP data source and use the Modbus read data function which will return the registers in Hex:
                            You can also try the 'point locator test', click the 'read' button and Mango will return the value it sees there.
                              amer jamil @jeremyh
                              @jeremyh Thank you so much jeremy. You really save my life. I try 3109 in my java code, and it show the correct value that I want. Thank you so much for helping me out. Can you explain more on how you get the 3109 value ? Why in the documentation it say that 3110 ?
                              God bless you Jeremy..
                              • jeremyhJ Offline
                                jeremyh
                                Modbus4J already does the 'subtract 40001' bit for you, so your colleague gave you a bit of misdirection there. It's still usually necessary if you are setting up a Modbus master in a PLC or something.
                                And some manufacturers start counting registers from 0 and some from 1, so sometimes (actually, often) what you think is register 3110 in your slave is 3109 according to your master.
                                A modbus scanner which shows you a whole bunch of registers is usually handy for figuring this out.
                                Just trial and error..
                                  amer jamil @jeremyh
                                  @jeremyh so what should I do next is, minus 1 from all the register that I want since it start count from 0 right ? Thank you so much again. Thank you for helping me around since the beginning.
                                  jeremyhJ 1 Reply Last reply Reply Quote 0
                                  • jeremyhJ Offline
                                    jeremyh @amer jamil
                                    Yes subtract 1 from all the registers in the documentation.
                                    • jeremyhJ Offline
                                      jeremyh
                                      Out of curiosity are you logging all the data in a database on disk? Or just in memory to draw the graphs?
                                      amer jamilA 2 Replies Last reply Reply Quote 0
                                        amer jamil @jeremyh
                                        @jeremyh yaa, the data will be insert into the database every minute.
                                          amer jamil @jeremyh
                                          @jeremyh Hello Jeremy. Want to ask you one more question. I am not from the Electric background. So, I find a difficulty in calculating the power consumption of the meter. For you information, my system going to add the data in the database for every one minute. How am i going to calculate the power consumption for the device for a day (24 hours). I have Kw value for every minute.
                                          Do I have to add the Kw value for every minute up to the whole day ?
                                          Thank you.
                                          • jeremyhJ Offline
                                            jeremyh
                                            Power (kw) is an instantaneous measurement. Energy (kWh), which is sounds like you want, is Power over Time. One kW of power being drawn for one hour is 1 kWh of energy. Half a kW for two hours is still 1 kWh.
                                            To convert kW to kWh you would have to integrate the kW measurement i.e calculate the area under a plot of power over time. This is only as accurate as your measurement/sampling interval which is only 1 minute.
                                            The real answer is to find the registers for cumulative energy (kWh and kVAh generally) in your meters and use that measurement to compute hourly/daily/annual kWh and kVAh energies. It will be a lot easier and a lot more accurate than trying to work it out yourself.