What's leading to these frequent rtn errors?
-
anyone can help to give me an answer? thanks so much.
Attachment: download link
-
At least in regards to the timeouts if they're frequent, I would
- investigate the wiring.
- turn the max read registers down a little, maybe <100 (do a little experimenting)
- Increase the polling interval.
For those socket errors, are your data sources configured to use particular COM ports? The -1 makes me wonder.
-
it seems like the your modbus slave's problem,if you use the modscan32 to test the datasource 'stability use the same configuration on mango.