Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
What's leading to these frequent rtn errors?
-
anyone can help to give me an answer? thanks so much.
Attachment: download link
-
At least in regards to the timeouts if they're frequent, I would
- investigate the wiring.
- turn the max read registers down a little, maybe <100 (do a little experimenting)
- Increase the polling interval.
For those socket errors, are your data sources configured to use particular COM ports? The -1 makes me wonder.
-
it seems like the your modbus slave's problem,if you use the modscan32 to test the datasource 'stability use the same configuration on mango.