    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    What's leading to these frequent rtn errors?

    User help
    3
    4
    1.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • mebiusM
      mebius
      last edited by

      anyone can help to give me an answer? thanks so much.

      Attachment: download link

      1 Reply Last reply Reply Quote 0
      • phildunlapP
        phildunlap
        last edited by

        At least in regards to the timeouts if they're frequent, I would

        1. investigate the wiring.
        2. turn the max read registers down a little, maybe <100 (do a little experimenting)
        3. Increase the polling interval.

        For those socket errors, are your data sources configured to use particular COM ports? The -1 makes me wonder.

        1 Reply Last reply Reply Quote 0
        • hussamH
          hussam
          last edited by

          it seems like the your modbus slave's problem,if you use the modscan32 to test the datasource 'stability use the same configuration on mango.

          1 Reply Last reply Reply Quote 0