    CRC mismatch
    9 Posts 2 Posters 6.9k Views 1 Watching
    • G Offline
      greenday
      i have a problem to send a command to a device and get response,
      there is an exception that say CRC is mismatch but, i attached the request and response sniffed by serial monitor
      it seems everything is ok, but why i get CRC mismatch exception!!!?
      Native lib Version = RXTX-2.1-7
      Java lib Version = RXTX-2.1-7
      ready to send connect command
      com.serotonin.modbus4j.exception.ModbusTransportException: CRC mismatch: given=1
      065, calc=49192
      at com.serotonin.modbus4j.base.ModbusUtils.checkCRC(ModbusUtils.java:87)
          at com.serotonin.modbus4j.serial.rtu.RtuMessageResponse.createRtuMessage
      Response(RtuMessageResponse.java:21)
      at com.serotonin.modbus4j.serial.rtu.RtuMessageParser.parseMessageImpl(R
      tuMessageParser.java:21)
      at com.serotonin.modbus4j.base.BaseMessageParser.parseMessage(BaseMessag
      eParser.java:17)
      at com.serotonin.messaging.MessageControl.data(MessageControl.java:133)
      at com.serotonin.messaging.InputStreamListener.run(InputStreamListener.j
      ava:76)
      **Request: 2012/03/03 02:26:34 ?.?.07964 (+23.5156 seconds)
      01 10 00 A8 00 02 04 35 35 35 35 30 F4 ...¨...55550ô
      Answer: 2012/03/03 02:26:34 ?.?.12664 (+0.0469 seconds)
      01 10 00 A8 00 02 04 29 93 ...¨...)?
        Can you turn on IO logging to get a trace of what the lib is seeing?
        • G Offline
          greenday
          Thanks for your reply, but how to enable IO logging ?
            ModbusMaster.setIoLog(PrintWriter)
            Also, have you tried ModbusMaster.setDiscardDataDelay. Maybe try setting that to something like 200ms and see if that helps.
            • G Offline
              greenday
              Sorry, but i can not find ModbusMaster.setIoLog(...) or ModbusMaster.setDiscardDataDelay(...) in Modbus4j library project.
              I'm sure that i use last version of modbus4j that i download from sourceforge, so what can i do now?
              update 1 -------------------------------------
              Ok now i found that those functions are in cvs repository,
              i will try them and send report here
              update 2 -------------------------------------
              i try to use IoLog, but nothing happen, logger did not write even an character!!!
              about setDiscardDataDelay also nothing happen,
              but i found that if i ignore the exception, i can run the next command on my device without error!
              because the data that we send and receive is correct.
              so what is that crc problem?
                I uploaded a newer jar file to the repo. It includes epoll support now too.
                Try setting the iolog to System.out or something like that. It works for me.
                • G Offline
                  greenday
                  Hi
                  my problem still exist and my code throw CRC exception.
                  but finally i can run I/O logging and here is the result:
                  Stable Library
                  1331106184515 O 011000a80002043535353530f4
                  1331106184609 I 011000a80002042993
                  065, calc=49192
                  at com.serotonin.modbus4j.base.ModbusUtils.checkCRC(ModbusUtils.java:104
                  Response(RtuMessageResponse.java:41)
                  tuMessageParser.java:41)
                  eParser.java:37)
                  at com.serotonin.messaging.MessageControl.data(MessageControl.java:170)
                  ava:76)
                  1331106186531 O 011000a80002043535353530f4
                  1331106186562 I 011000a80002042993
                  065, calc=49192
                  eParser.java:37)
                  ava:76)
                    I get the same result. The incoming response looks otherwise ok. The part "011000a80002" looks right. What is suspicious is that the response has 3 bytes at its tail instead of just two: "042993". A CRC is only two bytes.
