    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website
    Help for bacnet and bacnet4J
    Scheduled Pinned Locked Moved BACnet4J general discussion
    21 Posts 4 Posters 37.2k Views 1 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • I Offline
      ilyass
      Hi,
      I am new in Bacnet and Bacnet4J. I am developping an slave bacnet application. this application has to discover a list of bacnet objects/devices and after to manage its. I am using VTS (Virtual Tset Shell) to test my application.
      I have some questions, so :
      1- i create a localDevice
      LocalDevice localDevice = new LocalDevice(1, "10.193.224.255", "10.193.224.239");
      10.193.224.255 : address broadcast
      and after i initialise it
      try {
               	localDevice.initialize();
               }catch(IOException e) {
               	System.out.println("IO Error!");
               	e.printStackTrace();
               	return;
      finally i send a broadcast request
      localDevice.sendBroadcast(0xBAC0, new WhoIsRequest(null, null));
      but the list of object is empty and VTS doesn't receive any thing, i don't know why because with VTS i create devices and objects that have "10.193.224.177" address IP. So i don't know how i can do this
      2- what is the different between remoteDevice and localDevice ?
      3- second test : with VTS i send WhoIsRequest
      after i create a bacnet object in my application
               BACnetObject bacnetObj = new BACnetObject(localDevice, new ObjectIdentifier(ObjectType.analogInput, 10));
               bacnetObj.setProperty(PropertyIdentifier.objectName, new CharacterString("TemperatureSensorOneRF"));
               bacnetObj.setProperty(PropertyIdentifier.description, new CharacterString("Controller of TemperatureSensor"));
      after i send :
       localDevice.sendBroadcast(0xBAC0, new IAmRequest(new ObjectIdentifier(ObjectType.analogInput, 10), new UnsignedInteger(1024), Segmentation.noSegmentation, new UnsignedInteger(236)));
      But VTS doesn't receive any thing
      thanks for help
      1 Reply Last reply Reply Quote 0
      • M Offline
        mlohbihler
        Can you use wireshark to try and figure out what's going on? At least to produce some message traces?
        Best regards,
        Matthew
        • I Offline
          ilyass
          Hi,
          I found the solution of my problem. On VTS I configured the network as remote network but i test in local network. So i changed it and now i receive informations from my application
          Thank you for your help.
          Just an other question, i have this exception when i send UnconfirmedTextMessage via VTS :
          com.serotonin.bacnet4j.exception.BACnetException: Error while creating APDU:
          	at com.serotonin.bacnet4j.npdu.ip.IpMessageControl$IncomingMessageExecutor.runImpl(IpMessageControl.java:501)
          	at com.serotonin.bacnet4j.npdu.ip.IpMessageControl$IncomingMessageExecutor.run(IpMessageControl.java:455)
          	at java.util.concurrent.ThreadPoolExecutor$Worker.runTask(ThreadPoolExecutor.java:886)
          	at java.util.concurrent.ThreadPoolExecutor$Worker.run(ThreadPoolExecutor.java:908)
          	at java.lang.Thread.run(Thread.java:619)
          Caused by: com.serotonin.bacnet4j.exception.BACnetException: java.lang.reflect.InvocationTargetException
          	at com.serotonin.bacnet4j.type.Encodable.read(Encodable.java:174)
          	at com.serotonin.bacnet4j.type.Encodable.read(Encodable.java:186)
          	at com.serotonin.bacnet4j.type.constructed.Choice.read(Choice.java:65)
          	at com.serotonin.bacnet4j.type.constructed.Choice.<init>(Choice.java:54)
          	at com.serotonin.bacnet4j.service.unconfirmed.UnconfirmedTextMessageRequest.<init>(UnconfirmedTextMessageRequest.java:100)
          	at com.serotonin.bacnet4j.service.unconfirmed.UnconfirmedRequestService.createUnconfirmedRequestService(UnconfirmedRequestService.java:46)
          	at com.serotonin.bacnet4j.apdu.UnconfirmedRequest.<init>(UnconfirmedRequest.java:62)
          	at com.serotonin.bacnet4j.apdu.APDU.createAPDU(APDU.java:38)
          	at com.serotonin.bacnet4j.npdu.ip.IpMessageControl$IncomingMessageExecutor.runImpl(IpMessageControl.java:498)
          	... 4 more
          Caused by: java.lang.reflect.InvocationTargetException
          	at sun.reflect.NativeConstructorAccessorImpl.newInstance0(Native Method)
          	at sun.reflect.NativeConstructorAccessorImpl.newInstance(NativeConstructorAccessorImpl.java:39)
          	at sun.reflect.DelegatingConstructorAccessorImpl.newInstance(DelegatingConstructorAccessorImpl.java:27)
          	at java.lang.reflect.Constructor.newInstance(Constructor.java:513)
          	at com.serotonin.bacnet4j.type.Encodable.read(Encodable.java:171)
          	... 12 more
          Caused by: com.serotonin.bacnet4j.exception.BACnetErrorException: 29
          	at com.serotonin.bacnet4j.type.primitive.CharacterString.validateEncoding(CharacterString.java:138)
          	at com.serotonin.bacnet4j.type.primitive.CharacterString.<init>(CharacterString.java:80)
          	... 17 more
          do you know why ?
          thanks
          • M Offline
            mlohbihler
            The character encoding you are using is not recognized. The reference value is 29, but the only valid values AFAIK are:
                public interface Encodings {
                    byte ANSI_X3_4 = 0;
                    byte IBM_MS_DBCS = 1;
                    byte JIS_C_6226 = 2;
                    byte ISO_10646_UCS_4 = 3;
                    byte ISO_10646_UCS_2 = 4;
                    byte ISO_8859_1 = 5;
            Can you provide a trace of the message?
            Best regards,
            Matthew
            • I Offline
              ilyass
              With VTS, when i sent UnconfirmedTextMessage, i specified a numeric class witch doesn't exists, so my application throws exception
              thank you for your help
              Attachment: download link
              • M Offline
                mlohbihler
                Code changes have been made so that a more informative error message is provided.
                Best regards,
                Matthew
                • I Offline
                  ilyass
                  Hi,
                  I have a question about SubscribeCOVRequest; it is possible to make the subscription COV for all time and not for a specific lifetime ?
                  thanks for help
                  • M Offline
                    mlohbihler
                    From the spec:
                    13.14.1.5 Lifetime
                    This parameter, of type Unsigned, shall convey the desired lifetime of the subscription in seconds. A value of zero shall
                    indicate an indefinite lifetime, without automatic cancellation. A non-zero value shall indicate the number of seconds that
                    may elapse before the subscription shall be automatically cancelled. If both the 'Issue Confirmed Notifications' and 'Lifetime'
                    parameters are absent, then this shall indicate a cancellation request. If the 'Lifetime' parameter is present then the 'Issue
                    Confirmed Notifications' parameter shall be present.
                    Best regards,
                    Matthew
                    • I Offline
                      ilyass
                      Hi,
                      I have a problem with a new ObjectType that i added, it's CREDENTIAL_INPUT
                      when i execute
                      for each propertyReference i do
                      Encodable encodable = props.getNoErrorCheck(oid, pr);
                      pr is **PropertyReference **and props is PropertyValues and oid is my ObjectIdentifier
                      the result is
                      type.toString()=Credential Input
                      +pr.toString()=Object name--AmbiguousValue
                      +encodable.toString()=Ambiguous([75,e,0,4f,54,45,53,20,52,45,41,44,45,52,20,31])
                      +pr.toString()=Object identifier--AmbiguousValue
                      +objectIdentifier=Ambiguous([c4,9,40,40,0])
                      +pr.toString()=Object type--AmbiguousValue
                      +pr.toString()=Description--AmbiguousValue
                      +pr.toString()=Present value--AmbiguousValue
                      +pr.toString()=Status flags--AmbiguousValue
                      +pr.toString()=Reliability--AmbiguousValue
                      +pr.toString()=Out of service--AmbiguousValue
                      +pr.toString()=Update time--AmbiguousValue
                      updateTime=Ambiguous([])
                      +pr.toString()=Profile name--AmbiguousValue
                      instanceNumber=16384
                      Do you have an Idea ?
                      thanks for help
                      • M Offline
                        mlohbihler
                        Did you define the object type with all of its attributes in com.serotonin.bacnet4j.obj.ObjectProperties?
                        Best regards,
                        Matthew
                        • I Offline
                          ilyass
                          Hi,
                          Thanks for your help, i didn't do that
                          It works know
                          • I Offline
                            ilyass
                            Hi,
                            I have always the same problem with the subscriptionCOV service. I want to make it without cancellation. So from the spec we have :
                            13.14.1.5 Lifetime
                            So i put this
                            SubscribeCOVRequest service = new SubscribeCOVRequest(
                            					new UnsignedInteger(1), objectIdentifier,
                            					new Boolean(true), new UnsignedInteger(0));
                            try {
                                    localDevice.send(remoteDevice, service);
                            	log.info("subsciption of " + objectIdentifier.getObjectType()
                            						+ "-" + objectIdentifier.getInstanceNumber() + " done");
                            } catch (BACnetException e) {
                            	log.error("unable to send <SubscribeCOVRequest> for the Object "
                            		+ objectIdentifier.getObjectType()+  "-"+objectIdentifier.getInstanceNumber()+ "\t"+ e.getMessage());
                            I tested lifetime = null, but it doesn't work
                            thanks for help
                            • M Offline
                              mlohbihler
                              You mean the request fails? If so, can you provide details of the BACnet exception?
                              Or do you mean that the subscription still expires? This may be due to the equipment to which you are sending the request. Or maybe not.
                              Best regards,
                              Matthew
                              • I Offline
                                ilyass
                                I mean that the notification doesn't work, but no exception is made.
                                when i send this subscription, i received just one time the notification.
                                • M Offline
                                  mlohbihler
                                  Still don't understand. If you received any notification at all, doesn't that mean the subscription worked, at least for some time?
                                  Best regards,
                                  Matthew
                                  • J Offline
                                    jeremie
                                    Hi,
                                    I think I have an idea what Ilyass tries to mean :
                                    when he uses COV on an object with a lifetime greater than 0, he receives correcty events when the PresentValue of the COVing object changes.
                                    But when he tries with a lifetime equals to 0 (no timeout for COV subscription), he catchs only one time the COV event.
                                    For information, in Mango, the point COVing mechanism is configure with a lifetime greather than 0 : you use COV for a certain time, and when this time is finished, you COV again. Have you got a reason to do this, instead of use a lifetime of 0?
                                    • M Offline
                                      mlohbihler
                                      It works fine for me. But let's be sure we're talking about the same thing...
                                      In my tests i used BACnet4J as subscriber and subscribee. The subscriber sent the following request:
                                                  ObjectIdentifier oid = new ObjectIdentifier(ObjectType.binaryInput, 0);
                                                  SubscribeCOVRequest req = new SubscribeCOVRequest(new UnsignedInteger(0), oid, new Boolean(true),
                                      ... received regular COV notifications from the subscribee. (Specifically, the test code is SimpleSubscriptionClient and SlaveDeviceTest, both of which are now checked into the CVS.
                                      Note that COV subscriptions are only supported by certain object types, as enumerated in the static code block in ObjectCovSubscription (notably excuding analog objects).
                                      Best regards,
                                      Matthew
                                      • J Offline
                                        jeremie
                                        Thank for your SimpleSubscriptionClient test file :)
                                        Maybe you can add the unsubscribe code (because COV is done with an indefinite lifetime) :
                                        localDevice.send(d, new SubscribeCOVRequest(new UnsignedInteger(0), oid, null, null));
                                        • M Offline
                                          mlohbihler
                                          Good point. And i never answered your question...
                                          Infinite subscription lifetimes are convenient, but in practice they are problematic. Say the subscriber sends a 0 (infinite) lifetime. As far as it is concerned it will get COVs until it unsubscribes. But if the subscribee suffers a power failure it will likely lose the subscription, the COV notifications will stop, and the subscriber will never be the wiser.
                                          Conversely, if the subscriber restarts unexpectedly, the subscribee will continue to send notifications that will never be received (worst case).
                                          Using finite lease times and regular resubscriptions isn't a perfect solution to power failure (et al) situations, but it at least tends toward system stability.
                                          Best regards,
                                          Matthew
                                          • R Offline
                                            R-GiGgS84
                                            hi there, i am currently working on a way to retrieve information from a bacnet object if there are changes. Can anyone guide me on how this can be done or is there any sample for me to understand it?
                                            Thanks in advance! :)
                                            • First post