• Recent
    • Tags
    • Popular
    • Register
    • Login
    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
    Radix IoT Website Mango Documentation Radix IoT LinkedIn
    cannot load database
    Scheduled Pinned Locked Moved MangoES Hardware
    39 Posts 3 Posters 50.1k Views 4 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • J Offline
      Jay1089 @phildunlap
      @phildunlap said in cannot load database:
      /path/to/Mango/bin/ma.sh start
      Is it applicable to MangoES hardware. Mango is not installed in my computer. I am accessing the small MangoES standalone device which acts as a SCADA
      1 Reply Last reply Reply Quote 0
      • J Offline
        Jay1089
        RequestError: Unable to load /status/mango.json?time=1565839042939 status: 0
        this is the error popup in the browser when trying to access MangoES device. Hope it gives some idea
        • J Offline
          Jay1089
          I am more interested in restoring this device to Factory Default and create new works in it
          • phildunlapP Offline
            phildunlap
            Ah, I overlooked that it was a MangoES so I provided an informative if inaccurate way of writing the correct path. On a MangoES it would be /opt/mango/bin/ma.sh start
            There is not the ability to restore the device to a factory default. You can start Mango fresh, though, by deleting or moving your Mango/databases/ which Mango isn't running.
            Since the upgrade tool on the modules page isn't present in 2.5, you may consider downloading the 2.8 core from https://store.infiniteautomation.com/core , placing the .zip file into the /opt/mango/ directory and then start Mango. It would start up without modules installed, but you could download those from the modules page.
            1 Reply Last reply Reply Quote 1
            • J Offline
              Jay1089
              FATAL 2019-08-22 20:28:41,277 (com.serotonin.m2m2.db.DatabaseProxy.initialize:173) - Unable to connect to database of type H2
              org.springframework.jdbc.CannotGetJdbcConnectionException: Could not get JDBC Connection; nested exception is org.h2.jdbc.JdbcSQLException: File corrupted while reading record: "index not found 93". Possible solution: use the recovery tool [90030-180]
              at org.springframework.jdbc.datasource.DataSourceUtils.getConnection(DataSourceUtils.java:80)
              at org.springframework.jdbc.core.JdbcTemplate.execute(JdbcTemplate.java:388)
              at org.springframework.jdbc.core.JdbcTemplate.query(JdbcTemplate.java:468)
              at org.springframework.jdbc.core.JdbcTemplate.query(JdbcTemplate.java:478)
              at org.springframework.jdbc.core.JdbcTemplate.queryForObject(JdbcTemplate.java:488)
              at org.springframework.jdbc.core.JdbcTemplate.queryForObject(JdbcTemplate.java:494)
              at org.springframework.jdbc.core.JdbcTemplate.queryForInt(JdbcTemplate.java:507)
              at com.serotonin.m2m2.db.H2Proxy.tableExists(H2Proxy.java:215)
              at com.serotonin.m2m2.db.DatabaseProxy.newDatabaseCheck(DatabaseProxy.java:187)
              at com.serotonin.m2m2.db.DatabaseProxy.initialize(DatabaseProxy.java:103)
              at com.serotonin.m2m2.Lifecycle.databaseInitialize(Lifecycle.java:595)
              at com.serotonin.m2m2.Lifecycle.initialize(Lifecycle.java:261)
              at com.serotonin.m2m2.Main.main(Main.java:103)
              Caused by: org.h2.jdbc.JdbcSQLException: File corrupted while reading record: "index not found 93". Possible solution: use the recovery tool [90030-180]
              at org.h2.message.DbException.getJdbcSQLException(DbException.java:345)
              at org.h2.message.DbException.get(DbException.java:179)
              at org.h2.message.DbException.get(DbException.java:155)
              at org.h2.store.PageStore.getPage(PageStore.java:813)
              at org.h2.index.PageDataIndex.getPage(PageDataIndex.java:233)
              at org.h2.index.PageDataNode.freeRecursive(PageDataNode.java:272)
              at org.h2.index.PageDataIndex.removeAllRows(PageDataIndex.java:397)
              at org.h2.index.PageDataIndex.truncate(PageDataIndex.java:382)
              at org.h2.store.PageStore.removeOldTempIndexes(PageStore.java:397)
              at org.h2.store.PageStore.openExisting(PageStore.java:373)
              at org.h2.store.PageStore.open(PageStore.java:288)
              at org.h2.engine.Database.getPageStore(Database.java:2382)
              at org.h2.engine.Database.open(Database.java:663)
              at org.h2.engine.Database.openDatabase(Database.java:263)
              at org.h2.engine.Database.<init>(Database.java:257)
              at org.h2.engine.Engine.openSession(Engine.java:60)
              at org.h2.engine.Engine.openSession(Engine.java:167)
              at org.h2.engine.Engine.createSessionAndValidate(Engine.java:145)
              at org.h2.engine.Engine.createSession(Engine.java:128)
              at org.h2.engine.Engine.createSession(Engine.java:26)
              at org.h2.engine.SessionRemote.connectEmbeddedOrServer(SessionRemote.java:347)
              at org.h2.jdbc.JdbcConnection.<init>(JdbcConnection.java:108)
              at org.h2.jdbc.JdbcConnection.<init>(JdbcConnection.java:92)
              at org.h2.Driver.connect(Driver.java:72)
              at org.h2.jdbcx.JdbcDataSource.getJdbcConnection(JdbcDataSource.java:190)
              at org.h2.jdbcx.JdbcDataSource.getXAConnection(JdbcDataSource.java:353)
              at org.h2.jdbcx.JdbcDataSource.getPooledConnection(JdbcDataSource.java:385)
              at org.h2.jdbcx.JdbcConnectionPool.getConnectionNow(JdbcConnectionPool.java:227)
              at org.h2.jdbcx.JdbcConnectionPool.getConnection(JdbcConnectionPool.java:199)
              at org.springframework.jdbc.datasource.DataSourceUtils.doGetConnection(DataSourceUtils.java:111)
              at org.springframework.jdbc.datasource.DataSourceUtils.getConnection(DataSourceUtils.java:77)
              ... 12 more
              ERROR 2019-08-22 20:28:41,317 (com.serotonin.m2m2.Main.main:108) - Error during initialization
              ... 12 more
              The above is the error details i get when i run the command you mentioned. Also i tried to delete the databse, It cant be deleted completely. What kind of recovery tool they have for correcting this error?
              Any help is appreciated. Thanks
              • J Offline
                Jay1089
                I tried 2.8 inside the Mango but it couldn't run. It is still running the old version.
                • J Offline
                  Jay1089
                  MA_HOME is /opt/mango
                  ma-start: MA started with Process ID: 28182
                  INFO 2019-08-22 23:28:07,482 (com.serotonin.m2m2.Main.main:82) - Starting Mango 2.8.8 with Schema Version: 13
                  WARN 2019-08-22 23:28:07,677 (com.serotonin.m2m2.Main.loadModules:356) - Module loggingConsole: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,679 (com.serotonin.m2m2.Main.loadModules:356) - Module openv4j: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,682 (com.serotonin.m2m2.Main.loadModules:356) - Module pointLinks: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,684 (com.serotonin.m2m2.Main.loadModules:356) - Module persistent: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,687 (com.serotonin.m2m2.Main.loadModules:356) - Module http: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,690 (com.serotonin.m2m2.Main.loadModules:356) - Module meta: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,692 (com.serotonin.m2m2.Main.loadModules:356) - Module templateConfig: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,693 (com.serotonin.m2m2.Main.loadModules:356) - Module virtualDS: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,694 (com.serotonin.m2m2.Main.loadModules:356) - Module onewire: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,696 (com.serotonin.m2m2.Main.loadModules:356) - Module scheduledEvents: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,697 (com.serotonin.m2m2.Main.loadModules:356) - Module dashboards: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,698 (com.serotonin.m2m2.Main.loadModules:356) - Module mangoNoSqlDatabase: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,700 (com.serotonin.m2m2.Main.loadModules:356) - Module scripting: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,701 (com.serotonin.m2m2.Main.loadModules:356) - Module sstTheme: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,703 (com.serotonin.m2m2.Main.loadModules:356) - Module twilio: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,712 (com.serotonin.m2m2.Main.loadModules:356) - Module log4JReset: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,714 (com.serotonin.m2m2.Main.loadModules:356) - Module mangoApi: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,715 (com.serotonin.m2m2.Main.loadModules:356) - Module mbus: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,716 (com.serotonin.m2m2.Main.loadModules:356) - Module jspViews: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,718 (com.serotonin.m2m2.Main.loadModules:356) - Module internal: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,719 (com.serotonin.m2m2.Main.loadModules:356) - Module jmxds: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,720 (com.serotonin.m2m2.Main.loadModules:356) - Module sqlds: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,723 (com.serotonin.m2m2.Main.loadModules:356) - Module pop3: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,724 (com.serotonin.m2m2.Main.loadModules:356) - Module sstGlobalScripts: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,726 (com.serotonin.m2m2.Main.loadModules:356) - Module bonjourBroadcaster: this module requires a core version of 2.4, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,728 (com.serotonin.m2m2.Main.loadModules:356) - Module modbus: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,729 (com.serotonin.m2m2.Main.loadModules:356) - Module serial: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,730 (com.serotonin.m2m2.Main.loadModules:356) - Module opcda: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,732 (com.serotonin.m2m2.Main.loadModules:356) - Module graphicalViews: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,733 (com.serotonin.m2m2.Main.loadModules:356) - Module dataFile: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,742 (com.serotonin.m2m2.Main.loadModules:356) - Module dglux: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,744 (com.serotonin.m2m2.Main.loadModules:356) - Module dataImport: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,745 (com.serotonin.m2m2.Main.loadModules:356) - Module sstGraphics: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,747 (com.serotonin.m2m2.Main.loadModules:356) - Module snmp: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,748 (com.serotonin.m2m2.Main.loadModules:356) - Module pid: this module requires a core version of 2.4, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,750 (com.serotonin.m2m2.Main.loadModules:356) - Module reports: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,751 (com.serotonin.m2m2.Main.loadModules:356) - Module maintenanceEvents: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,753 (com.serotonin.m2m2.Main.loadModules:356) - Module galil: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,754 (com.serotonin.m2m2.Main.loadModules:356) - Module watchlists: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,756 (com.serotonin.m2m2.Main.loadModules:356) - Module sqlConsole: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,757 (com.serotonin.m2m2.Main.loadModules:356) - Module log4jDS: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,758 (com.serotonin.m2m2.Main.loadModules:356) - Module controlcore: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,760 (com.serotonin.m2m2.Main.loadModules:356) - Module BACnet: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,761 (com.serotonin.m2m2.Main.loadModules:356) - Module vmstat: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,763 (com.serotonin.m2m2.Main.loadModules:356) - Module dnp3: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,764 (com.serotonin.m2m2.Main.loadModules:356) - Module pachube: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  WARN 2019-08-22 23:28:07,765 (com.serotonin.m2m2.Main.loadModules:356) - Module asciiFile: this module requires a core version of 2.5, which does not match the current core version of 2.8.8. Module not loaded.
                  INFO 2019-08-22 23:28:08,011 (com.serotonin.m2m2.Main.loadModules:416) - Loading module 'abpccc', v1.0.4 by Deltamation Software
                  INFO 2019-08-22 23:28:08,091 (com.serotonin.m2m2.Main.loadModules:416) - Loading module 'abeip', v1.0.6 by Deltamation Software
                  INFO 2019-08-22 23:28:08,103 (com.serotonin.m2m2.Main.loadModules:416) - Loading module 'SystemManager', v1.0.0 by (unknown vendor)
                  INFO 2019-08-22 23:28:08,110 (com.serotonin.m2m2.util.DocumentationManifest.parseManifestFile:60) - Documentation manifest file not found: /opt/mango/web/modules/SystemManager/web/dox/manifest.xml
                  INFO 2019-08-22 23:28:08,257 (com.serotonin.m2m2.Lifecycle.initialize:216) - Initializing Spring Object Mapper
                  ERROR 2019-08-22 23:28:09,218 (com.serotonin.m2m2.Main.main:119) - Error during initialization
                  java.lang.RuntimeException: java.net.BindException: Address already in use
                  at com.serotonin.m2m2.Lifecycle.webServerInitialize(Lifecycle.java:810)
                  at com.serotonin.m2m2.Lifecycle.initialize(Lifecycle.java:223)
                  at com.serotonin.m2m2.Main.main(Main.java:115)
                  Caused by: java.net.BindException: Address already in use
                  at sun.nio.ch.Net.bind0(Native Method)
                  at sun.nio.ch.Net.bind(Net.java:414)
                  at sun.nio.ch.Net.bind(Net.java:406)
                  at sun.nio.ch.ServerSocketChannelImpl.bind(ServerSocketChannelImpl.java:214)
                  at sun.nio.ch.ServerSocketAdaptor.bind(ServerSocketAdaptor.java:74)
                  at org.eclipse.jetty.server.ServerConnector.open(ServerConnector.java:321)
                  at org.eclipse.jetty.server.AbstractNetworkConnector.doStart(AbstractNetworkConnector.java:80)
                  at org.eclipse.jetty.server.ServerConnector.doStart(ServerConnector.java:236)
                  at org.eclipse.jetty.util.component.AbstractLifeCycle.start(AbstractLifeCycle.java:68)
                  at org.eclipse.jetty.server.Server.doStart(Server.java:366)
                  at com.serotonin.m2m2.Lifecycle.webServerInitialize(Lifecycle.java:807)
                  ... 2 more
                  INFO 2019-08-22 23:28:09,224 (com.serotonin.m2m2.Lifecycle.terminate:353) - Mango Lifecycle terminating...
                  ERROR 2019-08-22 23:28:09,238 (com.serotonin.m2m2.Lifecycle.terminate:425) - com.serotonin.provider.InputStreamEPollProvider
                  ERROR 2019-08-22 23:28:09,240 (com.serotonin.m2m2.Lifecycle.terminate:433) - com.serotonin.provider.ProcessEPollProvider
                  INFO 2019-08-22 23:28:09,240 (com.serotonin.m2m2.Lifecycle.terminate:453) - Mango Lifecycle terminated.
                  ma-start: no restart flag found, not restarting MA
                  ma-start: MA done
                  Updated to 2.8 version. but still can't open the Mango normally. its stuck in 40% loading
                    phildunlap
                    To the stack trace involving,
                    I would advise restoring a database backup. See this these resources for ways of doing that:
                    https://help.infiniteautomation.com/how-to-restore-a-h2-database-backup
                    https://forum.infiniteautomation.com/topic/2748/how-to-restore-a-database-backup
                    This usually means that Mango is already running on that port, but it could also mean that another application is running and has bound that port. The solution if Mango is already running is to access the Mango that is running, and if another application has bound it you can change the port Mango binds to in the Mango/overrides/properties/env.properties file.
                    • J Offline
                      Jay1089
                      My help is for MangoES hardware. I think you are talking about Mango software running on a System
                      • J Offline
                        Jay1089
                        To add to the problems, I had installed a module MySQL Database server and now the MangoES refusing to connect through IP. any alternatives to retrirvr back the last change? i can ping, but no connection can be established through Webmin or through browser
                        • MattFoxM Offline
                          MattFox
                          Do you have a copy of your env.properties on hand?
                          If so can you please paste it between some code tags???
                          Follow Phil's instructions as above, also run mango from the bash console.
                          Secondly Phil also added that you may have an instance of mango already running in the background.
                          try
                          pas aux | grep mango > mangoinstances.txt
                          Something should be outputted into that file to show something is running.
                          I also suggest you stop making amendments and changes to your system, it's harder to follow and diagnose if you do that.
                          Fox
                          Do not follow where the path may lead; go instead where there is no path.
                          And leave a trail - Muriel Strode
                          • J Offline
                            Jay1089
                            Thanks Fox for responding. But now I don't have any access to the MangoES. As I said before i can ping, but can't use Webmin to get into MangoES hardware. Any alternatives to access webmin again?
                            Connection refused through Network
                            • MattFoxM Offline
                              MattFox
                              You mean you're unable to use putty and SSH into the unit?
                              Just because webmin is out, SSH should still be running...
                              • J Offline
                                Jay1089
                                Yes even putty cant get in. Connection refused
                                • MattFoxM Offline
                                  MattFox
                                  Assuming you're running a windows box, let's see if it's even on the network.
                                  Get yourself angry ip scanner or similar to scan the network.
                                  If there's nothing, I wonder if your network card gave up the ghost...
                                  • J Offline
                                    Jay1089
                                    I have the advanced IP scanner, and the MangoES is available. Only it refuses to accept any connection. Also before i could access the network foler of Mango, But now its invisible and there is nothing showing up in the network.
                                    • MattFoxM Offline
                                      MattFox
                                      Sounds like a power cycle is in order. Give it a good ol' hard reset. It's an old unit so I wouldn't rule out hardware failing. I've had a few V2's die on me, and one of the traits they shared before dying completely was the networking part of the system calling it a day.
                                      • J Offline
                                        Jay1089
                                        Just switching off the power for long time and switch it back on?
                                        MattFoxM 1 Reply Last reply Reply Quote 0
                                        • MattFoxM Offline
                                          MattFox @Jay1089
                                          @jay1089 Yep, count to 30 then fire it back up, perhaps monitor the LED's on the case - I assume here it's similar to a V2 with an aluminium cast case with 4 LEDs on the front.
                                          • J Offline
                                            Jay1089
                                            Yes four LED up front. One green and other blinks when network connected. Other two doesn't lit up at all
                                            Hello! It looks like you're interested in this conversation, but you don't have an account yet.
                                            Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.