      khuang @MattFox
      @mattfox What do you mean by setting the normal as 0? Do you mean creating an inactive action and scripting return 0?
      Is this what you mean:
        No set inactive action to none. From what I gather you've got the event to fire on change.. What's the logic you're after? if something goes high fire this script? Need more info to diagnose how to set an inactive region.
        EDIT: Just read above. Get the point in context and check the value,
        if ( point.last(1,0)[0].value == 0 && point.value == 1 )
         return true; //fire handler
        return false; //don't fire handler
        That way it checks if the point has changed the right way and then only returns true for that; otherwise it returns false;
        Ideally just set a high limit and set it to 1. The event will fire on 1 or above and return to normal on zero.
        K 1 Reply Last reply Reply Quote 1
          Or, if the source point is binary, use a state detector on true and like Fox said, no inactive action.
          • K Offline
            khuang @MattFox
            @mattfox said in Process Event handler to fire external script:
            The logic that I am after is that it fires my script but I do not want the scripts to continuously fire.
            Right now there are two problems:
            1. the set point handler is triggering all the time (the reason why I believe it is triggering all the time is because my set point cannot be set back to 0) and setting my ssh data point to true all the time. It should execute once and be done. Right now the data point is stuck at 1, and I am unable to change it back to 0.
            2. my script which is in the set command of the ssh data point still is not executing, which is the purpose behind me pursuing ssh datasources and data points
            EDIT: I recreated the SSH datapoint, and set point handler and I got the set command to fire but at a 6 second delay. It also looks like the entire MangoES box is lagging at the same rate.
            EDIT2: After restarting the MangoES box and deactivating several other data sources that have various polling and triggers associated with it, the CPU reduced to 360% (8 cores). Before the CPU was being hit too hard so the script was not running correctly.
              For your virtual datapoint, if it's set to logging all it'll continuously update/trigger the event.
              Set logging to update on point value change only as you only need it to work when it changes between 1 and 0, not 1 and 1.
                It would depend on whatever event detector has been placed on the point.
                  MattFox @phildunlap
                  @phildunlap Also true...
                  • K Offline
                    khuang
                    Currently for the event detector I have it as "when the state is one". So I guess "when the state is one" means 0 to 1 and 1 to 1?
                    What if I created another event detector for "when the state is zero" and kill the process that way?
                      Let's see a screenshot of your datapoint settings.
                      From what I gather, you have an SSH source which runs a python script which then sets the value of the binary datapoint. If that point is set to one, fire an event handler.
                      Does that sound right?
                      • K Offline
                        khuang
                        Yes, that is correct.
                        Here is a screenshot of my virtual datapoint which serves as the source for firing the event handler:
                        I manually set the virtual datapoint so it only goes from 0 to 1 or 1 to 0, and not 0 to 0 or 1 to 1.
                        This is my SSH datapoint which gets set by the event handler. I have it get scripted to return true because I don't care what the value of this data point is but just that the set command gets fired:
                          Can you post the JSON for the event detector / source point? State event detectors will not retrigger the active event handler from repeated samples of the same state, but would retrigger the event if the point or data source were restarted (i.e. saved, Mango restarts, etc)
                            Actually yes, the JSON would be better there is still a lot of information missing.
                            • K Offline
                              khuang
                              Yes, here is the JSON of the event handler:
                                 "eventHandlers":[
                                       "xid":"EH_caaac4a3-6ff5-4046-8eaa-0ff5be6a6370",
                                       "alias":"",
                                       "handlerType":"EMAIL",
                                       "eventTypes":[
                                             "sourceType":"DATA_SOURCE",
                                             "XID":"DS_2b8b5316-3bd1-4b4e-82d2-c5f00dbd4ba4",
                                             "dataSourceEventType":"SCRIPT_ERROR"
                                       "activeRecipients":[
                                             "recipientType":"ADDRESS",
                                             "address":"khuang@cityliftparking.com"
                                       "sendEscalation":false,
                                       "sendInactive":false,
                                       "includeSystemInformation":true,
                                       "includePointValueCount":10,
                                       "includeLogfile":true,
                                       "customTemplate":"",
                                       "additionalContext":[
                                       "script":"",
                                       "scriptPermissions":{
                                          "scriptDataPointReadPermission":"superadmin, user",
                                          "scriptDataPointSetPermission":"superadmin, user",
                                          "scriptDataSourcePermission":"superadmin, user"
                                       "disabled":false
                                       "xid":"EH_2d361442-9b2e-40ff-82bd-3f85c42d3480",
                                       "alias":"",
                                       "handlerType":"SET_POINT",
                                       "eventTypes":[
                                             "sourceType":"DATA_POINT",
                                             "dataPointXID":"DP_d8a89826-e771-4760-ac46-9064a5e3b3d0",
                                             "detectorXID":"ED_80c9adf7-f1ad-4058-a60a-05a58f53ecf6"
                                       "targetPointId":"DP_41011e72-6228-4ae6-a4e3-6fdce7c45ec7",
                                       "activeAction":"SCRIPT_VALUE",
                                       "activeScript":"return true;",
                                       "inactiveAction":"NONE",
                                          "scriptDataPointReadPermission":"superadmin",
                                          "scriptDataPointSetPermission":"superadmin",
                                          "scriptDataSourcePermission":"superadmin"
                                       "disabled":false
                              @phildunlap You said that the script could get retriggered if I restarted the data source and data point, which is what I was doing. So maybe that was the cause. I was restarting the source and point because I was unable to set the ssh data point in the watch list.
                              EDIT: I think I see what the problem might have been (with the lagging). When I restart the SSH data source/point, the event handler fires again and launches my script in another session and it does for each time I restart the source/point. And eventually it hoses up my entire system.
                                @phildunlap said in Process Event handler to fire external script:
                                But no matter, the restarting of the point or source was likely the cause of resending. So, now the issue is that even using SSH you're experiencing those issues with python modules being undefined? What was that post about the Hello World text and the SSH invoking the script about? Or, is everything working now and it was melting from the multiple runs of the script?
                                • K Offline
                                  khuang @phildunlap
                                  @phildunlap It was the melting from the multiple runs of the script which made it appear that the script was not working. Right now everything is working. The command in the 'set command' of my ssh datapoint is firing when the state changes to true for my source whereas it the same command was giving errors in the process event handler so the lesson learned for me is to use a set point event handler when my script uses relative paths and environmental variables.
                                  Only problem now is I need to be careful because each time the source goes to 1, it starts up another run of my script and with 3 of those, my system crashes. Now I just need a way to kill the process when the state changes to false.
                                    It's going to be related to event detector and point settings. Export the JSON for the point, we cannot see how you've got the event detector configured and point settings configured
                                      You can add another virtual point into the context for the set point handler, and set a value to it in the script before returning. Then in the script you do something like this,
                                      if( lastSet.time >= CONTEXT.getRuntime() - 15000 ) //15 seconds
                                        return UNCHANGED;
                                      lastSet.set(!lastSet.value); //we care about times, not values, so alternate a binary
                                      return true;
                                      • K Offline
                                        khuang
                                        @MattFox This is the SSH data point:
                                                "xid":"DP_41011e72-6228-4ae6-a4e3-6fdce7c45ec7",
                                                "name":"Trigger",
                                                "enabled":true,
                                                "loggingType":"ON_CHANGE",
                                                "purgeType":"YEARS",
                                                "pointLocator":{
                                                   "dataType":"ALPHANUMERIC",
                                                   "setCommand":"\/home\/mango\/detect-start.sh",
                                                   "queryable":false,
                                                   "settable":true
                                                "eventDetectors":[
                                                "plotType":"STEP",
                                                "rollup":"NONE",
                                                "unit":"",
                                                "templateXid":"Alphanumeric_Default",
                                                "simplifyType":"NONE",
                                                "chartColour":"red",
                                                "chartRenderer":{
                                                   "type":"TABLE",
                                                   "limit":10
                                                "dataSourceXid":"DS_40cb68b0-350f-4b16-b54b-5bc359cf8241",
                                                "defaultCacheSize":1,
                                                "deviceName":"MangoES",
                                                "discardExtremeValues":false,
                                                "intervalLoggingPeriod":15,
                                                "purgeOverride":false,
                                                "purgePeriod":1,
                                                "readPermission":"",
                                                "setPermission":"",
                                                "tags":{
                                                "textRenderer":{
                                                   "type":"PLAIN",
                                                   "useUnitAsSuffix":true,
                                                   "unit":"",
                                                   "renderedUnit":"",
                                                   "suffix":""
                                                "tolerance":0.0
                                        And here's the virtual data point that I use to trigger:
                                                 "xid":"DP_d8a89826-e771-4760-ac46-9064a5e3b3d0",
                                                 "name":"doorIsOpen",
                                                 "enabled":true,
                                                 "pointLocator":{
                                                    "dataType":"BINARY",
                                                    "changeType":{
                                                       "type":"NO_CHANGE",
                                                       "startValue":"True"
                                                    "settable":true
                                                 "eventDetectors":[
                                                       "type":"BINARY_STATE",
                                                       "xid":"ED_80c9adf7-f1ad-4058-a60a-05a58f53ecf6",
                                                       "name":"",
                                                       "alarmLevel":"NONE",
                                                       "durationType":"SECONDS",
                                                       "duration":0,
                                                       "state":true
                                                       "xid":"ED_915a14f9-17da-4885-9c22-a53648617c04",
                                                       "name":"",
                                                       "duration":0,
                                                       "state":false
                                                 "plotType":"STEP",
                                                 "rollup":"NONE",
                                                 "unit":"",
                                                 "templateXid":"Binary_Default",
                                                 "chartColour":"blue",
                                                 "chartRenderer":{
                                                    "type":"TABLE",
                                                    "limit":10
                                                 "dataSourceXid":"DS_5d06b8ba-c91b-4c93-b594-92c5009ec67e",
                                                 "deviceName":"Virtual Data Source",
                                                 "purgePeriod":1,
                                                 "setPermission":"",
                                                 "tags":{
                                                 "textRenderer":{
                                                    "type":"BINARY",
                                                    "oneColour":"#ff0000",
                                                    "oneLabel":"one",
                                                    "zeroColour":"blue",
                                                    "zeroLabel":"zero"
                                                 "tolerance":0.0
                                        @phildunlap What is lastSet in this case? It says lastSet is undeclared.
                                          That's the variable name I gave to a binary virtual point that would be in the Set point handler's "Additional Context."
                                          I guess you could in theory have issues then where you wanted the script to be invoked more than once in a fifteen second interval, but at that point you're really on the hook for specifying the logic you need very clearly. It may be easier for your script to use a lock file or some such.
                                          • K Offline
                                            khuang @phildunlap
                                            @phildunlap Ok, I see what you mean. So if my source point has not changed for 15 seconds, I can treat it as unchanged and do something off of that.
                                            For now, I just created another data point event detector for the source point to detect a state of 0. And when the state is 0, I run a process command that kills the python script. It seems to get the job done, and now when I run "top" I can see the python process going away and back as I toggle the source point.
                                            Thanks for the help guys!