    How to clean a very large H2 Database
    27 Posts 2 Posters 15.9k Views 2 Watching
      Hmm. That's definitely why I always say,
      Move your existing Mango/databases/mah2.h2.db file elsewhere for safe keeping
      You should be able to start up on that database. If your events table is missing after a restore, it would strike that either the backup or restore process was not allowed to complete. You could purge your events and userEvents tables if they're a source of some of the size or slowdown using the 'Purge all events' button in the screenshot of purge settings you posted.
      • E Offline
        etantonio
        I don't know where is the problem, really often I purge all events, expecially before a backup. In any case I still turn back to original database becoming each day bigger.
          You could try converting this instance over to MySQL. There was an issue with H2 databases growing that didn't get a true resolution until the 3.4 series with the persistent publisher, for instance. MySQL does not have the same issue with binary data sections not getting reused or freed when updated.
          • E Offline
            etantonio
            I'm trying to convert it to mysql,
            so I've installed MySQL 8, created a schema named "mango"
            then in my env.properties I've now:
            db.type=mysql
            db.url=jdbc:mysql://localhost/mango
            db.username=solergy
            db.password=secret
            db.mysqldump=
            db.mysql=
            convert.db.type=h2
            convert.db.url=jdbc:h2:${ma.home}/databases/mah2
            convert.db.username=
            convert.db.password=
            but the result is that:
            INFO 2018-10-03 18:22:00,037 (com.serotonin.m2m2.db.BasePooledProxy.initializeI
            mpl:36) - Initializing pooled connection manager
            FATAL 2018-10-03 18:22:00,792 (com.serotonin.m2m2.db.DatabaseProxy.initialize:19
            0) - Unable to connect to database of type MYSQL
            org.springframework.jdbc.CannotGetJdbcConnectionException: Could not get JDBC Co
            nnection; nested exception is org.apache.commons.dbcp.SQLNestedException: Cannot
            create PoolableConnectionFactory (Could not create connection to database serve
            r.)
            at org.springframework.jdbc.datasource.DataSourceUtils.getConnection(Dat
            aSourceUtils.java:80)
            at org.springframework.jdbc.core.JdbcTemplate.execute(JdbcTemplate.java:
            615)
            Thanks for your help
            Antonio
              I would it'd be the db.url that would be going wrong. Two things could be at issue,
              1. It's not interpreting the absence of port as the default port, resolve this by explicitly adding a :3306 like jdbc:mysql://localhost:3306/mango
              2. localhost is not resolving to an address that comports with the bind address in your MySQL configuration (like ::1 if it's not enabling IPv6). Resolve this by adjusting the bind address in the MySQL configuration, or by trying the explicit local address instead of the hostname, like jdbc:mysql://127.0.0.1:3306/mango
              But a lot of error output is missing in your post, such as the 'caused by' section in the stack track. It could be that you do not have the users credentials or privileges correct. Consult this thread for instructions on creating the MySQL database, a user, and granting privileges on that database to that user: https://forum.infiniteautomation.com/topic/3559/convert-from-h2-to-mysql-database-guidelines
              • E Offline
                etantonio
                according to your suggestion now the env.properties is the following:
                db.type=mysql
                db.url=jdbc:mysql://127.0.0.1:3306/mango
                db.username=solergy
                db.password=secret
                db.mysqldump=
                db.mysql=
                convert.db.type=h2
                the mango database for user solergy is created, granted and up and running:
                but still mango doesn't start:
                INFO  2018-10-04 10:27:16,771 (com.serotonin.m2m2.db.BasePooledProxy.initializeI
                FATAL 2018-10-04 10:27:18,016 (com.serotonin.m2m2.db.DatabaseProxy.initialize:19
                r.)
                615)
                        at org.springframework.jdbc.core.JdbcTemplate.query(JdbcTemplate.java:68
                0)
                        at org.springframework.jdbc.core.JdbcTemplate.query(JdbcTemplate.java:71
                2)
                        at org.springframework.jdbc.core.JdbcTemplate.query(JdbcTemplate.java:72
                2)
                        at com.serotonin.db.spring.ExtendedJdbcTemplate.queryForObject(ExtendedJ
                dbcTemplate.java:39)
                dbcTemplate.java:63)
                        at com.serotonin.db.DaoUtils.queryForObject(DaoUtils.java:336)
                        at com.serotonin.m2m2.db.dao.SystemSettingsDao.getValue(SystemSettingsDa
                o.java:158)
                        at com.serotonin.m2m2.db.dao.SystemSettingsDao.getIntValue(SystemSetting
                sDao.java:178)
                        at com.serotonin.m2m2.db.upgrade.DBUpgrade.checkUpgrade(DBUpgrade.java:5
                1)
                        at com.serotonin.m2m2.db.upgrade.DBUpgrade.checkUpgrade(DBUpgrade.java:3
                4)
                        at com.serotonin.m2m2.db.DatabaseProxy.initialize(DatabaseProxy.java:180
                        at com.serotonin.m2m2.Lifecycle.databaseInitialize(Lifecycle.java:609)
                        at com.serotonin.m2m2.Lifecycle.initialize(Lifecycle.java:287)
                        at com.serotonin.m2m2.Main.main(Main.java:115)
                Caused by: org.apache.commons.dbcp.SQLNestedException: Cannot create PoolableCon
                nectionFactory (Could not create connection to database server.)
                        at org.apache.commons.dbcp.BasicDataSource.createPoolableConnectionFacto
                ry(BasicDataSource.java:1549)
                        at org.apache.commons.dbcp.BasicDataSource.createDataSource(BasicDataSou
                rce.java:1388)
                        at org.apache.commons.dbcp.BasicDataSource.getConnection(BasicDataSource
                .java:1044)
                        at org.springframework.jdbc.datasource.DataSourceUtils.doGetConnection(D
                ataSourceUtils.java:111)
                aSourceUtils.java:77)
                        ... 15 more
                Caused by: com.mysql.jdbc.exceptions.jdbc4.MySQLNonTransientConnectionException:
                        at sun.reflect.NativeConstructorAccessorImpl.newInstance(Unknown Source)
                        at sun.reflect.DelegatingConstructorAccessorImpl.newInstance(Unknown Sou
                rce)
                        at java.lang.reflect.Constructor.newInstance(Unknown Source)
                        at com.mysql.jdbc.Util.handleNewInstance(Util.java:411)
                        at com.mysql.jdbc.Util.getInstance(Util.java:386)
                        at com.mysql.jdbc.SQLError.createSQLException(SQLError.java:1015)
                        at com.mysql.jdbc.SQLError.createSQLException(SQLError.java:989)
                        at com.mysql.jdbc.SQLError.createSQLException(SQLError.java:975)
                        at com.mysql.jdbc.SQLError.createSQLException(SQLError.java:920)
                        at com.mysql.jdbc.ConnectionImpl.connectOneTryOnly(ConnectionImpl.java:2
                568)
                        at com.mysql.jdbc.ConnectionImpl.createNewIO(ConnectionImpl.java:2304)
                        at com.mysql.jdbc.ConnectionImpl.<init>(ConnectionImpl.java:834)
                        at com.mysql.jdbc.JDBC4Connection.<init>(JDBC4Connection.java:47)
                rce)
                        at com.mysql.jdbc.ConnectionImpl.getInstance(ConnectionImpl.java:416)
                        at com.mysql.jdbc.NonRegisteringDriver.connect(NonRegisteringDriver.java
                :346)
                        at org.apache.commons.dbcp.DriverConnectionFactory.createConnection(Driv
                erConnectionFactory.java:38)
                        at org.apache.commons.dbcp.PoolableConnectionFactory.makeObject(Poolable
                ConnectionFactory.java:582)
                        at org.apache.commons.dbcp.BasicDataSource.validateConnectionFactory(Bas
                icDataSource.java:1556)
                ry(BasicDataSource.java:1545)
                        ... 19 more
                Caused by: java.lang.NullPointerException
                        at com.mysql.jdbc.ConnectionImpl.getServerCharacterEncoding(ConnectionIm
                pl.java:3279)
                        at com.mysql.jdbc.MysqlIO.sendConnectionAttributes(MysqlIO.java:1940)
                        at com.mysql.jdbc.MysqlIO.proceedHandshakeWithPluggableAuthentication(My
                sqlIO.java:1866)
                        at com.mysql.jdbc.MysqlIO.doHandshake(MysqlIO.java:1252)
                        at com.mysql.jdbc.ConnectionImpl.coreConnect(ConnectionImpl.java:2486)
                519)
                        ... 33 more
                ERROR 2018-10-04 10:27:18,400 (com.serotonin.m2m2.Main.main:119) - Error during
                initialization
                r.)
                615)
                0)
                2)
                2)
                o.java:158)
                sDao.java:178)
                1)
                4)
                rce.java:1388)
                .java:1044)
                        ... 15 more
                rce)
                568)
                rce)
                :346)
                        ... 19 more
                pl.java:3279)
                sqlIO.java:1866)
                519)
                        ... 33 more
                INFO  2018-10-04 10:27:18,448 (com.serotonin.m2m2.Lifecycle.terminate:353) - Man
                go Lifecycle terminating...
                Exception in thread "high-pool-1-thread-1" java.lang.NullPointerException
                        at com.serotonin.m2m2.CoreLicenseDefinition$2.run(CoreLicenseDefinition.
                java:149)
                        at com.serotonin.timer.sync.Synchronizer$TaskWrapper.run(Synchronizer.ja
                va:155)
                        at java.util.concurrent.ThreadPoolExecutor.runWorker(Unknown Source)
                        at java.util.concurrent.ThreadPoolExecutor$Worker.run(Unknown Source)
                INFO  2018-10-04 10:27:18,625 (com.serotonin.m2m2.db.BasePooledProxy.terminateIm
                pl:110) - Stopping database
                INFO  2018-10-04 10:27:18,634 (com.serotonin.m2m2.Lifecycle.terminate:453) - Man
                go Lifecycle terminated.
                  Did you perchance change the db.stream property to true ?
                  I don't believe we've done much testing against MySQL 8 (thanks for posting the version information!), so it's possible there are issues related to that. You could try and older version and see if that works out of the box. I know 5.5 has been used a great deal.
                  • E Offline
                    etantonio
                    Hy,
                    db.stream is unchanged, this is remaining properties for db on env.properties:
                    db.forceUseIndex=true
                    db.fetchSize=-1
                    db.stream=false
                    maybe I've to choose a certain character encoding in mysql?
                    pl.java:3279)
                      No, I wouldn't think so. It's never come up in the past, but I think few people were using the MySQL server version released last April and they may be new issues. I did search the error a little and find something in the code that may have something to do with it, but I do intend to look into this more and try to run on MySQL 8.
                        I installed MySQL server 8 on my Windows machine and found I could convert an H2 database without issue. I also tried telling Java that it was in Italy (in case locale was affecting the getServerCharacterEncoding method) but it still converted without issue.
                        This is done for you in the MySQLProxy class, it modifies the db.url for UTF-8:
                        https://github.com/infiniteautomation/ma-core-public/blob/main/Core/src/com/serotonin/m2m2/db/MySQLProxy.java#L28
                        A suggestion I saw is to try the latest JDBC. This is a 2.8 system? I would guess you have a very outdated Mango/lib/mysql-connector-java-x.y.z.jar file. You could try the version bundled with the latest Mango 3, or you could download the latest MySQL jdbc jar and replace the outdated with the new. You can download the latest here: https://dev.mysql.com/downloads/connector/j/5.1.html
                        • E Offline
                          etantonio
                          Ok,
                          after driver change, installation is started but after a long while during migration I had this error,
                          can I do something to avoid it and continue migration?
                          Using Java at java
                          INFO  2018-10-05 08:57:59,936 (com.serotonin.m2m2.Main.main:82) - Starting Mango
                           2.8.4 with Schema Version: 13
                          INFO  2018-10-05 08:58:01,596 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'asciiFile', v1.3.0 by Infinite Automation
                          INFO  2018-10-05 08:58:01,656 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'BACnet', v2.3.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:01,666 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'controlcore', v1.2.0 by Infinite Automation
                          INFO  2018-10-05 08:58:01,676 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'dashboards', v3.3.0 by Infinite Automation Systems Inc.
                          INFO  2018-10-05 08:58:01,826 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'dataFile', v1.2.0 by Infinite Automation
                          INFO  2018-10-05 08:58:01,846 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'dataImport', v1.5.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:01,856 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'dataPointDetailsView', v1.1.0 by Infinite Automation
                          INFO  2018-10-05 08:58:01,866 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'dnp3', v1.7.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:01,876 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'egauge', v1.2.0 by Infinite Automation
                          INFO  2018-10-05 08:58:01,886 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'excelReports', v1.1.1 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,006 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'graphicalViews', v1.7.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,316 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'http', v1.6.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,366 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'internal', v1.6.1 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,386 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'log4jDS', v1.2.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,396 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'log4JReset', v1.2.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,406 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'loggingConsole', v1.2.0 by Infinite Automation
                          INFO  2018-10-05 08:58:02,426 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'maintenanceEvents', v1.6.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,436 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'mangoApi', v1.2.0 by Infinite Automation
                          INFO  2018-10-05 08:58:02,446 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'mbus', v1.2.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,456 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'meta', v2.3.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,476 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'modbus', v1.7.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,536 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'onewire', v1.6.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,606 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'opcda', v1.7.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,616 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'pakbus', v1.1.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,676 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'persistent', v1.7.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,706 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'pointLinks', v1.6.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,726 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'pop3', v1.6.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,736 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'reports', v2.3.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,796 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'scheduledEvents', v1.6.0 by Infinite Automation
                          INFO  2018-10-05 08:58:02,886 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'scripting', v1.2.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,906 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'serial', v1.3.0 by Infinite Automation
                          INFO  2018-10-05 08:58:02,926 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'snmp', v1.6.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,966 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'sqlConsole', v1.6.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,976 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'sqlds', v1.7.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:02,996 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'ssh', v1.2.0 by Infinite Automation
                          INFO  2018-10-05 08:58:03,006 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'sstGlobalScripts', v1.6.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:03,016 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'sstGraphics', v1.2.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:03,056 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'sstTheme', v1.2.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:03,066 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'TCPIP', v1.2.0 by Infinite Automation
                          INFO  2018-10-05 08:58:03,076 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'templateConfig', v1.1.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:03,106 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'twilio', v1.2.0 by Infinite Automation
                          INFO  2018-10-05 08:58:03,116 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'virtualDS', v1.6.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:03,126 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'vmstat', v1.6.0 by Infinite Automation Software
                          INFO  2018-10-05 08:58:03,136 (com.serotonin.m2m2.Main.loadModules:416) - Loadin
                          g module 'watchlists', v1.8.0 by Infinite Automation Software
                          WARN  2018-10-05 08:58:05,118 (com.serotonin.m2m2.Main.loadModules:623) - Unused
                           classes entry: com.infiniteautomation.mango.pakbus.dwr.PakBusEditDwr
                          INFO  2018-10-05 08:58:05,368 (com.serotonin.m2m2.Lifecycle.initialize:216) - In
                          itializing Spring Object Mapper
                          INFO  2018-10-05 08:58:08,428 (com.serotonin.m2m2.Lifecycle.loadLic:471) - Check
                          ing license...
                          INFO  2018-10-05 08:58:09,298 (com.serotonin.m2m2.db.BasePooledProxy.initializeI
                          Fri Oct 05 08:58:10 CEST 2018 WARN: Establishing SSL connection without server's
                           identity verification is not recommended. According to MySQL 5.5.45+, 5.6.26+ a
                          nd 5.7.6+ requirements SSL connection must be established by default if explicit
                           option isn't set. For compliance with existing applications not using SSL the v
                          erifyServerCertificate property is set to 'false'. You need either to explicitly
                           disable SSL by setting useSSL=false, or set useSSL=true and provide truststore
                          for server certificate verification.
                          Fri Oct 05 08:58:11 CEST 2018 WARN: Establishing SSL connection without server's
                          INFO  2018-10-05 09:02:03,183 (com.serotonin.m2m2.db.H2Proxy.initializeImpl:42)
                          - Initializing H2 connection manager
                          WARN  2018-10-05 09:02:03,718 (com.serotonin.m2m2.db.DBConvert.execute:41) - Run
                          ning database conversion from H2 to MYSQL
                          WARN  2018-10-05 09:02:08,243 (com.serotonin.m2m2.db.DBConvert.copyTable:87) -
                          --> Converting table systemSettings...
                          WARN  2018-10-05 09:02:08,843 (com.serotonin.m2m2.db.DBConvert.copyTable:136) -
                           --> Finished converting table systemSettings. 78 records copied.
                          WARN  2018-10-05 09:02:08,844 (com.serotonin.m2m2.db.DBConvert.copyTable:87) -
                          --> Converting table users...
                          WARN  2018-10-05 09:02:09,074 (com.serotonin.m2m2.db.DBConvert.copyTable:136) -
                           --> Finished converting table users. 5 records copied.
                          WARN  2018-10-05 09:02:09,080 (com.serotonin.m2m2.db.DBConvert.copyTable:87) -
                          --> Converting table userComments...
                          WARN  2018-10-05 09:02:09,089 (com.serotonin.m2m2.db.DBConvert.copyTable:136) -
                           --> Finished converting table userComments. 0 records copied.
                          WARN  2018-10-05 09:02:09,095 (com.serotonin.m2m2.db.DBConvert.copyTable:87) -
                          --> Converting table mailingLists...
                          WARN  2018-10-05 09:02:09,427 (com.serotonin.m2m2.db.DBConvert.copyTable:136) -
                           --> Finished converting table mailingLists. 1 records copied.
                          WARN  2018-10-05 09:02:09,434 (com.serotonin.m2m2.db.DBConvert.copyTable:87) -
                          --> Converting table mailingListInactive...
                          WARN  2018-10-05 09:02:09,442 (com.serotonin.m2m2.db.DBConvert.copyTable:136) -
                           --> Finished converting table mailingListInactive. 0 records copied.
                          WARN  2018-10-05 09:02:09,445 (com.serotonin.m2m2.db.DBConvert.copyTable:87) -
                          --> Converting table mailingListMembers...
                          WARN  2018-10-05 09:02:09,770 (com.serotonin.m2m2.db.DBConvert.copyTable:136) -
                           --> Finished converting table mailingListMembers. 1 records copied.
                          WARN  2018-10-05 09:02:09,776 (com.serotonin.m2m2.db.DBConvert.copyTable:87) -
                          --> Converting table templates...
                          WARN  2018-10-05 09:02:10,642 (com.serotonin.m2m2.db.DBConvert.copyTable:136) -
                           --> Finished converting table templates. 4 records copied.
                          WARN  2018-10-05 09:02:10,648 (com.serotonin.m2m2.db.DBConvert.copyTable:87) -
                          --> Converting table dataSources...
                          WARN  2018-10-05 09:02:11,113 (com.serotonin.m2m2.db.DBConvert.copyTable:136) -
                           --> Finished converting table dataSources. 12 records copied.
                          WARN  2018-10-05 09:02:11,117 (com.serotonin.m2m2.db.DBConvert.copyTable:87) -
                          --> Converting table dataPoints...
                          WARN  2018-10-05 09:02:38,963 (com.serotonin.m2m2.db.DBConvert.copyTable:136) -
                           --> Finished converting table dataPoints. 201 records copied.
                          WARN  2018-10-05 09:02:38,972 (com.serotonin.m2m2.db.DBConvert.copyTable:87) -
                          --> Converting table pointValues...
                          ERROR 2018-10-05 10:07:39,219 (com.serotonin.m2m2.Main.main:119) - Error during
                          initialization
                          com.serotonin.ShouldNeverHappenException: java.sql.SQLException: 'NaN' is not a
                          valid numeric or approximate numeric value
                                  at com.serotonin.m2m2.db.DatabaseProxy.initialize(DatabaseProxy.java:134
                          Caused by: java.sql.SQLException: 'NaN' is not a valid numeric or approximate nu
                          meric value
                                  at com.mysql.jdbc.SQLError.createSQLException(SQLError.java:965)
                                  at com.mysql.jdbc.SQLError.createSQLException(SQLError.java:898)
                                  at com.mysql.jdbc.SQLError.createSQLException(SQLError.java:887)
                                  at com.mysql.jdbc.SQLError.createSQLException(SQLError.java:861)
                                  at com.mysql.jdbc.PreparedStatement.setDouble(PreparedStatement.java:330
                          0)
                                  at com.mysql.jdbc.PreparedStatement.setNumericObject(PreparedStatement.j
                          ava:3531)
                                  at com.mysql.jdbc.PreparedStatement.setObject(PreparedStatement.java:369
                          5)
                                  at com.mysql.jdbc.JDBC42PreparedStatement.setObject(JDBC42PreparedStatem
                          ent.java:99)
                                  at com.mysql.jdbc.PreparedStatement.setObject(PreparedStatement.java:362
                          0)
                          ent.java:83)
                                  at org.apache.commons.dbcp.DelegatingPreparedStatement.setObject(Delegat
                          ingPreparedStatement.java:166)
                                  at com.serotonin.m2m2.db.DBConvert.copyTable(DBConvert.java:119)
                                  at com.serotonin.m2m2.db.DBConvert.execute(DBConvert.java:54)
                                  at com.serotonin.m2m2.db.DatabaseProxy.initialize(DatabaseProxy.java:131
                                  ... 3 more
                          INFO  2018-10-05 10:07:39,224 (com.serotonin.m2m2.Lifecycle.terminate:353) - Man
                          java:149)
                          va:155)
                          INFO  2018-10-05 10:07:39,279 (com.serotonin.m2m2.db.BasePooledProxy.terminateIm
                          INFO  2018-10-05 10:07:39,281 (com.serotonin.m2m2.Lifecycle.terminate:453) - Man
                          I think the problem could be that pointvalue is nullable
                          you suggest me to clean values with an sql like
                          "delete from pointvalues where pointvalue is null;"
                            That looks like it would be caused by MySQL not supporting NaN, Infinity, or -Infinity as valid values in a column described as a double. If one has Mango already running on MySQL and attempts to set the value of a point to NaN, you get 0, if you do Infinity, you get Double.MAX_VALUE
                            But for converting, it doesn't look like there's any handling for the differences in what values are acceptable in one database or another. You could fix this by removing or changing these values before doing the conversion, by running this either through the Mango/bin/h2-web-console script or on the /sqlConsole.shtm page of Mango running on the old database:
                            -- for use to remove values from the H2 pointValues table that cannot be brought into MySQL
                            delete from pointValues where pointValue=CAST('NaN' AS DOUBLE PRECISION)
                            delete from pointValues where pointValue=CAST('Infinity' AS DOUBLE PRECISION);
                            delete from pointValues where pointValue=CAST('-Infinity' AS DOUBLE PRECISION)
                            Most commercial users use the NoSQL database to avoid problems with larger point values tables (since in Mango 3 all licensed cores can use the NoSQL database, unlike in 2.x where it is a separate license). That's probably why the issue has not been significant in the past. If you want to use SQL to store your point values, you definitely have to keep that table size under control or Mango will begin to slow down.
                            • E Offline
                              etantonio
                              The db convertion from H2 to mysql is running (10 hours just to convert table pointValues) but I think there's something strange, at the moment I have only data from last 80 days concerning about 100 variables stored at 1 sample/minute, so I think 80x100x60x24=11,5Million rows in table pointValues, instead the table is around 40Million points, corresponding to an H2 database of 3.5GB corresponding also to a mysql pointValues table using 3.5GB.
                              To delete data before last 80 days (originally 5 months) I used the datasource purge for each used datasource. The purge from admin settings seems not to work on a big H2 database or in any case it tooks a very long time.
                              • E Offline
                                etantonio
                                I'm searching for the reason why my H2 database is growing so fast,
                                I think that this "Logging TYpe = All Data" could be an error:
                                but, looking at the data, it seems that it takes a new value each minute
                                according to Data Source logging
                                so, it seems, it is not a problem, is it right?
                                  If you are not using the NoSQL database, yes pointvalues are a contributing factor to the database expansion (and in some people's cases probably the only factor). But, the issue is here: https://github.com/infiniteautomation/ma-core-public/issues/1344
                                  The likelihood is that sometime (probably sooner than later, maybe 3.6?) we will have a DB upgrade that does the necessary side work to upgrade an PageStore H2 database created in 196 to 197, as referenced in the issues referenced in that issue. In version 197 of H2 the problem of saving a LOB not reusing space has been resolved.
                                  But, if something like your pointValues pointValueAnnotations or events tables are just very full, the next version of the database may not help in your case.
                                  • E Offline
                                    etantonio
                                    This post is deleted!
                                    • E Offline
                                      etantonio
                                      I used this query to search for datapoints to reduce:
                                      SELECT count(*) as totale, dataPointId, d.name FROM pointValues p, dataPoints d
                                      where p.dataPointID = d.id
                                      group by p.dataPointId , d.name order by totale desc;
                                      I will tune the results of this query,
                                      I also founded 8500000 records in PointValueAnnotations all like the following row
                                      TEXTPOINTVALUESHORT | TEXTPOINTVALUELONG | SOURCEMESSAGE
                                                          |                    | scripting.annotation|
                                      are these rows useful for something or I can delete it?
                                      Who produce these rows?
                                      Thanks, Antonio
                                        That is a consequence of a Scripting data source setting points that belong to other data sources, so that those values can be seen to have come from elsewhere after the fact. Yes you could delete those rows, you may possibly have to do a backup and a restore to reclaim the disk space.
                                        • E Offline
                                          etantonio
                                          Thanks, I will delete such rows but I think other similar rows will be created in the future, there's a way to avoid this?
                                          Antonio
                                            Our solution was to code up the NoSQL module so that people wouldn't have trouble with their pointValues tables. That's the surefire way to avoid it.