    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
    Radix IoT Website Mango Documentation Radix IoT LinkedIn
    Git Hooks
    Scheduled Pinned Locked Moved Dashboard Designer & Custom AngularJS Pages
    15 Posts 4 Posters 7.1k Views 4 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • R Offline
      rshah
      Hi All,
      Jumping back to this -- say we do want to pull our code to Mango directly, where is the file located?
      For reference, we created our dashboards by going to the edit pages option and creating a new dashboard -- Also, the file we are working on is not a full HTML file, it doesn't have a <head> only a <body> -- so I'm not even sure if this will work.
      Is this something overrides are for? We looked into them a bit but are confused on how they exactly work.
      Thanks!
      1 Reply Last reply Reply Quote 0
      • phildunlapP Offline
        phildunlap
        Hi rshah,
        The pages created on the edit-pages or in the DashboardDesigner are stored in the jsonData table. You could definitely have something fetch it from git and update the entry in the table if you're using MySQL. It would probably take some developing, though.
        1 Reply Last reply Reply Quote 1
        • R Offline
          rshah
          @phildunlap said in Git Hooks:
          Got it -- thanks!
          Would it be easier to use overrides?
          RS
            phildunlap
            Ah yes, good idea. I was able to bring in an HTML file from my Mango/overrides/web/ directory with the edit page,
            <div ng-include="'/includeMe.html'"></div>
            • R Offline
              rshah
              Thanks again @phildunlap !
              To date, we've been leaving off the <html>, <head> and <body> tags -- I assume even with using this override system we should continue to do that? Here's a sample of the entire code we have in the document (we're still working on switching over to using a watchlist to get points rather than ma-get-point-value per your suggestion):
              <!-- We only want to obtain last 12 hours of data, so use Angular Moment Library to do figure out what last 12 hours are-->
              <ma-now update-interval="1 minutes" output="to"></ma-now>
              <ma-calc input="to | maMoment:'subtract':12:'hours'" output="from"></ma-calc>
              <!-- Obtain all CURRENT point values -->
              <!-- General Booster Pump -->
              <ma-get-point-value
                  point-xid="boosterPumpsSuctionPress"
                  point="boosterPumpsSuctionPress">
              </ma-get-point-value>
              <ma-get-point-value
                  point-xid="boosterPumpsSetpointPress"
                  point="boosterPumpsSetpointPress">
              <ma-get-point-value
                  point-xid="boosterPumpsPowerOnStatus"
                  point="boosterPumpsPowerOnStatus">
              <ma-get-point-value
                  point-xid="boosterPumpsOutputPress"
                  point="boosterPumpsOutputPress">
              <ma-get-point-value
                  point-xid="boosterPumpsLowSuctionPressAlarm"
                  point="boosterPumpsLowSuctionPressAlarm">
              <ma-get-point-value
                  point-xid="boosterPumpsLowPressAlarm"
                  point="boosterPumpsLowPressAlarm">
              <ma-get-point-value
                  point-xid="boosterPumpsHighPressAlarm"
                  point="boosterPumpsHighPressAlarm">
              <ma-get-point-value
                  point-xid="boosterPumpsGeneralAlarm"
                  point="boosterPumpsGeneralAlarm">
              <!-- Booster Pump 1 -->
              <ma-get-point-value
                  point-xid="boosterPump1RH"
                  point="boosterPump1RH">
              <ma-get-point-value
                  point-xid="boosterPump1RunStatus"
                  point="boosterPump1RunStatus">
              <ma-get-point-value
                  point-xid="boosterPump1ServiceStatus"
                  point="boosterPump1ServiceStatus">
              <ma-get-point-value
                  point-xid="boosterPump1VFDA"
                  point="boosterPump1VFDA">
              <ma-get-point-value
                  point-xid="boosterPump1VFDAlarm"
                  point="boosterPump1VFDAlarm">
              <ma-get-point-value
                  point-xid="boosterPump1VFDHz"
                  point="boosterPump1VFDHz">
              <ma-get-point-value
                  point-xid="boosterPump1VFDPwr"
                  point="boosterPump1VFDPwr">
              <!-- Booster Pump 2 -->
              <ma-get-point-value
                  point-xid="boosterPump2RH"
                  point="boosterPump2RH">
              <ma-get-point-value
                  point-xid="boosterPump2RunStatus"
                  point="boosterPump2RunStatus">
              <ma-get-point-value
                  point-xid="boosterPump2ServiceStatus"
                  point="boosterPump2ServiceStatus">
              <ma-get-point-value
                  point-xid="boosterPump2VFDA"
                  point="boosterPump2VFDA">
              <ma-get-point-value
                  point-xid="boosterPump2VFDAlarm"
                  point="boosterPump2VFDAlarm">
              <ma-get-point-value
                  point-xid="boosterPump2VFDHz"
                  point="boosterPump2VFDHz">
              <ma-get-point-value
                  point-xid="boosterPump2VFDPwr"
                  point="boosterPump2VFDPwr">
              <!-- Get last 12 hour of flow, suction, and output pressure data, averaged over 1 minute -->
              <ma-point-values
                  rendered="true"
                  values="boosterPumpsSuctionPressHistorical"
                  from="from"
                  to="to"
                  rollup="AVERAGE"
                  rollup-interval="1 minutes">
              </ma-point-values>
              <ma-point-values
                  rendered="true"
                  values="boosterPumpsOutputPressHistorical"
                  from="from"
                  to="to"
                  rollup="AVERAGE"
              </ma-point-values>
              <ma-point-values
                  point-xid="boosterPumpsFlowRate"
                  rendered="true"
                  values="boosterPumpsFlowRateHistorical"
                  from="from"
                  to="to"
                  rollup="AVERAGE"
              </ma-point-values>
              <!-- Displays only if the app is still loading -->
              <div ng-if="appLoading">
                  <span>App is loading..</span>
              </div>
              <div ng-cloak layout="column" class="centerText" flex>
                  <h1 class="centerText">Cold Water Booster Pumps (Basement)</h3>
                  <!-- Row 1 -->
                  <div layout="row">
                      <md-card flex="25">
                          <md-card-title>
                              <md-card-title-text>
                                  Pump System Power Status
                              </md-card-title-text>
                          </md-card-title>
                          <md-card-content layout="column">
                              {{boosterPumpsPowerOnStatus.renderedValue}}
                          </md-card-content>
                      </md-card>
                      <md-card flex="25">
                          <md-card-title>
                                  Suction Pressure
                          </md-card-title>
                              {{boosterPumpsSuctionPress.renderedValue}}
                          </md-card-content>
                      </md-card>
                      <md-card flex="25">
                          <md-card-title>
                                  Setpoint Pressure
                          </md-card-title>
                              {{boosterPumpsSetpointPress.renderedValue}}
                          </md-card-content>
                      </md-card>
                      <md-card flex="25">
                          <md-card-title>
                                  Output Pressure
                          </md-card-title>
                              {{boosterPumpsOutputPress.renderedValue}}
                          </md-card-content>
                      </md-card>
                  </div>
                  <!-- Row 2 -->
                  <div layout="row">
                      <md-card flex="25">
                          <md-card-title>
                                  High Pressure Alarm
                          </md-card-title>
                              {{boosterPumpsHighPressAlarm.renderedValue}}
                          </md-card-content>
                      </md-card>
                      <md-card flex="25">
                          <md-card-title>
                                  Low Suction Pressure Alarm
                          </md-card-title>
                              {{boosterPumpsLowSuctionPressAlarm.renderedValue}}
                          </md-card-content>
                      </md-card>
                      <md-card flex="25">
                          <md-card-title>
                                  General Alarm
                          </md-card-title>
                              {{boosterPumpsGeneralAlarm.renderedValue}}
                          </md-card-content>
                      </md-card>
                      <md-card flex="25">
                          <md-card-title>
                                  Low Pressure Alarm
                          </md-card-title>
                              {{boosterPumpsLowPressAlarm.renderedValue}}
                          </md-card-content>
                      </md-card>
                  </div>
              <!-- Row 3 -->
                  <div layout="row">
                      <!-- PUMP 1 INFORMATION -->
                      <md-card flex="50">
                          <md-card-title>
                                  <h2>Pump 1</h2>
                          </md-card-title>
                          <md-card-content layout="row">
                              <md-card flex="33">
                                  <md-card-title>
                                          Service Status
                                  </md-card-title>
                                      {{boosterPump1ServiceStatus.renderedValue}}
                                  </md-card-content>
                              </md-card>
                              <md-card flex="33">
                                  <md-card-title>
                                          Running Status
                                  </md-card-title>
                                      {{boosterPump1RunStatus.renderedValue}}
                                  </md-card-content>
                              </md-card>
                              <md-card flex="33">
                                  <md-card-title>
                                          Run Hours
                                  </md-card-title>
                                      {{boosterPump1RH.renderedValue}}
                                  </md-card-content>
                              </md-card>
                          </md-card-content>
                              <h3>Variable Frequency Drive</h3>
                          </md-card-content>
                              <md-card flex="25">
                                  <md-card-title>
                                          Alarm
                                  </md-card-title>
                                      {{boosterPump1VFDAlarm.renderedValue}}
                                  </md-card-content>
                              </md-card>
                              <md-card flex="25">
                                  <md-card-title>
                                          Amps
                                  </md-card-title>
                                      {{boosterPump1VFDA.renderedValue}}
                                  </md-card-content>
                              </md-card>
                              <md-card flex="25">
                                  <md-card-title>
                                          Frequency
                                  </md-card-title>
                                      {{boosterPump1VFDHz.renderedValue}}
                                  </md-card-content>
                              </md-card>
                              <md-card flex="25">
                                  <md-card-title>
                                          Power
                                  </md-card-title>
                                      {{boosterPump1VFDPwr.renderedValue}}
                                  </md-card-content>
                              </md-card>
                          </md-card-content>
                      </md-card>
                      <!-- PUMP 2 INFORMATION -->
                      <md-card flex="50">
                          <md-card-title>
                                  <h2>Pump 2</h2>
                          </md-card-title>
                              <md-card flex="33">
                                  <md-card-title>
                                          Service Status
                                  </md-card-title>
                                      {{boosterPump2ServiceStatus.renderedValue}}
                                  </md-card-content>
                              </md-card>
                              <md-card flex="33">
                                  <md-card-title>
                                          Running Status
                                  </md-card-title>
                                      {{boosterPump2RunStatus.renderedValue}}
                                  </md-card-content>
                              </md-card>
                              <md-card flex="33">
                                  <md-card-title>
                                          Run Hours
                                  </md-card-title>
                                      {{boosterPump2RH.renderedValue}}
                                  </md-card-content>
                              </md-card>
                          </md-card-content>
                          </md-card-content>
                              <md-card flex="25">
                                  <md-card-title>
                                          Alarm
                                  </md-card-title>
                                      {{boosterPump2VFDAlarm.renderedValue}}
                                  </md-card-content>
                              </md-card>
                              <md-card flex="25">
                                  <md-card-title>
                                          Amps
                                  </md-card-title>
                                      {{boosterPump2VFDA.renderedValue}}
                                  </md-card-content>
                              </md-card>
                              <md-card flex="25">
                                  <md-card-title>
                                          Frequency
                                  </md-card-title>
                                      {{boosterPump2VFDHz.renderedValue}}
                                  </md-card-content>
                              </md-card>
                              <md-card flex="25">
                                  <md-card-title>
                                          Power
                                  </md-card-title>
                                      {{boosterPump2VFDPwr.renderedValue}}
                                  </md-card-content>
                              </md-card>
                          </md-card-content>
                      </md-card>
                  </div>
                  <!-- ROW 4 -->
                  <div layout="row">
                      <md-card flex="100">
                          <md-card-content>
                              <ma-serial-chart
                              style="height: 490px; width: 100%"
                              series-1-values="boosterPumpsSuctionPressHistorical"
                              series-1-title="Booster Pump - Suction Pressure"
                              series-1-color="#FF0000"
                              series-1-axis="left"
                              series-1-type="smoothedLine"
                              series-2-values="boosterPumpsOutputPressHistorical"
                              series-2-title="Booster Pump - Output Pressure"
                              series-2-color="#FF8700"
                              series-2-axis="left"
                              series-2-type="smoothedLine"
                              series-3-values="boosterPumpsFlowRateHistorical"
                              series-3-title="Booster Pump - Flow Rate"
                              series-3-color="#00FFFF"
                              series-3-axis="right"
                              series-3-type="smoothedLine"
                              legend="true"
                              options="{
                                  synchronizeGrid: false,
                                  valueAxes:[
                                          axisColor:'#212125',
                                          color:'white',
                                          title: 'Pressure (PSIG)',
                                          titleColor: 'white',
                                          fontSize: 26,
                                          titleFontSize: 26,
                                          minimum:30,
                                          maximum:140,
                                          color:'white',
                                          title: 'Flow Rate (GPM)',
                                          fontSize: 26,
                                          titleFontSize: 26,
                                          minimum:0,
                                          maximum:40
                              </ma-serial-chart>
                          </md-card-content>
                      </md-card>
                  </div>
                  <!-- END OF PAGE -->
              </div>
              <style>
                  md-card-title {
                      padding-top: 0px !important;
                  .centerText {
                      text-align: center;
                  .firing {
                      background-color: green !important;
                  .firingDHW {
                      color: lightgreen !important;
                  .alarm {
                      background-color: red !important;
                  .noAlarm {
                      color: lightgreen;
                      font-weight: bold;
                  md-card-title-text {
                      font-size: 130%;
                  md-card-content {
                      font-size: 110%;
              </style>
              • Jared WiltshireJ Offline
                Jared Wiltshire
                @rshah the custom pages should not be full HTML pages, they are snippets of HTML which are included into the main document.
                I would not recommend trying to insert anything into the database directly.
                You can certainly include a file from overrides as @phildunlap showed you, you could then just do a git pull into your repository inside the overrides directory to update the pages.
                If you do want to use a git hook I would suggest using the REST API (with token auth) to save the contents into the JSON store.
                Developer at Radix IoT
                • MattFoxM Offline
                  MattFox
                  I use git for my new dashboards, works really well. A good way to test as I go.
                  My pages use template files so I can do full custom content and embed it into the mango page using the userModule extension that Jared showed me a few months ago. All of my pages are components with the html as a templateUrl property.
                  However to answer your question, sorry no I don't use git hooks. No point adding further complexity for something which should be simple to code and maintain.
                  Do not follow where the path may lead; go instead where there is no path.
                  And leave a trail - Muriel Strode
                  • R Offline
                    rshah
                    Hey @MattFox / @Jared-Wiltshire / @phildunlap ,
                    Wondering if you guys have run into an issue with using ng-include in a div with it changing the page size?
                    I am assuming the div has a default style being applied to it which is making things larger, but I haven't been able to find anything. Screenshots below:
                    Version 1 - code stored in overrides, included with ng-include in a div (as you can see, everything is larger and a scroll bar is added to the page since the content doesn't fit)
                    Code:
                    Screen:
                    0_1528733961415_2018-06-11 11_14_53-Updated Waterfall Information Screen - Mango v3.png
                    Version 2 - Code pasted directly into the edit pages menu, scroll bar is gone, everything fits fine:
                    Code:
                    Screen (as you can see scroll bar is gone, everything fits)
                    0_1528734044649_2018-06-11 11_15_39-Updated Waterfall Information Screen - Mango v3.png
                      Jared Wiltshire
                      @rshah Yeah I'd open up the developer tools and check the computed styles to figure out what is happening -
                      • R Offline
                        rshah
                        Doesn't look like there are a ton of styles being applied to the div that would mess with anything, we used inline styles everywhere so they should have priority.
                        Do you see anything that catches your eye?
                        • MattFoxM Offline
                          MattFox
                          @rshah would you be willing to share the contents of your templates/pages? Happy to have a look in my own time to see why, I had a similar issue with mapbox-gl. Added some additional css and bingo I was away.
                            Jared Wiltshire
                            Try adding flex layout="column" to the div attributes.
                            • R Offline
                              rshah
                              @jared-wiltshire said in Git Hooks:
                              That did it! Thanks!
                              What did you notice that caused you to think that was the solution @Jared-Wiltshire ?
                              Also thanks for your help @MattFox -- If you ever have time I'd love to send you some of our code to pick your brain on how we're handling ma-serial-chart.
                              Jared WiltshireJ 1 Reply Last reply Reply Quote 0
                                Jared Wiltshire @rshah
                                @rshah said in Git Hooks:
                                Just a hunch after playing with this stuff for a long time, the parent element had these set and it was obviously affecting the children's layout somehow.
                                Hello! It looks like you're interested in this conversation, but you don't have an account yet.
                                Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.
                                With your input, this post could be even better 💗
                                Register Login
                                • First post
                                  Last post