      Hi Aldo,
      You are correct, it should indeed be returned via return source.value (but if your script is that simple you need not have one (a point link with an empty script just sets the value simply)).
      However, the ability to call set() was added to all scripting environments, so target.set(source.value); should also work (Note that you will need script permissions configured on the point link to set points)
      We did fix a NullPointerException fairly recently related to Point Links. It's possible your point link is configured not to set the annotation, but that null pointer is what is causing you not to see the value. If so, I would say try setting the annotation again or updating to the latest.
      Other conditions would produce a point link failure event that you could see in your events table.
      Edit: And you mean, "appears not to set the target," correct?
      • AldoRamosA Offline
        AldoRamos
        Correct on the typo; I've fixed it.
          AldoRamos
          I don't see any NullPointerException in the log, but I do occasionally get:
          FATAL 2017-10-19 13:28:05,674 (com.serotonin.m2m2.util.timeout.RejectedHighPriorityTaskEventGenerator.rejected:47) - High priority task: com.serotonin.m2m2.rt.dataImage.DataPointRT rejected because Task Currently Running
          This doesn't appear to correlate with attempts to execute the point link, but it's the only error message I am seeing, so I have to wonder.
            AldoRamos
            Also, the empty script was implied in the documentation, but I wasn't certain (especially given the problems we are experiencing with point links)
              AldoRamos
              And FWIW, this is running core 2.8.8 build 635, pointLinks 1.6.0
                Hmm. That rejected task would probably be an interval logging task for a data point, but that would still enable the cache to have the result of the point link set.
                The NullPointerException may have been escaping to stderr, I can't recall, or if it was logged as an uncaught task exception. If you point link doesn't set the annotation this could very likely cause it. target.set() wouldn't be an option in 2.8.8
                You also checked your events and didn't have any cause?
                "Disabled" isn't checked on your point link, is it?
                  AldoRamos
                  I do have it set to write annotation (and I have toggled it on & off several times in attempts to debug). Now that I think about it, I never see any annotations (except for manual set values), as expected given the behavior.
                  "Disabled" is not set (I wish it was a simple idiot mistake like that), although I have toggled it in attempts to debug.
                    I have tested the version you are on, it works as I expect (and is not affected by the annotation issue I believe, or that's only if you've got a websocket open to the target point perhaps).
                    Here is my configuration:
                       "dataSources":[
                             "xid":"DS_808993",
                             "name":"PL_TEST",
                             "enabled":true,
                             "type":"VIRTUAL",
                             "alarmLevels":{
                                "POLL_ABORTED":"URGENT"
                             "purgeType":"YEARS",
                             "updatePeriodType":"MINUTES",
                             "updatePeriods":1,
                             "editPermission":"",
                             "purgeOverride":false,
                             "purgePeriod":1
                       "dataPoints":[
                             "xid":"DP_479771",
                             "name":"Source",
                             "enabled":true,
                             "loggingType":"INTERVAL",
                             "pointLocator":{
                                "dataType":"NUMERIC",
                                "changeType":{
                                   "type":"NO_CHANGE",
                                   "startValue":"50"
                                "settable":true
                             "eventDetectors":[
                             "plotType":"SPLINE",
                             "unit":"",
                             "templateXid":"Numeric_Default",
                             "chartColour":"black",
                             "chartRenderer":{
                                "type":"IMAGE",
                                "timePeriodType":"DAYS",
                                "numberOfPeriods":1
                             "dataSourceXid":"DS_808993",
                             "defaultCacheSize":1,
                             "deviceName":"PL_TEST",
                             "discardExtremeValues":false,
                             "intervalLoggingPeriod":1,
                             "purgePeriod":1,
                             "readPermission":"",
                             "setPermission":"",
                             "textRenderer":{
                                "type":"ANALOG",
                                "useUnitAsSuffix":true,
                                "unit":"",
                                "renderedUnit":"",
                                "format":"0.00"
                             "tolerance":0.0
                             "xid":"DP_393152",
                             "name":"Target",
                             "enabled":true,
                             "pointLocator":{
                                "changeType":{
                                   "type":"NO_CHANGE",
                                   "startValue":"10"
                                "settable":true
                             "eventDetectors":[
                             "unit":"",
                             "chartRenderer":{
                                "type":"IMAGE",
                                "numberOfPeriods":1
                             "purgePeriod":1,
                             "setPermission":"",
                             "textRenderer":{
                                "type":"ANALOG",
                                "unit":"",
                                "renderedUnit":"",
                                "format":"0.00"
                             "tolerance":0.0
                       "pointLinks":[
                             "xid":"PL_112332",
                             "sourcePointId":"DP_479771",
                             "targetPointId":"DP_393152",
                             "event":"CHANGE",
                             "logLevel":"NONE",
                             "disabled":false,
                             "script":"return source.value",
                             "scriptPermissions":{
                                "customPermissions":"",
                             "writeAnnotation":true
                       "watchLists":[
                             "xid":"WL_908992",
                             "name":"(unnamed)",
                             "user":"admin",
                             "dataPoints":[
                                "DP_479771",
                                "DP_393152"
                             "data":null,
                             "editPermission":null,
                             "folderIds":null,
                             "params":null,
                             "query":null,
                             "readPermission":null,
                             "type":"static"
                    Is it possible that you've pointed the link at a point that doesn't support setting, or that its device is failing the set so the value doesn't change?
                      AldoRamos
                      The target is a virtual data point (user input) so no device to fail. And I did check the "Settable" parameter. Several times. ;-)
                      My configuration is essentially identical to what you shared.
                      As I mentioned, it was working once upon a time, so it's extremely puzzling where the problem could be arising.
                        Is it possible that you're not using the latest NoSQL module? I guess if you had an older version and a lock had gotten stuck on that point in the database that would cause something like what you're seeing. You shouldn't be able to set any values to that target point via any means in that condition, though: none would make it into the database. If it were the NoSQL module, though, I would still expect a modbus device, say, to send the set command out.
                          AldoRamos
                          No, this is not using NoSQL.
                          And again, the target point is a Virtual Point (user input)
                            And you don't have obvious messages about Timer Cancelled, or running out of memory, or anything like that?
                            And you've tried restarting the instance?
                            I am certain the example I posted works, and I was using the version you're using.
                              AldoRamos
                              Correct, no “Timer Cancelled” messages, no running out of memory (since I added swap) or any other messages at this point.
                              I do occasionally get this error message:
                              WARN  2017-10-20 14:11:12,771 (com.serotonin.m2m2.rt.dataSource.PollingDataSource.incrementUnsuccessfulPolls:107) - Data Source GCI Input aborted 28 polls since it started.
                              And yes, I have restarted the instance. Several times. ;-)
                                Hmm, that's a real puzzler!
                                I have no context for what that data source is, so its having aborted polls is probably irrelevant. You say the source point is updating.
                                If the point link ran, and an error occurred in the SetPointWorkItem, it would have been logged. You could check your SQL logs if you haven't.
                                Is your instance bogged down, and perhaps every time you expect the point link to fire you see the number of medium priority work items increase, and that isn't decreasing, perhaps they are not executing.
                                You can launch your instance with ./ma.sh start and if anything were escaping to stderr you would see it.
                                You can launch Mango on a fresh database and try to replicate.
                                You can post or email JSON you think would replicate it and I'll try.
                                  AldoRamos
                                  We're preparing to upgrade that server to 3.2, so I'm putting off any further attempts until then. At that point, I'll try your suggestions (if the problem persists), and report back to you.
                                  For what it's worth, we attempted creating an event handler to accomplish the same effect, but the result was the same.
                                  We are able to change the value manually (user input) but having difficulty with any programmatic changes.
                                  We'll update you on Monday. Have a great weekend.
                                  Aldo
                                    AldoRamos
                                    Just noticed this interesting message in the logs, when shutting down:
                                    INFO  2017-10-25 13:50:32,882 (com.serotonin.m2m2.rt.maint.BackgroundProcessing.joinTermination:363) - BackgroundProcessing waiting 5 more seconds for 3 active and 1300637 queued medium priority tasks to complete.
                                    INFO  2017-10-25 13:50:36,927 (com.serotonin.m2m2.rt.maint.BackgroundProcessing.joinTermination:375) - 1300637 medium priority tasks forcefully terminated.
                                    That does not sound normal, and it would explain the error we were already seeing:
                                    FATAL 2017-10-24 13:40:41,368 (com.serotonin.m2m2.util.timeout.RejectedHighPriorityTaskEventGenerator.rejected:47) - High priority task: com.serotonin.m2m2.rt.dataImage.DataPointRT rejected because Task Currently Running
                                    Thoughts? What would cause this?
                                    P.S. I imported a backup of the settings from a few weeks ago, when it was working; no change
                                      @phildunlap said in Are there Point Link (pointLink) tutorials, or examples?:
                                        AldoRamos
                                        There really shouldn't be any significant load; it's just receiving on a Persistent TCP Data Source, waiting for user input on a Virtual Data Source, and the previously mentioned point links.
                                          How big are your events and pointValues tables?
                                          The NoSQL module is much, much more efficient than using the SQL table.
                                            AldoRamos
                                            They were big enough that I canceled "SELECT COUNT(*)" queries because I ran out of patience waiting for results. We had been logging all data (then interval) in an effort to force charts to draw points (binary points, would be ON for hours/days before being OFF for 5 seconds at a time).
                                            I truncated the tables, restarted Mango, and now it's behaving as expected.
                                            The troubling symptom is that it seemed the number of queued tasks was never decreasing. Yes, the table is filling up, but even just an SQL insert should eventually catch up (one would think). Hopefully once we migrate to 3.2 and NoSQL this becomes a non-issue, but it is a surprise to find this to be a bottleneck.
                                            One critical piece of information: this is running on an AWS server, with an Aurora RDS backend. Have you come across any issues with Aurora?
                                            Finally, since this was a side-effect of attempting to force logging to create better charts for data that remains unchanged for a long time, do you have any recommendations to accomplish the desired results?
                                            Aldo
                                            P.S. I have emailed separately regarding licenses; awaiting reply.