    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    How to change the http sending value parameter

    User help
    3
    78
    20.3k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • J
      jmatos @jmatos
      last edited by

      @jmatos said in How to change the http sending value parameter:

      Hi Phildunlap,

      As you know the solution is already installed at client facilities.

      unfortunately I have cross with a "huge" problem that I can't figure out. :-(

      When there is more than two (2) - say six - simultaneous alarm I can't get them all out on the http publisher. The alarms are registered in historic but only two reach the destination. It seems that they are lost between the publisher and from this to network. I've used wireshark and I dont see they getting out.

      I've try to increase the cache size (is necessary to restart the all mango instance or a simple save is enough?)

      May you please help me on this one?

      Thanks in advance,
      Jose

      Do you have any answer to me regarding this issue?

      1 Reply Last reply Reply Quote 0
      • phildunlapP
        phildunlap
        last edited by

        Hi jmatos,

        I would wonder,

        1. What is the update event for the publisher?
        2. What is the logging type for the Alarm out point?
        3. Are you using the NoSQL database?

        My expectation is that the logging type for the alarm point is discarding some seemingly-backdated data in the concurrent update situation, or possible that the data is occurring at the same millisecond, and the NoSQL database can't store more than one value at one timestamp.

        1 Reply Last reply Reply Quote 0
        • J
          jmatos
          last edited by jmatos

          Hi phildunlap

          1. All
          2. When point value changes
          3. I think so (How can I be sure?)

          More info: When I go to menu [Data Point Details] history all the alarm out are registered OK.

          Here on lab I try an simulated an alarm out send through the http publisher to the same destination software with a virtual source generating a random number every 1ooms and all them reach the destination.

          Tomorrow I'll go to the client and try this virtual send.

          updating after visit the client:

          Test results with real BACnet objects on client:
          At two times I had to restart Mango and five of five(!) alarms get to the destination! But just on the startup... :-( All the test afterwards only get the "old same" two.

          So, the alarms are registered at entry level and reported in the Data Point Details. But only two reach the destination.

          I think you maybe right concerning the same millisecond, but in this case something has to explain the five-of-five that reach the destination on startup.

          Is there some delay we can insert to workaround the possible same timestamp?

          Important: As I told you before, I'm not sure what DB is in use. How can I be sure and if not using NoSQL how do I change it? the problem can be in here... :-(

          Thanks in advance,
          Jose

          1 Reply Last reply Reply Quote 0
          • phildunlapP
            phildunlap
            last edited by

            Hmm.

            Before working on a workaround for the same milliseconds, let's try to confirm that's actually occurring (but maybe this would be the workaround). One thing you could try is putting a couple manual offsets in the point links' times, like:

            TIMESTAMP = source.time+1; //one millisecond later than the source's TS
            //you could use +2 on another one, and so on
            

            It's possible on startup it registered a COV notification, got that point values (everything would have different timestamps), but for some reason reverted to polling those points. In which case, all new values would have the timestamp of the poll.

            1 Reply Last reply Reply Quote 0
            • J
              jmatos
              last edited by jmatos

              Hi Phil,

              Where do I put it? Sorry but I can figure it out. Probably because I have 1800 point links... I'm lost here. :-(

              As instructed previously by you I put a Global script

              function getPrefix() { /*So that you may change the prefix for all scripts later if required */
                  return "4";
              }
              

              this is running on all point links. Is any way to add the time code here? Or am I confused? (its not the first time :D )

              thank you

              1 Reply Last reply Reply Quote 0
              • phildunlapP
                phildunlap
                last edited by phildunlap

                Wow 1800! Are they all to the same target point? At a certain number we may want to rethink the general tactic of wedging lots of points' alarms out one point. But, if it works, ok.

                Off hand I can't think of a way to do what I was describing in the global script, but here's a python script to mass modify your point links. You probably want to keep a JSON backup of them, in case you wish to revert.

                import json
                
                configFile = open("/path/to/Mango/backup/Mango-Configuration.json")
                config = json.load( configFile )
                configFile.close()
                
                x = 0
                for pl in config["pointLinks"] :
                  if pl["script"] != "" :
                    pl["script"] = "TIMESTAMP=source.time+" + str(x) + ";\\n" + pl["script"]
                    x += 1
                
                outputFile = open("/path/to/output.json", "w+")
                outputFile.write( json.dumps( {"pointLinks": config["pointLinks"]}, indent=4, sort_keys=False, separators=(",",": ") )
                outputFile.close()
                
                J 1 Reply Last reply Reply Quote 0
                • J
                  jmatos
                  last edited by

                  I'm hopping to test the first code in six or 8 link points. That I can do one by one... ;-)

                  Thanks in advance for the second code.

                  I'll feedback to you.

                  Cheers

                  1 Reply Last reply Reply Quote 0
                  • J
                    jmatos @phildunlap
                    last edited by

                    @phildunlap said in How to change the http sending value parameter:

                    Wow 1800! Are they all to the same target point? At a certain number we may want to rethink the general tactic of wedging lots of points' alarms out one point. But, if it works, ok.

                    Off hand I can't think of a way to do what I was describing in the global script, but here's a python script to mass modify your point links. You probably want to keep a JSON backup of them, in case you wish to revert.

                    import json
                    
                    configFile = open("/path/to/Mango/backup/Mango-Configuration.json")
                    config = json.load( configFile )
                    configFile.close()
                    
                    x = 0
                    for pl in config["pointLinks"] :
                      if pl["script"] != "" :
                        pl["script"] = "TIMESTAMP=source.time+" + str(x) + ";\\n" + pl["script"]
                        x += 1
                    
                    outputFile = open("/path/to/output.json", "w+")
                    outputFile.write( json.dumps( {"pointLinks": config["pointLinks"]}, indent=4, sort_keys=False, separators=(",",": ")
                    outputFile.close()
                    

                    Sorry. I get an invalid syntax at outputFile.close()

                    1 Reply Last reply Reply Quote 0
                    • phildunlapP
                      phildunlap
                      last edited by

                      Whoops. Looks like there was a missing parenthesis. Fixed.

                      J 1 Reply Last reply Reply Quote 0
                      • J
                        jmatos @phildunlap
                        last edited by

                        @phildunlap said in How to change the http sending value parameter:

                        Whoops. Looks like there was a missing parenthesis. Fixed.

                        As the syntax error persists I try one more missed parenthesis. Your answer and Notepad++ made me see that conclusion. So 2 added.

                        outputFile.write( json.dumps( {"pointLinks": config["pointLinks"]}, indent=4, sort_keys=False, separators=(",",": ") ) )
                        

                        Thank you

                        1 Reply Last reply Reply Quote 0
                        • phildunlapP
                          phildunlap
                          last edited by

                          Oof, sorry. I've convinced myself I can write these little python things and not test them, but I really should have the preamble and output copied in so I can't do little things like that!

                          1 Reply Last reply Reply Quote 0
                          • J
                            jmatos
                            last edited by

                            Hi Phil,

                            I'm not figure it out... the code

                            TIMESTAMP = source.time+1; //one millisecond later than the source's TS
                            //you could use +2 on another one, and so on
                            

                            Adds only a timestamp or in fact inserts a delay? Or both?

                            Thank you

                            1 Reply Last reply Reply Quote 0
                            • phildunlapP
                              phildunlap
                              last edited by phildunlap

                              The idea was to alter the timestamp set to the almnr point by some number of milliseconds into the future. They are varied because using the NoSQL database you cannot have two values at the same millisecond, and if these point links are triggered by one data source's polling (or just multiple points on some of the data sources), there's a high probability there are duplicate timestamps on the target point.

                              I'm not sure that's going to solve the issue you're describing, but it was something to try.

                              Edit: no delay should have been inserted.

                              Edit again, to explain:
                              TIMESTAMP is a variable name checked after the script returns its value, and if defined it is used as the timestamp for the value on the point set by the point link (or also the value assigned to a meta point, in that case)

                              1 Reply Last reply Reply Quote 0
                              • J
                                jmatos
                                last edited by

                                Hi Phil,

                                It does not work... :(

                                So I have cross my fingers and do a version upgrade to MANGO 3...

                                Now MANGO's not responding! (snif!). "ERR_CONNECTION_REFUSED" is all I get as browser response. The Webmin is working fine. Is there something else I can try before I restore the Mango directory ?

                                Thank you

                                1 Reply Last reply Reply Quote 0
                                • phildunlapP
                                  phildunlap
                                  last edited by

                                  Hi Jose,

                                  I wouldn't expect the issue you're describing to be resolved by upgrading. But, you probably have an error in startup that we could see if you attempted to start Mango manually on the command line.

                                  So navigate to Mango/bin and run either ./ma.sh start or ma-start.bat

                                  Actually figuring out what's going on in your situation may be too difficult through the forum. I understand the issue to be something like...

                                  1. Mango 1 polls a data source
                                  2. Many points links set a point on Mango 1 many times.
                                  3. The values of that point are published through an HTTP publisher
                                  4. The receiving end is not ending up with the same set of data as the sending end, but no errors are being recorded on either Mango

                                  There's a lot to explore there.

                                  1 Reply Last reply Reply Quote 0
                                  • J
                                    jmatos
                                    last edited by phildunlap

                                    here is the result

                                    mango@mangoES3249:/opt/mango/bin$sudo ./ma.sh start
                                    sudo: unable to resolve host mangoES3249
                                    [sudo] password for mango:
                                    sudo: ./ma.sh: command not found
                                    mango@mangoES3249:/opt/mango/bin$ma.sh start
                                    -bash: ma.sh: command not found
                                    mango@mangoES3249:/opt/mango/bin$dir
                                    ext-available  ext-enabled  h2-web-console.bat  h2-web-console.sh  ma-init.sh  ma.pid  ma-restart.sh  ma.sh  ma-start.bat  ma-start.sh  ma-stop.sh  upgrade.bat  upgrade.sh
                                    
                                    1 Reply Last reply Reply Quote 0
                                    • phildunlapP
                                      phildunlap
                                      last edited by

                                      Try...

                                      sudo /opt/mango/bin/ma.sh start

                                      sudo su; ./ma.sh start

                                      1 Reply Last reply Reply Quote 0
                                      • phildunlapP
                                        phildunlap
                                        last edited by phildunlap

                                        It's possible ma.sh isn't executable, do sudo chmod +x /opt/mango/bin/ma.sh

                                        1 Reply Last reply Reply Quote 0
                                        • J
                                          jmatos
                                          last edited by

                                          to all I get the same result:

                                          sudo: unable to resolve host mangoES3249
                                          

                                          unless for

                                          sudo su; ./ma.sh start
                                          

                                          where I get the PuTTY screen again - with the calendar, cpu info, etc. - as when I entered

                                          1 Reply Last reply Reply Quote 0
                                          • phildunlapP
                                            phildunlap
                                            last edited by

                                            You would do the ./ma.sh start after the sudo su scrolls by the login screen again. When you're root@mangoES3249:~

                                            Hmm. That message suggests something is amiss in your /etc/hosts or /etc/hostname file. I bet you've got a line like 127.0.1.1 mangoes in your /etc/hosts file, where you'd want to change it to 127.0.1.1 mangoES3249 then log out and in again. The unable to resolve host message should be gone.