    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    Modbus RTU Low and High Register Information

    Scheduled Pinned Locked Moved User help
    4 Posts 2 Posters 2.2k Views 2 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • J Offline
      jason81
      last edited by

      I'm trying to get some info from a modbus RTU device and some of the data is sent at the same register but one is a low register the other value at the high register.

      71 H Occupied Cooling Setpoint
      71 L Occupied Heating Setpoint
      72 H Un-Occupied Cooling Setpoint
      72 L Un-Occupied Heating Setpoint

      What datatype do I use to read and or command the individual values? Above is an example of 4 points that I need to view and command. The first two are both at register 71 but Occupied Cooling Setpoint is under the H or High and Occupied Heating Setpoint is under the L or Low register. Im looking to map each point value and be able to command as needed.

      1 Reply Last reply Reply Quote 0
      • phildunlapP Offline
        phildunlap
        last edited by

        Hi Jason,

        Can you post the manual for that device or a link? That sounds wonky!

        I am guessing you meant the low byte and the high byte of the register?

        There is no support for that directly in Modbus4J, but you could make it work in Mango by using a 16bit data type (probably 2 byte signed or unsigned integer and some point links (bit masks like, 71&0xFF && (71>>8)&0xFF). We can go into a solution there, but I'm really curious, from how you were using the word register in multiple senses, if there isn't more in the manual to shed light on why a company would elect to use Modbus but not elect to respect the specification of 16bits being the word size.

        1 Reply Last reply Reply Quote 0
        • J Offline
          jason81
          last edited by

          Here is the manual for the device.0_1492031464463_upload-4687a129-8284-4695-9883-449ddc53a193 ![alt text](image url)

          1 Reply Last reply Reply Quote 0
          • phildunlapP Offline
            phildunlap
            last edited by phildunlap

            Madness!

            Okay, well, here'd be my first guess:

            1. Create a Modbus data source, Create a data point for register 71 reading a 2 byte unsigned integer, you configuration may look like this:
            
            {
               "dataSources":[
                  {
                     "xid":"DS_cba83af5-38f8-4830-a07a-daeda155bc5b",
                     "name":"wonky-byte-packing",
                     "enabled":false,
                     "type":"MODBUS_IP",
                     "alarmLevels":{
                        "POINT_WRITE_EXCEPTION":"URGENT",
                        "POLL_ABORTED":"URGENT",
                        "DATA_SOURCE_EXCEPTION":"URGENT",
                        "POINT_READ_EXCEPTION":"URGENT"
                     },
                     "purgeType":"YEARS",
                     "updatePeriodType":"SECONDS",
                     "transportType":"TCP",
                     "encapsulated":false,
                     "host":"localhost",
                     "port":502,
                     "contiguousBatches":false,
                     "createSlaveMonitorPoints":false,
                     "discardDataDelay":0,
                     "ioLogFileSizeMBytes":1.0,
                     "logIO":false,
                     "maxHistoricalIOLogs":1,
                     "maxReadBitCount":2000,
                     "maxReadRegisterCount":125,
                     "maxWriteRegisterCount":120,
                     "multipleWritesOnly":false,
                     "quantize":false,
                     "retries":2,
                     "timeout":500,
                     "updatePeriods":20,
                     "editPermission":"",
                     "purgeOverride":false,
                     "purgePeriod":1
                  }
               ],
               "dataPoints":[
                  {
                     "xid":"DP_00c2c077-a245-4768-aed8-774bb0f7f982",
                     "name":"OccupiedTemps",
                     "enabled":false,
                     "loggingType":"ALL",
                     "intervalLoggingPeriodType":"MINUTES",
                     "intervalLoggingType":"AVERAGE",
                     "purgeType":"YEARS",
                     "pointLocator":{
                        "range":"HOLDING_REGISTER",
                        "modbusDataType":"TWO_BYTE_INT_UNSIGNED",
                        "writeType":"SETTABLE",
                        "additive":0.0,
                        "bit":0,
                        "charset":"ASCII",
                        "multiplier":1.0,
                        "offset":71,
                        "registerCount":0,
                        "slaveId":1,
                        "slaveMonitor":false
                     },
                     "eventDetectors":[
                     ],
                     "plotType":"SPLINE",
                     "rollup":"NONE",
                     "unit":"",
                     "chartColour":"",
                     "chartRenderer":{
                        "type":"IMAGE",
                        "timePeriodType":"DAYS",
                        "numberOfPeriods":1
                     },
                     "dataSourceXid":"DS_cba83af5-38f8-4830-a07a-daeda155bc5b",
                     "defaultCacheSize":1,
                     "deviceName":"wonky-byte-packing",
                     "discardExtremeValues":false,
                     "discardHighLimit":1.7976931348623157E308,
                     "discardLowLimit":-1.7976931348623157E308,
                     "intervalLoggingPeriod":1,
                     "intervalLoggingSampleWindowSize":0,
                     "overrideIntervalLoggingSamples":false,
                     "preventSetExtremeValues":false,
                     "purgeOverride":false,
                     "purgePeriod":1,
                     "readPermission":"",
                     "setExtremeHighLimit":1.7976931348623157E308,
                     "setExtremeLowLimit":-1.7976931348623157E308,
                     "setPermission":"",
                     "textRenderer":{
                        "type":"ANALOG",
                        "useUnitAsSuffix":true,
                        "unit":"",
                        "renderedUnit":"",
                        "format":"0.00"
                     },
                     "tolerance":0.0
                  }
               ]
            }
            
            1. Next we'll need a scripting data source and four points, "Set Occupied Heating Setpoint", "Set Occupied Cooling Setpoint", "Occupied Heating Setpoint" and "Occupied Cooling Setpoint". I'll just use their acronyms as variable names. They're all settable numeric. The script body may look like (the modbus point from step 1 will be in the context, let's say variable name "occupiedSetpoints",
            if( sohs.value != -1 ) { //Someone is trying to set the heating setpoint
              if( socs.value != -1) {
                occupiedSetpoints.set( socs.value<<8 | sohs.value ); //we may need to set both
                sohs.set( -1 ); //Clear it so we don't keep setting too much
                socs.set( -1 );
              } else {
                occupiedSetpoints.set( ocs.value<<8 | sohs.value );
                sohs.set( -1 );
              }
            } else if( socs.value != -1 ) {
              occupiedSetpoints.set( socs.value<<8 | ohs.value );
              socs.set( -1 );
            }
            

            That whole data source's configuration might look like this:

            {
               "dataSources":[
                  {
                     "xid":"DS_760b73e5-5444-4a8e-9258-48648b093b04",
                     "name":"HandleWonkiness",
                     "enabled":false,
                     "type":"SCRIPTING",
                     "alarmLevels":{
                        "SCRIPT_ERROR":"URGENT",
                        "DATA_TYPE_ERROR":"URGENT",
                        "POLL_ABORTED":"URGENT",
                        "LOG_ERROR":"URGENT"
                     },
                     "purgeType":"YEARS",
                     "context":[
                        {
                           "varName":"occupiedSetpoints",
                           "dataPointXid":"DP_00c2c077-a245-4768-aed8-774bb0f7f982"
                        }
                     ],
                     "logLevel":"NONE",
                     "cronPattern":"0\/1 * * * * ?",
                     "executionDelaySeconds":0,
                     "historicalSetting":false,
                     "script":"if( sohs.value != -1 ) { \/\/Someone is trying to set the heating setpoint\r\n  if( socs.value != -1) {\r\n    occupiedSetpoints.set( socs.value<<8 | sohs.value ); \/\/we may need to set both\r\n    sohs.set( -1 ); \/\/Clear it so we don't keep setting too much\r\n    socs.set( -1 );\r\n  } else {\r\n    occupiedSetpoints.set( ocs.value<<8 | sohs.value );\r\n    sohs.set( -1 );\r\n  }\r\n} else if( socs.value != -1 ) {\r\n  occupiedSetpoints.set( socs.value<<8 | ohs.value );\r\n  socs.set( -1 );\r\n}",
                     "scriptPermissions":{
                        "customPermissions":"",
                        "dataPointReadPermissions":"superadmin",
                        "dataPointSetPermissions":"superadmin",
                        "dataSourcePermissions":"superadmin"
                     },
                     "editPermission":"",
                     "purgeOverride":false,
                     "purgePeriod":1
                  }
               ],
               "dataPoints":[
                  {
                     "xid":"DP_1dd39f06-c252-4bf2-bd75-27108ad1812c",
                     "name":"Set Occupied Heating Setpoint",
                     "enabled":true,
                     "loggingType":"ALL",
                     "intervalLoggingPeriodType":"MINUTES",
                     "intervalLoggingType":"AVERAGE",
                     "purgeType":"YEARS",
                     "pointLocator":{
                        "dataType":"NUMERIC",
                        "settable":true,
                        "varName":"sohs"
                     },
                     "eventDetectors":[
                     ],
                     "plotType":"SPLINE",
                     "rollup":"NONE",
                     "unit":"",
                     "templateXid":"Numeric_Default",
                     "chartColour":"",
                     "chartRenderer":{
                        "type":"IMAGE",
                        "timePeriodType":"DAYS",
                        "numberOfPeriods":1
                     },
                     "dataSourceXid":"DS_760b73e5-5444-4a8e-9258-48648b093b04",
                     "defaultCacheSize":1,
                     "deviceName":"HandleWonkiness",
                     "discardExtremeValues":false,
                     "discardHighLimit":1.7976931348623157E308,
                     "discardLowLimit":-1.7976931348623157E308,
                     "intervalLoggingPeriod":1,
                     "intervalLoggingSampleWindowSize":0,
                     "overrideIntervalLoggingSamples":false,
                     "preventSetExtremeValues":false,
                     "purgeOverride":false,
                     "purgePeriod":1,
                     "readPermission":"",
                     "setExtremeHighLimit":1.7976931348623157E308,
                     "setExtremeLowLimit":-1.7976931348623157E308,
                     "setPermission":"",
                     "textRenderer":{
                        "type":"ANALOG",
                        "useUnitAsSuffix":true,
                        "unit":"",
                        "renderedUnit":"",
                        "format":"0.00"
                     },
                     "tolerance":0.0
                  },
                  {
                     "xid":"DP_b57761e9-ce04-41d2-9ea8-8018eab7ec4e",
                     "name":"Set Occupied Cooling Setpoint",
                     "enabled":true,
                     "loggingType":"ALL",
                     "intervalLoggingPeriodType":"MINUTES",
                     "intervalLoggingType":"AVERAGE",
                     "purgeType":"YEARS",
                     "pointLocator":{
                        "dataType":"NUMERIC",
                        "settable":true,
                        "varName":"socs"
                     },
                     "eventDetectors":[
                     ],
                     "plotType":"SPLINE",
                     "rollup":"NONE",
                     "unit":"",
                     "templateXid":"Numeric_Default",
                     "chartColour":"",
                     "chartRenderer":{
                        "type":"IMAGE",
                        "timePeriodType":"DAYS",
                        "numberOfPeriods":1
                     },
                     "dataSourceXid":"DS_760b73e5-5444-4a8e-9258-48648b093b04",
                     "defaultCacheSize":1,
                     "deviceName":"HandleWonkiness",
                     "discardExtremeValues":false,
                     "discardHighLimit":1.7976931348623157E308,
                     "discardLowLimit":-1.7976931348623157E308,
                     "intervalLoggingPeriod":1,
                     "intervalLoggingSampleWindowSize":0,
                     "overrideIntervalLoggingSamples":false,
                     "preventSetExtremeValues":false,
                     "purgeOverride":false,
                     "purgePeriod":1,
                     "readPermission":"",
                     "setExtremeHighLimit":1.7976931348623157E308,
                     "setExtremeLowLimit":-1.7976931348623157E308,
                     "setPermission":"",
                     "textRenderer":{
                        "type":"ANALOG",
                        "useUnitAsSuffix":true,
                        "unit":"",
                        "renderedUnit":"",
                        "format":"0.00"
                     },
                     "tolerance":0.0
                  },
                  {
                     "xid":"DP_654eebab-d687-4083-8f09-80a160d9e375",
                     "name":"Occupied Heating Setpoint",
                     "enabled":true,
                     "loggingType":"ALL",
                     "intervalLoggingPeriodType":"MINUTES",
                     "intervalLoggingType":"AVERAGE",
                     "purgeType":"YEARS",
                     "pointLocator":{
                        "dataType":"NUMERIC",
                        "settable":true,
                        "varName":"ohs"
                     },
                     "eventDetectors":[
                     ],
                     "plotType":"SPLINE",
                     "rollup":"NONE",
                     "unit":"",
                     "templateXid":"Numeric_Default",
                     "chartColour":"",
                     "chartRenderer":{
                        "type":"IMAGE",
                        "timePeriodType":"DAYS",
                        "numberOfPeriods":1
                     },
                     "dataSourceXid":"DS_760b73e5-5444-4a8e-9258-48648b093b04",
                     "defaultCacheSize":1,
                     "deviceName":"HandleWonkiness",
                     "discardExtremeValues":false,
                     "discardHighLimit":1.7976931348623157E308,
                     "discardLowLimit":-1.7976931348623157E308,
                     "intervalLoggingPeriod":1,
                     "intervalLoggingSampleWindowSize":0,
                     "overrideIntervalLoggingSamples":false,
                     "preventSetExtremeValues":false,
                     "purgeOverride":false,
                     "purgePeriod":1,
                     "readPermission":"",
                     "setExtremeHighLimit":1.7976931348623157E308,
                     "setExtremeLowLimit":-1.7976931348623157E308,
                     "setPermission":"",
                     "textRenderer":{
                        "type":"ANALOG",
                        "useUnitAsSuffix":true,
                        "unit":"",
                        "renderedUnit":"",
                        "format":"0.00"
                     },
                     "tolerance":0.0
                  },
                  {
                     "xid":"DP_879c5c66-784c-4d5e-960e-96cda59bb260",
                     "name":"Occupied Cooling Setpoint",
                     "enabled":true,
                     "loggingType":"ALL",
                     "intervalLoggingPeriodType":"MINUTES",
                     "intervalLoggingType":"AVERAGE",
                     "purgeType":"YEARS",
                     "pointLocator":{
                        "dataType":"NUMERIC",
                        "settable":true,
                        "varName":"ocs"
                     },
                     "eventDetectors":[
                     ],
                     "plotType":"SPLINE",
                     "rollup":"NONE",
                     "unit":"",
                     "templateXid":"Numeric_Default",
                     "chartColour":"",
                     "chartRenderer":{
                        "type":"IMAGE",
                        "timePeriodType":"DAYS",
                        "numberOfPeriods":1
                     },
                     "dataSourceXid":"DS_760b73e5-5444-4a8e-9258-48648b093b04",
                     "defaultCacheSize":1,
                     "deviceName":"HandleWonkiness",
                     "discardExtremeValues":false,
                     "discardHighLimit":1.7976931348623157E308,
                     "discardLowLimit":-1.7976931348623157E308,
                     "intervalLoggingPeriod":1,
                     "intervalLoggingSampleWindowSize":0,
                     "overrideIntervalLoggingSamples":false,
                     "preventSetExtremeValues":false,
                     "purgeOverride":false,
                     "purgePeriod":1,
                     "readPermission":"",
                     "setExtremeHighLimit":1.7976931348623157E308,
                     "setExtremeLowLimit":-1.7976931348623157E308,
                     "setPermission":"",
                     "textRenderer":{
                        "type":"ANALOG",
                        "useUnitAsSuffix":true,
                        "unit":"",
                        "renderedUnit":"",
                        "format":"0.00"
                     },
                     "tolerance":0.0
                  }
               ]
            }
            

            Note that you could use a different value than -1, but most people don't set their A/C values anywhere near freezing so you're probably okay there.

            1. And finally we'll need to have some point links from the modbus point to our two points for each of the current setpoints. That means in the point link source point for both links and "Occpied Heating Setpoint" is the target of one (The other is Occupied Cooling Setpoint).

            One link will have the body,

            return source.value & 0xFF;
            

            the other will be

            return source.value>>8 & 0xFF;
            

            Those may have a configuration like:

            {
               "pointLinks":[
                  {
                     "xid":"PL_eacbf9a9-d919-49f4-88d1-ed59cb19c243",
                     "sourcePointId":"DP_00c2c077-a245-4768-aed8-774bb0f7f982",
                     "targetPointId":"DP_879c5c66-784c-4d5e-960e-96cda59bb260",
                     "event":"CHANGE",
                     "logLevel":"NONE",
                     "disabled":false,
                     "script":"return source.value>>8 & 0xFF;",
                     "scriptPermissions":{
                        "customPermissions":"",
                        "dataPointReadPermissions":"superadmin",
                        "dataPointSetPermissions":"superadmin",
                        "dataSourcePermissions":"superadmin"
                     },
                     "writeAnnotation":false
                  },
                  {
                     "xid":"PL_94a9ac52-4770-4b90-b3a3-a294d60b2d03",
                     "sourcePointId":"DP_00c2c077-a245-4768-aed8-774bb0f7f982",
                     "targetPointId":"DP_654eebab-d687-4083-8f09-80a160d9e375",
                     "event":"CHANGE",
                     "logLevel":"NONE",
                     "disabled":false,
                     "script":"return source.value & 0xFF;",
                     "scriptPermissions":{
                        "customPermissions":"",
                        "dataPointReadPermissions":"superadmin",
                        "dataPointSetPermissions":"superadmin",
                        "dataSourcePermissions":"superadmin"
                     },
                     "writeAnnotation":false
                  }
               ]
            }
            
            1 Reply Last reply Reply Quote 0