    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    Mango connet with BACnet ms/tp device through PC RS-232 port

    Mango General
    3
    8
    4.7k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • J
      jackchang
      last edited by

      Hello,

      I try to connet the BACnet MS/TP device through PC RS-232 port. The ms/tp controller conneted with rs-485 to rs-323 converter, then connect to PC rs-232 port.

      I have set up BACnet device property in the system setting pages:

      0_1471936282336_Screenshot from 2016-08-23 14:55:04.png

      But I can not discovery the ms/tp controllers:
      0_1471936359261_Screenshot from 2016-08-23 14:56:05.png

      Can anybody kindly support me on this?

      Best regards,
      Jack Chang

      1 Reply Last reply Reply Quote 0
      • J
        jackchang
        last edited by

        Sometimes will show the ms/tp device:
        0_1471937349012_1.PNG

        But then show "timeout waiting for response", and no BACnet objests show in the table.

        1 Reply Last reply Reply Quote 0
        • J
          jackchang
          last edited by

          Hello,

          Nobody answer this question?

          I check my setting many times. Today I got this:
          0_1472553798234_Screenshot from 2016-08-30 18:40:57.png

          1 Reply Last reply Reply Quote 0
          • J
            jackchang
            last edited by

            Hello All,

            I changed another RS232 to RS485 conventer, and the MS/TP controllers has been poll in!

            J 1 Reply Last reply Reply Quote 0
            • zdabbasZ
              zdabbas
              last edited by

              Hi

              I did have problems with Bacnet MS/TP, the only way I could do discovery or proper polling is through a Johnson controller or .
              But I have an idea that may work and will let you know soon, I'm going to get a Bacnet TCP to Bacnet MS/tp and try it that way.

              J 1 Reply Last reply Reply Quote 0
              • J
                jackchang @zdabbas
                last edited by

                @zdabbas
                Hello zdabbsa,

                Thanks for your reply. Do you want to route the ms/tp controllers to B/IP through the Johnson controller? I don't know if Mango can read/write the ms/tp controllers's data through the BACnet router.

                Best Regards,
                Jack Chang

                1 Reply Last reply Reply Quote 0
                • zdabbasZ
                  zdabbas
                  last edited by zdabbas

                  Jack
                  At this point the Johnson is doing the timing and helping with the discovery of the Backnet ms/tp units. my problem is that when I remove the Johnson controller from the network Mango is unable to control or send commands to them through bacnet ms/tp. my suspesion is that Mango MS/tp protocol is not able to give the right timing and speed of the serial to the units. but when the johnson put back in the network every runs fine.

                  now I have a small delay in response time from the bacnet units the delay is between 4-9 sec and I'm suspecting the Johnson controller is causing it. since I have Bacnet TCP running with no problems I thought I would install a bacnet ms/tp to bacnet tcp converter and have the mango on the TCP side to see if the delay problem can be resolved.

                  1 Reply Last reply Reply Quote 0
                  • J
                    jrobinson @jackchang
                    last edited by

                    @jackchang I know this was 2 years ago, but if you're still around could you point me to which RS232 to RS485 converter you used?