    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    TCP/IP Data Source, Talking to MOXA Serial RS232?

    User help
    4
    6
    5.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • danD
      dan
      last edited by

      Hey Guys, long time no chat, Mango works so well I haven't had to touch the system I put in for running an irrigation system.

      Now I have a case where I have the following setup:

      Mango -> TCP/IP Data Source -> Moxa Ethernet to RS232 Converter -> Solar Reg (RS232)

      I've tried a few things but struggling to get my head around the syntax required, I just don't get any response. The Moxa is in TCP Server Mode which connects to the serial port and waits for instruction from the TCP Port 4001.

      I have to send the regulator the following commands for example:

      AA 55 AA 55 AA 55 EB 90 EB 90 EB 90

      I had a look at the wiki and tried a couple of things on there related to both serial data source and TCP/IP data source with no luck.

      Any help would be much appreciated thanks :)

      Cheers
      Dan

      1 Reply Last reply Reply Quote 0
      • duncanD
        duncan
        last edited by duncan

        Hi Dan,

        I presume you are using one of the Moxa MGate series Modbus TCP gateways. We use these devices extensively with Mango and they are fairly easy to setup.
        My advice is to ensure you have the correct wiring on the DB9 from your RS232 device to your Mgate. On the Moxa Mgate DB9 pin 2 is RxD, Pin 3 is TxD and pin 5 is ground.
        Download and install the Mgate manager software. Configure the Mgate accordingly RTU slave or ASCI Slave.
        Ensure you have the correct settings in the Serial section that corrspond to your RS232 device.
        Ensure you have the correct IP settings. Save this configuration to the Mgate device. Check your IP settings on Mango as well.
        Download a copy of Modscan or similar and test your Modbus connectivity. If you cant see any data then Mango cant either. The default port is 502 (TCP) on both Mango and the Mgate.

        Cheers

        Duncan

        1 Reply Last reply Reply Quote 0
        • danD
          dan
          last edited by

          Hi Duncan, thanks for your reply. I too have a lot of MGate MODBUS units around, this setup unfortunately is direct serial and not MODBUS.
          We are using NPort 5150's to convert RS232 serial to Ethernet, there is no MODBUS involved here. The Moxa listens on port 4001.
          If it was MODBUS I'd probably have no issues as we've done it before many times. The regulator we need to talk to only talks serial.
          The later models do support MODBUS but we are wanting to talk serial for the old ones.

          Regards
          Dan

          1 Reply Last reply Reply Quote 0
          • Woody BeverleyW
            Woody Beverley
            last edited by

            Perhaps Wireshark can help you with this troubleshooting.

            Shooting from the hip.....

            We suspect maybe the issue is in sending HEX values. Since the datasource uses Strings maybe you are trying to send binary values but they are being transmitted as ASCII characters.

            Pretty sure the data source converts the Read command and Write command to the UTF-8 charset. This makes sending 0xAA (170 decimal) a problem because there is no UTF-8 char for that value.

            -WoodyB

            1 Reply Last reply Reply Quote 0
            • danD
              dan
              last edited by

              Hi Woody, thanks for that. I will investigate further.
              I think we'll definitely have more luck with the newer regs that support just straight MODBUS over IP, much easier to setup ;)

              Cheers
              Dan