    Modbus4J Modbus RTU master
    24 Posts 3 Posters 39.9k Views 2 Watching
    • jeremyhJ Offline
      jeremyh
      Try using 3110 and and 3109 in your Java code then. Modbus4J is pretty 'smart' and probably makes such an adjustment for you.
      You might like to get a modbus scanning application and run it on your PC to verify that the data is where you think it is, Mango has such a tool built in so if you have already installed Mango I would suggest using that. Just set up a Modbus TCP data source and use the Modbus read data function which will return the registers in Hex:
      You can also try the 'point locator test', click the 'read' button and Mango will return the value it sees there.
      amer jamilA 1 Reply Last reply Reply Quote 0
      • amer jamilA Offline
        amer jamil @jeremyh
        @jeremyh Thank you so much jeremy. You really save my life. I try 3109 in my java code, and it show the correct value that I want. Thank you so much for helping me out. Can you explain more on how you get the 3109 value ? Why in the documentation it say that 3110 ?
        God bless you Jeremy..
        • jeremyhJ Offline
          jeremyh
          Modbus4J already does the 'subtract 40001' bit for you, so your colleague gave you a bit of misdirection there. It's still usually necessary if you are setting up a Modbus master in a PLC or something.
          And some manufacturers start counting registers from 0 and some from 1, so sometimes (actually, often) what you think is register 3110 in your slave is 3109 according to your master.
          A modbus scanner which shows you a whole bunch of registers is usually handy for figuring this out.
          Just trial and error..
            amer jamil @jeremyh
            @jeremyh so what should I do next is, minus 1 from all the register that I want since it start count from 0 right ? Thank you so much again. Thank you for helping me around since the beginning.
            jeremyhJ 1 Reply Last reply Reply Quote 0
            • jeremyhJ Offline
              jeremyh @amer jamil
              Yes subtract 1 from all the registers in the documentation.
              • jeremyhJ Offline
                jeremyh
                Out of curiosity are you logging all the data in a database on disk? Or just in memory to draw the graphs?
                amer jamilA 2 Replies Last reply Reply Quote 0
                  amer jamil @jeremyh
                  @jeremyh yaa, the data will be insert into the database every minute.
                    amer jamil @jeremyh
                    @jeremyh Hello Jeremy. Want to ask you one more question. I am not from the Electric background. So, I find a difficulty in calculating the power consumption of the meter. For you information, my system going to add the data in the database for every one minute. How am i going to calculate the power consumption for the device for a day (24 hours). I have Kw value for every minute.
                    Do I have to add the Kw value for every minute up to the whole day ?
                    Thank you.
                    • jeremyhJ Offline
                      jeremyh
                      Power (kw) is an instantaneous measurement. Energy (kWh), which is sounds like you want, is Power over Time. One kW of power being drawn for one hour is 1 kWh of energy. Half a kW for two hours is still 1 kWh.
                      To convert kW to kWh you would have to integrate the kW measurement i.e calculate the area under a plot of power over time. This is only as accurate as your measurement/sampling interval which is only 1 minute.
                      The real answer is to find the registers for cumulative energy (kWh and kVAh generally) in your meters and use that measurement to compute hourly/daily/annual kWh and kVAh energies. It will be a lot easier and a lot more accurate than trying to work it out yourself.
                        amer jamil @jeremyh
                        @jeremyh below is the sample of my database.
                        could you teach me how to calculate.
                        • jeremyhJ Offline
                          jeremyh
                          Just use the deltas. In energy/utility metering a 15 minute interval is generally used.
                          at 10:00am the MWh used was 122.858
                          at 10:15am the MWh used was 122.859
                          122.859 - 122.858 = 0.001 MWh or 1kWh used in the 15 minute period.
                          Because you are measuring in MWh you lack the resolution to get tenths of kWh, so you should consider storing more decimals if you can, or reading from a kWh register if you can.
                          If that's not an option then you could integrate using the method/s discussed here: http://physics.stackexchange.com/questions/109295/calculating-kwh-from-time-series-of-kw
                          You could very crudely say that if the average demand over the 15 minute period is 4.75kW then the energy consumed in that 15 minute period (which is 1/4th of an hour) is (1/4 hours)*4.75 kWh = 1.1kWh.
                            amer jamil @jeremyh
                            @jeremyh
                            Is it correct ? Do i need to sum all the KW and I will get the total consumption for an hour ?
                            (1/4 * 4.8) + (1/4 * 4.9) + (1/4 * 4.8) + (1/4 * 4.8) = 4.825 KWH
                            • jeremyhJ Offline
                              jeremyh
                              No. You would need to do:
                              (1/samples per hour) * (sum of kilowatts over period) = kilowatt-hours
                              i.e. (can't believe you made me type this):
                              (1/60) * (4.872+4.873+4.808+4.896+4.744+4.768+4.896+4.832+4.816+4.776+4.888+4.872+4.760+4.840+4.792) = 1.2kWh
                              This is honestly a really bad and dumb way to do this though. It is very inaccurate and if you miss any measurements your energy will be even further off. Just add the kWh register (rather than MWh) from your panel meter and calculate the difference every period - that is what it's there for!
                              If you ended up with 15-minute energy kWh then to get hourly energy you would just sum the kWh. Energy can be added to energy.