• Recent
    • Tags
    • Popular
    • Register
    • Login
    1. Home
    2. ottawa_admin

    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website
    O
    • Profile
    • Following 0
    • Followers 0
    • Topics 3
    • Posts 8
    • Best 1
    • Controversial 0
    • Groups 0

    ottawa_admin

    @ottawa_admin

    1
    Reputation
    191
    Profile views
    8
    Posts
    0
    Followers
    0
    Following
    Joined Last Online

    ottawa_admin Unfollow Follow

    Best posts made by ottawa_admin

    • RE: MangoES Timestamp Does Not Match Local Time

      @joelhaggar Thank you for the information. I was able to look through the NTP and timesyncd config files, and things looked alright. However I discovered I was having problems with internet connectivity and DNS resolving on the device in question. I discovered that it didn't have a default IP routing path. Considering we didn't need an outwards internet connection for our projects, makes sense that I didn't pick up on it.

      I looked at another MangoES device on the same network and discovered it had an internet connection, so my issue was isolated. I added a default IP route using "sudo ip route add default via XX.XX.XX.XX dev eth0", and borrowed the gateway info from a functioning device. I then overwrote the DNS resolve file found at "/etc/resolv.conf" with "nameserver 8.8.8.8".

      Not sure how things go out of hand in the first place, but I used "sudo date +%T -s "hh:mm:ss" to bring the unsynced time within a few seconds of the local time. I then forced the NTP to restart using "sudo service ntp restart", checked the ntp status using "sudo service ntp status", and then it looked like my ntp hosts were being resolved correctly and the time had resynced.

      Appreciate the help Joel!

      posted in User help
      O
      ottawa_admin

    Latest posts made by ottawa_admin

    • RE: MangoES Timestamp Does Not Match Local Time

      @joelhaggar I ran "sudo service networking restart" and resolv.conf doesn't appear to have changed. I also ran "sudo service mango restart" and still no change. Although please advise if I should do another test.

      Thanks for the tip Mr. Sysak! :) Definitely would have been a concern if it was being overwritten and the drift continued.

      posted in User help
      O
      ottawa_admin
    • RE: MangoES Timestamp Does Not Match Local Time

      @joelhaggar Thank you for the information. I was able to look through the NTP and timesyncd config files, and things looked alright. However I discovered I was having problems with internet connectivity and DNS resolving on the device in question. I discovered that it didn't have a default IP routing path. Considering we didn't need an outwards internet connection for our projects, makes sense that I didn't pick up on it.

      I looked at another MangoES device on the same network and discovered it had an internet connection, so my issue was isolated. I added a default IP route using "sudo ip route add default via XX.XX.XX.XX dev eth0", and borrowed the gateway info from a functioning device. I then overwrote the DNS resolve file found at "/etc/resolv.conf" with "nameserver 8.8.8.8".

      Not sure how things go out of hand in the first place, but I used "sudo date +%T -s "hh:mm:ss" to bring the unsynced time within a few seconds of the local time. I then forced the NTP to restart using "sudo service ntp restart", checked the ntp status using "sudo service ntp status", and then it looked like my ntp hosts were being resolved correctly and the time had resynced.

      Appreciate the help Joel!

      posted in User help
      O
      ottawa_admin
    • RE: MangoES Timestamp Does Not Match Local Time

      @joelhaggar the previous screenshot was showing that the network time on the bottom right was 4:16pm (matched local time). And that the point logging history was showing a most recent update time of ~3:53pm with most recent point logged at ~3:52pm.

      When a new data point is logged, its timestamp matches the system time. However the issue is that system time doesn't match the time zone time exactly - it's delayed by ~24 mins.

      I confirmed through command line in PuTTY that the Mango's system time is behind by ~24 mins (10:12am) compared to the local time of 10:36am.

      See photo: Mango - Timestamp Discrepancy -Terminal.PNG

      posted in User help
      O
      ottawa_admin
    • MangoES Timestamp Does Not Match Local Time

      Hi there,

      I'm using a MangoES device with core v3.7.7.

      I've set the time zone of the MangoES to America/Toronto (through the UI and confirmed it is correctly set in the FTP directory in /etc/timezone). I restarted the database, however it appears that there is a ~24 minute delay between the Mango server time and local time. It affects all Modbus point logging and script executions, which is not ideal. I confirmed using javascript (new Date()) that the time is in fact delayed by 24 mins.

      Are there some steps I could follow to ensure the server time lines up with the time zone I've set?

      It could also be an issue with the overarching network - not savvy enough to know what influences the Mango time. Any help would be appreciated.

      See photo (I refreshed the datapt History before taking the sc) Mango - Timestamp Discrepancy.PNG

      posted in User help
      O
      ottawa_admin
    • Mango not Accessible by Web - Hung-Up During Start-Up?

      HI there,
      I can't seem to access one of our Mango instances through the UI on the web. However, I can still access through FTP and SSH. When I try restarting the instance through SSH it seems to get hung up on the last line in the log below. Any help would be appreciated.

      What initially caused the web interface to be inaccessible ("This site can’t be reached" on Google Chrome) was me stopping and starting the instance through SSH in preparation for upgrading the core library and all modules. At one point, while refreshing the browser at hostname/ui/login, the following error came up: "Error bootstrapping Mango UI app: Failed to fetch pre-login bootstrap data." I only saw this error once and could not replicate it.

      From the ma.log:

      INFO  2020-10-02T18:42:55,097 (com.serotonin.m2m2.Main.main:121) - Starting Mango 3.7.7 with Schema Version: 29 
      WARN  2020-10-02T18:42:55,817 (com.serotonin.m2m2.Main.loadModules:443) - Module mangoESConfiguration: this module requires a core version of 3.5, which does not match the current core version of 3.7.7. Module not loaded. 
      INFO  2020-10-02T18:42:56,600 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'sqlds', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,648 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'mqttClientDataSource', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,658 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'acurite', v3.7.0 by Terry Packer 
      INFO  2020-10-02T18:42:56,666 (com.serotonin.m2m2.util.DocumentationManifest.parseManifestFile:60) - Documentation manifest file not found: /opt/mango/web/modules/acurite/web/dox/manifest.xml 
      INFO  2020-10-02T18:42:56,669 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'TCPIP', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,678 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'asciiFile', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,688 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'sqlConsole', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,698 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'galil', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,707 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'lang_zh', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,709 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'sstGlobalScripts', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,719 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'mbus', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,733 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'log4jDS', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,744 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'persistent', v3.7.1 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,756 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'vmstat', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,766 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'mangoApi', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,778 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'pointLinks', v3.7.1 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,789 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'log4JReset', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,792 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'sstTheme', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,798 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'jmxds', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,807 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'twilio', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,820 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'meta', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,832 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'excelReports', v3.7.1 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,848 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'snmp', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,857 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'http', v3.7.1 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,871 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'controlcore', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,879 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'advancedComponents', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,883 (com.serotonin.m2m2.util.DocumentationManifest.parseManifestFile:60) - Documentation manifest file not found: /opt/mango/web/modules/advancedComponents/web/dox/manifest.xml 
      INFO  2020-10-02T18:42:56,888 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'jsonFileImport', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,896 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'graphicalViews', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,919 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'scripting', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,928 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'watchlists', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,943 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'dataPointDetailsView', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,951 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'modbus', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,962 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'slackPublisher', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,973 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'lang_es', v3.7.1 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,980 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'onewire', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,989 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'virtualDS', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:56,997 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'advancedScheduler', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,000 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'dashboardDesigner', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,004 (com.serotonin.m2m2.util.DocumentationManifest.parseManifestFile:60) - Documentation manifest file not found: /opt/mango/web/modules/dashboardDesigner/web/dox/manifest.xml 
      INFO  2020-10-02T18:42:57,007 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'dataFile', v3.7.1 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,024 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'mangoUI', v3.7.7 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,029 (com.serotonin.m2m2.util.DocumentationManifest.parseManifestFile:60) - Documentation manifest file not found: /opt/mango/web/modules/mangoUI/web/dox/manifest.xml 
      INFO  2020-10-02T18:42:57,059 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'ssh', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,068 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'dnp3', v3.7.3 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,077 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'dataImport', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,085 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'pop3', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,093 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'cloudConnect', v3.7.1 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,097 (com.serotonin.m2m2.util.DocumentationManifest.parseManifestFile:60) - Documentation manifest file not found: /opt/mango/web/modules/cloudConnect/web/dox/manifest.xml 
      INFO  2020-10-02T18:42:57,099 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'lang_pt', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,113 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'deviceConfig', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,117 (com.serotonin.m2m2.util.DocumentationManifest.parseManifestFile:60) - Documentation manifest file not found: /opt/mango/web/modules/deviceConfig/web/dox/manifest.xml 
      INFO  2020-10-02T18:42:57,120 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'templateConfig', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,128 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'Haystack', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,137 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'opcda', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,140 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'MangoIOTools', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,144 (com.serotonin.m2m2.util.DocumentationManifest.parseManifestFile:60) - Documentation manifest file not found: /opt/mango/web/modules/MangoIOTools/web/dox/manifest.xml 
      INFO  2020-10-02T18:42:57,146 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'BACnet', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,156 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'pid', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,164 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'zwave', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,184 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'egauge', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,192 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'scheduledEvents', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,202 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'loggingConsole', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,210 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'sstGraphics', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,225 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'mangoNoSqlDatabase', v3.7.1 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,235 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'reports', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,245 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'maintenanceEvents', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,253 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'serial', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:42:57,261 (com.serotonin.m2m2.Main.loadModules:650) - Loading module 'internal', v3.7.0 by Infinite Automation Systems Inc. 
      INFO  2020-10-02T18:43:07,533 (com.serotonin.m2m2.Lifecycle.loadLic:583) - Checking license... 
      WARN  2020-10-02T18:43:07,811 (com.serotonin.m2m2.TimedLicenseRegistrar.checkLicenses:64) - Mango NoSQL database is running in free mode, Mango will shutdown at 2:43:07 3/10/2020. 
      INFO  2020-10-02T18:43:08,132 (com.serotonin.m2m2.db.H2Proxy.initializeImpl:64) - Initializing H2 connection manager 
      INFO  2020-10-02T18:43:10,292 (com.serotonin.m2m2.db.upgrade.DBUpgrade.checkUpgrade:38) - Starting instance with core version 3.7.7, schema v29 
      INFO  2020-10-02T18:43:10,292 (com.infiniteautomation.nosql.MangoNoSqlProxy.initialize:77) - Starting MangoNoSql Database 
      INFO  2020-10-02T18:43:10,406 (com.infiniteautomation.tsdb.impl.IasTsdbImpl.<init>:144) - Database at /opt/mango/databases/mangoTSDB started 
      INFO  2020-10-02T18:43:10,515 (com.infiniteautomation.tsdb.impl.IasTsdbImpl.<init>:173) - Empty dir delete for database at /opt/mango/databases/mangoTSDB took 69ms 
      INFO  2020-10-02T18:43:10,532 (com.infiniteautomation.tsdb.impl.IasTsdbImpl.<init>:144) - Database at /opt/mango/databases/mangoTSDBAux started 
      INFO  2020-10-02T18:43:10,559 (com.infiniteautomation.tsdb.impl.IasTsdbImpl.<init>:173) - Empty dir delete for database at /opt/mango/databases/mangoTSDBAux took 0ms 
      INFO  2020-10-02T18:43:23,475 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:133) - Spring context 'runtimeContext' refreshed: org.springframework.context.annotation.AnnotationConfigApplicationContext@da6cbd 
      INFO  2020-10-02T18:43:23,492 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextStarted:147) - Spring context 'runtimeContext' started: org.springframework.context.annotation.AnnotationConfigApplicationContext@da6cbd 
      INFO  2020-10-02T18:43:24,008 (com.serotonin.m2m2.rt.DataSourceGroupInitializer.initialize:77) - Initializing 5 NORMAL priority data sources in 8 threads. 
      INFO  2020-10-02T18:43:24,705 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initializeDataSourceStartup:408) - Data source Mango Internal took 691ms to start 
      INFO  2020-10-02T18:43:24,711 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initializeDataSourceStartup:408) - Data source MangoES System took 697ms to start 
      INFO  2020-10-02T18:43:24,891 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initializeDataSourceStartup:408) - Data source MangoES System took 877ms to start 
      INFO  2020-10-02T18:43:25,213 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initializeDataSourceStartup:408) - Data source 309_Legget took 1203ms to start 
      INFO  2020-10-02T18:43:25,394 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initializeDataSourceStartup:408) - Data source BACNET_IP took 1382ms to start 
      INFO  2020-10-02T18:43:25,473 (com.serotonin.m2m2.rt.DataSourceGroupInitializer.initialize:109) - Initialization of 5 NORMAL priority data sources took 1465ms 
      INFO  2020-10-02T18:43:25,473 (com.serotonin.m2m2.rt.DataSourceGroupInitializer.initialize:77) - Initializing 1 LAST priority data sources in 8 threads. 
      INFO  2020-10-02T18:43:27,464 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initializeDataSourceStartup:408) - Data source KRP - 309 Legget - Data took 1989ms to start 
      INFO  2020-10-02T18:43:27,477 (com.serotonin.m2m2.rt.DataSourceGroupInitializer.initialize:109) - Initialization of 1 LAST priority data sources took 2004ms 
      INFO  2020-10-02T18:43:27,707 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initialize:176) - Starting 2 Publishers... 
      INFO  2020-10-02T18:43:27,708 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initialize:178) - Starting publisher: HTTP 
      INFO  2020-10-02T18:43:27,747 (com.serotonin.m2m2.rt.RuntimeManagerImpl.startPublisher:949) - Publisher 'HTTP' took 38.809859ms to start 
      INFO  2020-10-02T18:43:27,748 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initialize:178) - Starting publisher: EO_PERSISTENT 
      INFO  2020-10-02T18:43:27,748 (com.serotonin.m2m2.rt.RuntimeManagerImpl.initialize:188) - 2 Publisher's started in 124ms 
      INFO  2020-10-02T18:43:36,255 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:133) - Spring context 'rootWebContext' refreshed: Root WebApplicationContext 
      INFO  2020-10-02T18:43:46,076 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:133) - Spring context 'jspDispatcherContext' refreshed: WebApplicationContext for namespace 'JSP_DISPATCHER-servlet' 
      INFO  2020-10-02T18:43:47,177 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:133) - Spring context 'restDispatcherContext' refreshed: WebApplicationContext for namespace 'REST_DISPATCHER-servlet' 
      INFO  2020-10-02T18:43:50,699 (com.serotonin.m2m2.web.mvc.rest.v1.BacnetDiscoveryRestController.<init>:54) - Creating Discovery Rest Controller 
      INFO  2020-10-02T18:43:56,855 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:133) - Spring context 'restV1Context' refreshed: WebApplicationContext for namespace 'restV1DispatcherServlet-servlet' 
      INFO  2020-10-02T18:44:08,137 (com.infiniteautomation.mango.spring.MangoRuntimeContextConfiguration.contextRefreshed:133) - Spring context 'restV2Context' refreshed: WebApplicationContext for namespace 'restV2DispatcherServlet-servlet' 
      

      Thanks!

      posted in User help
      O
      ottawa_admin
    • RE: Unable to restart Cloud Mango

      Hi Phil,

      I've got my issue partially fixed..

      I had forgotten the golden rule - when in doubt turn on and off again. I rebooted our instance in AWS and that did the trick! My restart/stop/start commands are now functioning as expected. Apologies for wasting your time with that.

      I started from a fresh database. I then installed the enterprise bundle as you recommended. I then restored my core backup (core-database-H2-Aug-17-2019_011649.zip) through the UI. All of my data sources are there, however none of my points have their previous values.

      Just wondering how I should go about doing a backup through the command line in case my backup is a different version than the current interface. I've tried following a previous forum post but I'm not quite understanding the command line sequence.

      Are the configuration backups and incremental backups important for this task?

      Thanks again!

      posted in User help
      O
      ottawa_admin
    • RE: Unable to restart Cloud Mango

      Hi @phildunlap

      Thank you for your reply. I moved my databases directory and it regenerated, with only a file named "mah2.199.lock.db" being in the directory. Still no restart/start/stop from the command line (see log file below).

      From the ma-script.log file. The very bottom lines of August 19th are when I've been playing around with it and the commands stopped working.

      Wed Oct 4 21:35:17 UTC 2017 ma-start: starting MA
      Wed Oct 4 21:35:17 UTC 2017 ma-start: MA started with Process ID 18062
      Wed Oct 18 14:57:14 UTC 2017 ma-start: MA removing pid file for dead pid: 18062
      Wed Oct 18 14:57:14 UTC 2017 ma-start: starting MA
      Wed Oct 18 14:57:14 UTC 2017 ma-start: MA started with Process ID 18983
      Fri Oct 20 17:00:50 UTC 2017 ma-restart: restart initiated...
      Fri Oct 20 17:00:54 UTC 2017 ma-start: starting MA
      Fri Oct 20 17:00:54 UTC 2017 ma-start: MA started with Process ID 14210
      Fri Oct 20 18:51:29 UTC 2017 ma-start: upgrading core...
      Fri Oct 20 18:51:32 UTC 2017 ma-start: starting MA
      Fri Oct 20 18:51:32 UTC 2017 ma-start: MA started with Process ID 18952
      Fri Oct 20 21:05:20 UTC 2017 ma-restart: restart initiated...
      Fri Oct 20 21:05:25 UTC 2017 ma-start: starting MA
      Fri Oct 20 21:05:25 UTC 2017 ma-start: MA started with Process ID 24734
      Fri Oct 20 21:19:09 UTC 2017 ma-stop: stop initiated...
      Fri Oct 20 21:19:12 UTC 2017 ma-start: MA explicitly stopped. Exiting restart loop
      Fri Oct 20 21:19:12 UTC 2017 ma-start: MA done
      Fri Oct 20 21:20:26 UTC 2017 ma-start: starting MA
      Fri Oct 20 21:20:26 UTC 2017 ma-start: MA started with Process ID 1406
      Sat Oct 21 04:52:44 UTC 2017 ma-stop: stop initiated...
      Sat Oct 21 04:52:47 UTC 2017 ma-start: MA explicitly stopped. Exiting restart loop
      Sat Oct 21 04:52:47 UTC 2017 ma-start: MA done
      Sat Oct 21 04:54:35 UTC 2017 ma-start: starting MA
      Sat Oct 21 04:54:35 UTC 2017 ma-start: MA started with Process ID 20640
      Sat Oct 21 05:41:56 UTC 2017 ma-start: MA removing pid file for dead pid: 20640
      Sat Oct 21 05:41:56 UTC 2017 ma-start: starting MA
      Sat Oct 21 05:41:56 UTC 2017 ma-start: MA started with Process ID 1400
      Mon Oct 23 10:41:46 EDT 2017 ma-restart: restart initiated...
      Mon Oct 23 10:41:51 EDT 2017 ma-start: starting MA
      Mon Oct 23 10:41:51 EDT 2017 ma-start: MA started with Process ID 20281
      Mon Oct 23 10:41:57 EDT 2017 ma-start: no restart flag found, not restarting MA
      Mon Oct 23 10:41:57 EDT 2017 ma-start: MA done
      Mon Oct 23 10:44:45 EDT 2017 ma-start: starting MA
      Mon Oct 23 10:44:45 EDT 2017 ma-start: MA started with Process ID 20343
      Mon Oct 23 10:44:51 EDT 2017 ma-start: no restart flag found, not restarting MA
      Mon Oct 23 10:44:51 EDT 2017 ma-start: MA done
      Mon Oct 23 10:45:33 EDT 2017 ma.stop: No PID file found. Java process not stopped...
      Mon Oct 23 10:46:40 EDT 2017 ma-start: starting MA
      Mon Oct 23 10:46:40 EDT 2017 ma-start: MA started with Process ID 20402
      Mon Oct 23 10:46:46 EDT 2017 ma-start: no restart flag found, not restarting MA
      Mon Oct 23 10:46:46 EDT 2017 ma-start: MA done
      Mon Oct 23 10:47:17 EDT 2017 ma-start: starting MA
      Mon Oct 23 10:47:17 EDT 2017 ma-start: MA started with Process ID 20450
      Mon Oct 23 10:52:59 EDT 2017 ma-stop: stop initiated...
      Mon Oct 23 10:53:03 EDT 2017 ma-stop: stop initiated...
      Mon Oct 23 10:53:06 EDT 2017 ma-start: MA explicitly stopped. Exiting restart loop
      Mon Oct 23 10:53:06 EDT 2017 ma-start: MA done
      Mon Oct 23 10:53:50 EDT 2017 ma-start: starting MA
      Mon Oct 23 10:53:50 EDT 2017 ma-start: MA started with Process ID 20782
      Mon Oct 23 10:53:53 EDT 2017 ma-start: no restart flag found, not restarting MA
      Mon Oct 23 10:53:53 EDT 2017 ma-start: MA done
      Mon Oct 23 10:54:49 EDT 2017 ma-start: starting MA
      Mon Oct 23 10:54:49 EDT 2017 ma-start: MA started with Process ID 20822
      Mon Oct 23 10:54:52 EDT 2017 ma-start: no restart flag found, not restarting MA
      Mon Oct 23 10:54:52 EDT 2017 ma-start: MA done
      Mon Oct 23 10:56:42 EDT 2017 ma-start: starting MA
      Mon Oct 23 10:56:42 EDT 2017 ma-start: MA started with Process ID 20868
      Mon Oct 23 10:56:45 EDT 2017 ma-start: no restart flag found, not restarting MA
      Mon Oct 23 10:56:45 EDT 2017 ma-start: MA done
      Mon Oct 23 10:58:01 EDT 2017 ma-start: starting MA
      Mon Oct 23 10:58:01 EDT 2017 ma-start: MA started with Process ID 20918
      Mon Oct 23 10:58:04 EDT 2017 ma-start: no restart flag found, not restarting MA
      Mon Oct 23 10:58:04 EDT 2017 ma-start: MA done
      Mon Oct 23 10:58:18 EDT 2017 ma-start: starting MA
      Mon Oct 23 10:58:18 EDT 2017 ma-start: MA started with Process ID 20959
      Mon Oct 23 10:58:21 EDT 2017 ma-start: no restart flag found, not restarting MA
      Mon Oct 23 10:58:21 EDT 2017 ma-start: MA done
      Mon Oct 23 10:59:27 EDT 2017 ma-start: starting MA
      Mon Oct 23 10:59:27 EDT 2017 ma-start: MA started with Process ID 21032
      Mon Oct 23 10:59:30 EDT 2017 ma-start: no restart flag found, not restarting MA
      Mon Oct 23 10:59:30 EDT 2017 ma-start: MA done
      Mon Oct 23 10:59:53 EDT 2017 ma-start: starting MA
      Mon Oct 23 10:59:53 EDT 2017 ma-start: MA started with Process ID 21071
      Mon Oct 23 10:59:56 EDT 2017 ma-start: no restart flag found, not restarting MA
      Mon Oct 23 10:59:56 EDT 2017 ma-start: MA done
      Mon Oct 23 11:00:37 EDT 2017 ma-start: starting MA
      Mon Oct 23 11:00:37 EDT 2017 ma-start: MA started with Process ID 21111
      Mon Oct 23 11:03:44 EDT 2017 ma-start: MA already running with Process ID: 21111
      Mon Oct 23 11:03:44 EDT 2017 ma-start: MA done
      Mon Oct 23 11:03:50 EDT 2017 ma-stop: stop initiated...
      Mon Oct 23 11:03:52 EDT 2017 ma-start: MA explicitly stopped. Exiting restart loop
      Mon Oct 23 11:03:52 EDT 2017 ma-start: MA done
      Mon Oct 23 11:03:58 EDT 2017 ma-start: starting MA
      Mon Oct 23 11:03:58 EDT 2017 ma-start: MA started with Process ID 21353
      Wed Dec 6 13:18:55 EST 2017 ma-start: starting MA
      Wed Dec 6 13:18:55 EST 2017 ma-start: MA started with Process ID 22496
      Sun Dec 10 10:47:49 EST 2017 ma-start: starting MA
      Sun Dec 10 10:47:49 EST 2017 ma-start: MA started with Process ID 3402
      Mon Dec 11 16:23:49 EST 2017 ma-start: starting MA
      Mon Dec 11 16:23:49 EST 2017 ma-start: MA started with Process ID 13041
      Mon Dec 11 17:53:39 EST 2017 ma-start: starting MA
      Mon Dec 11 17:53:39 EST 2017 ma-start: MA started with Process ID 16843
      Tue Dec 19 11:57:55 EST 2017 ma-stop: stop initiated...
      Tue Dec 19 11:57:59 EST 2017 ma-stop: stop initiated...
      Tue Dec 19 11:58:00 EST 2017 ma-start: MA explicitly stopped. Exiting restart loop
      Tue Dec 19 11:58:00 EST 2017 ma-start: MA done
      Tue Dec 19 12:09:26 EST 2017 ma-start: starting MA
      Tue Dec 19 12:09:26 EST 2017 ma-start: MA started with Process ID 1449
      Wed Jan 3 15:20:02 EST 2018 ma-start: starting MA
      Wed Jan 3 15:20:02 EST 2018 ma-start: MA started with Process ID 8781
      Wed Jan 3 15:33:09 EST 2018 ma-start: starting MA
      Wed Jan 3 15:33:09 EST 2018 ma-start: MA started with Process ID 9477
      Wed Jan 3 17:02:00 EST 2018 ma-stop: stop initiated...
      Wed Jan 3 17:02:04 EST 2018 ma-start: MA explicitly stopped. Exiting restart loop
      Wed Jan 3 17:02:04 EST 2018 ma-start: MA done
      Wed Jan 3 17:02:58 EST 2018 ma-start: starting MA
      Wed Jan 3 17:02:58 EST 2018 ma-start: MA started with Process ID 13394
      Wed Jan 3 17:03:01 EST 2018 ma-start: no restart flag found, not restarting MA
      Wed Jan 3 17:03:01 EST 2018 ma-start: MA done
      Wed Jan 3 17:05:29 EST 2018 ma.stop: No PID file found. Java process not stopped...
      Wed Jan 3 17:07:01 EST 2018 ma.stop: No PID file found. Java process not stopped...
      Wed Jan 3 17:07:07 EST 2018 ma-start: starting MA
      Wed Jan 3 17:07:07 EST 2018 ma-start: MA started with Process ID 13619
      Wed Jan 3 17:07:10 EST 2018 ma-start: no restart flag found, not restarting MA
      Wed Jan 3 17:07:10 EST 2018 ma-start: MA done
      Wed Jan 3 17:07:48 EST 2018 ma-start: starting MA
      Wed Jan 3 17:07:48 EST 2018 ma-start: MA started with Process ID 13654
      Mon Jan 8 17:59:02 EST 2018 ma-start: MA already running with Process ID: 13654
      Mon Jan 8 17:59:02 EST 2018 ma-start: MA done
      Mon Jan 8 17:59:55 EST 2018 ma-stop: stop initiated...
      Mon Jan 8 18:00:22 EST 2018 ma-start: MA already running with Process ID: 13654
      Mon Jan 8 18:00:22 EST 2018 ma-start: MA done
      Mon Jan 8 18:04:14 EST 2018 ma-stop: stop initiated...
      Mon Jan 8 18:05:06 EST 2018 ma-start: MA already running with Process ID: 13654
      Mon Jan 8 18:05:06 EST 2018 ma-start: MA done
      Mon Jan 8 18:05:46 EST 2018 ma-start: MA already running with Process ID: 13654
      Mon Jan 8 18:05:46 EST 2018 ma-start: MA done
      Mon Jan 8 18:08:14 EST 2018 ma-stop: stop initiated...
      Mon Jan 8 18:09:01 EST 2018 ma-start: MA removing pid file for dead pid: 13654
      Mon Jan 8 18:09:01 EST 2018 ma-start: starting MA
      Mon Jan 8 18:09:01 EST 2018 ma-start: MA started with Process ID 1192
      Mon Jan 15 15:51:30 EST 2018 ma-stop: stop initiated...
      Mon Jan 15 15:51:30 EST 2018 ma-start: MA already running with Process ID: 1192
      Mon Jan 15 15:51:30 EST 2018 ma-start: MA done
      Mon Jan 15 15:51:51 EST 2018 ma-stop: stop initiated...
      Mon Jan 15 15:52:10 EST 2018 ma-start: MA explicitly stopped. Exiting restart loop
      Mon Jan 15 15:52:10 EST 2018 ma-start: MA done
      Mon Jan 15 15:53:32 EST 2018 ma-start: starting MA
      Mon Jan 15 15:53:32 EST 2018 ma-start: MA started with Process ID 32571
      Tue Jan 16 16:59:31 EST 2018 ma-stop: stop initiated...
      Tue Jan 16 17:03:14 EST 2018 ma-start: MA explicitly stopped. Exiting restart loop
      Tue Jan 16 17:03:14 EST 2018 ma-start: MA done
      Tue Jan 16 17:07:02 EST 2018 ma-start: running init extensions...
      Tue Jan 16 17:07:02 EST 2018 ma-start: running start extensions...
      Tue Jan 16 17:07:02 EST 2018 ma-start: starting MA
      Tue Jan 16 17:07:02 EST 2018 ma-start: MA started with Process ID 16077
      Thu Jan 18 03:18:36 EST 2018 ma-start: no restart flag found, not restarting MA
      Thu Jan 18 03:18:36 EST 2018 ma-start: MA done
      Thu Jan 18 08:54:40 EST 2018 ma-start: running init extensions...
      Thu Jan 18 08:54:40 EST 2018 ma-start: running start extensions...
      Thu Jan 18 08:54:40 EST 2018 ma-start: starting MA
      Thu Jan 18 08:54:40 EST 2018 ma-start: MA started with Process ID 22974
      Fri Jan 19 16:58:32 EST 2018 ma-start: running init extensions...
      Fri Jan 19 16:58:32 EST 2018 ma-start: running start extensions...
      Fri Jan 19 16:58:32 EST 2018 ma-start: MA removing pid file for dead pid: 22974
      Fri Jan 19 16:58:32 EST 2018 ma-start: starting MA
      Fri Jan 19 16:58:32 EST 2018 ma-start: MA started with Process ID 1212
      Fri Jan 19 16:59:31 EST 2018 ma-stop: stop initiated...
      Fri Jan 19 16:59:31 EST 2018 ma-start: MA already running with Process ID: 1212
      Fri Jan 19 16:59:31 EST 2018 ma-start: MA done
      Fri Jan 19 16:59:36 EST 2018 ma-start: no restart flag found, not restarting MA
      Fri Jan 19 16:59:36 EST 2018 ma-start: MA done
      Fri Jan 19 17:12:05 EST 2018 ma.stop: No PID file found. Java process not stopped...
      Fri Jan 19 17:12:27 EST 2018 ma-start: starting MA
      Fri Jan 19 17:12:27 EST 2018 ma-start: MA started with Process ID 3048
      Wed Jan 31 10:53:03 EST 2018 ma-stop: stop initiated...
      Wed Jan 31 10:53:03 EST 2018 ma-start: MA already running with Process ID: 3048
      Wed Jan 31 10:53:03 EST 2018 ma-start: MA done
      Wed Jan 31 10:53:10 EST 2018 ma-start: no restart flag found, not restarting MA
      Wed Jan 31 10:53:10 EST 2018 ma-start: MA done
      Wed Jan 31 10:55:18 EST 2018 ma.stop: No PID file found. Java process not stopped...
      Wed Jan 31 10:56:02 EST 2018 ma-start: starting MA
      Wed Jan 31 10:56:02 EST 2018 ma-start: MA started with Process ID 15605
      Wed Jan 31 10:56:20 EST 2018 ma-start: MA already running with Process ID: 15605
      Wed Jan 31 10:56:20 EST 2018 ma-start: MA done
      Mon Feb 5 13:42:59 EST 2018 ma-start: running stop extensions...
      Mon Feb 5 13:42:59 EST 2018 ma-stop: stop initiated...
      Mon Feb 5 13:43:03 EST 2018 ma-start: MA explicitly stopped. Exiting restart loop
      Mon Feb 5 13:43:03 EST 2018 ma-start: MA done
      Mon Feb 5 13:43:34 EST 2018 ma-start: running init extensions...
      Mon Feb 5 13:43:34 EST 2018 ma-start: running start extensions...
      Mon Feb 5 13:43:34 EST 2018 ma-start: starting MA
      Mon Feb 5 13:43:34 EST 2018 ma-start: MA started with Process ID 10499
      Mon Feb 5 15:29:28 EST 2018 ma-start: running restart extentions
      Mon Feb 5 15:29:28 EST 2018 ma-start: running start extensions...
      Mon Feb 5 15:29:28 EST 2018 ma-start: starting MA
      Mon Feb 5 15:29:28 EST 2018 ma-start: MA started with Process ID 15700
      Mon Feb 5 15:42:57 EST 2018 ma-start: running restart extentions
      Mon Feb 5 15:42:57 EST 2018 ma-start: upgrading core...
      Mon Feb 5 15:43:02 EST 2018 ma-start: running init extensions...
      Mon Feb 5 15:43:02 EST 2018 ma-start: running start extensions...
      Mon Feb 5 15:43:02 EST 2018 ma-start: starting MA
      Mon Feb 5 15:43:02 EST 2018 ma-start: MA started with Process ID 16454
      Tue Feb 6 08:49:06 EST 2018 ma-start: running restart extentions
      Tue Feb 6 08:49:06 EST 2018 ma-start: running start extensions...
      Tue Feb 6 08:49:06 EST 2018 ma-start: starting MA
      Tue Feb 6 08:49:06 EST 2018 ma-start: MA started with Process ID 2782
      Tue Feb 6 09:53:58 EST 2018 ma-start: running stop extensions...
      Tue Feb 6 09:53:58 EST 2018 ma-stop: stop initiated...
      Tue Feb 6 09:54:00 EST 2018 ma-start: MA explicitly stopped. Exiting restart loop
      Tue Feb 6 09:54:00 EST 2018 ma-start: MA done
      Tue Feb 6 09:54:05 EST 2018 ma-start: running init extensions...
      Tue Feb 6 09:54:05 EST 2018 ma-start: running start extensions...
      Tue Feb 6 09:54:05 EST 2018 ma-start: starting MA
      Tue Feb 6 09:54:05 EST 2018 ma-start: MA started with Process ID 6094
      Tue Feb 6 09:54:44 EST 2018 ma-start: no restart flag found, not restarting MA
      Tue Feb 6 09:54:44 EST 2018 ma-start: MA done
      Tue Feb 6 10:02:04 EST 2018 ma-start: running stop extensions...
      Tue Feb 6 10:02:04 EST 2018 ma.stop: No PID file found. Java process not stopped...
      Tue Feb 6 10:02:12 EST 2018 ma-start: running init extensions...
      Tue Feb 6 10:02:12 EST 2018 ma-start: running start extensions...
      Tue Feb 6 10:02:12 EST 2018 ma-start: starting MA
      Tue Feb 6 10:02:12 EST 2018 ma-start: MA started with Process ID 6315
      Tue Feb 6 10:02:51 EST 2018 ma-start: no restart flag found, not restarting MA
      Tue Feb 6 10:02:51 EST 2018 ma-start: MA done
      Tue Feb 6 10:05:22 EST 2018 ma-start: running stop extensions...
      Tue Feb 6 10:05:22 EST 2018 ma.stop: No PID file found. Java process not stopped...
      Tue Feb 6 10:05:28 EST 2018 ma-start: running init extensions...
      Tue Feb 6 10:05:28 EST 2018 ma-start: running start extensions...
      Tue Feb 6 10:05:28 EST 2018 ma-start: starting MA
      Tue Feb 6 10:05:28 EST 2018 ma-start: MA started with Process ID 6522
      Tue Feb 6 10:09:07 EST 2018 ma-start: running stop extensions...
      Tue Feb 6 10:09:07 EST 2018 ma-stop: stop initiated...
      Tue Feb 6 10:09:08 EST 2018 ma-start: MA explicitly stopped. Exiting restart loop
      Tue Feb 6 10:09:08 EST 2018 ma-start: MA done
      Tue Feb 6 10:09:40 EST 2018 ma-start: running init extensions...
      Tue Feb 6 10:09:40 EST 2018 ma-start: running start extensions...
      Tue Feb 6 10:09:40 EST 2018 ma-start: starting MA
      Tue Feb 6 10:09:40 EST 2018 ma-start: MA started with Process ID 6868
      Tue Feb 6 10:17:53 EST 2018 ma-start: running restart extentions
      Tue Feb 6 10:17:53 EST 2018 ma-start: running start extensions...
      Tue Feb 6 10:17:53 EST 2018 ma-start: starting MA
      Tue Feb 6 10:17:53 EST 2018 ma-start: MA started with Process ID 7372
      Tue Feb 6 14:25:18 EST 2018 ma-start: running restart extentions
      Tue Feb 6 14:25:18 EST 2018 ma-start: running start extensions...
      Tue Feb 6 14:25:18 EST 2018 ma-start: starting MA
      Tue Feb 6 14:25:18 EST 2018 ma-start: MA started with Process ID 20038
      Tue Feb 6 14:28:21 EST 2018 ma-start: running restart extentions
      Tue Feb 6 14:28:21 EST 2018 ma-start: running start extensions...
      Tue Feb 6 14:28:21 EST 2018 ma-start: starting MA
      Tue Feb 6 14:28:21 EST 2018 ma-start: MA started with Process ID 20257
      Mon Feb 12 11:38:55 EST 2018 ma-start: running restart extentions
      Mon Feb 12 11:38:55 EST 2018 ma-start: running start extensions...
      Mon Feb 12 11:38:55 EST 2018 ma-start: starting MA
      Mon Feb 12 11:38:55 EST 2018 ma-start: MA started with Process ID 19811
      Tue Feb 20 21:15:54 EST 2018 ma-start: running stop extensions...
      Tue Feb 20 21:15:54 EST 2018 ma-stop: stop initiated...
      Tue Feb 20 21:16:37 EST 2018 ma-start: MA explicitly stopped. Exiting restart loop
      Tue Feb 20 21:16:37 EST 2018 ma-start: MA done
      Tue Feb 20 21:22:31 EST 2018 ma-start: running init extensions...
      Tue Feb 20 21:22:31 EST 2018 ma-start: running start extensions...
      Tue Feb 20 21:22:31 EST 2018 ma-start: starting MA
      Tue Feb 20 21:22:31 EST 2018 ma-start: MA started with Process ID 26488
      Wed Feb 21 10:10:32 EST 2018 ma-start: running stop extensions...
      Wed Feb 21 10:10:32 EST 2018 ma-stop: stop initiated...
      Wed Feb 21 10:10:39 EST 2018 ma-start: MA explicitly stopped. Exiting restart loop
      Wed Feb 21 10:10:39 EST 2018 ma-start: MA done
      Wed Feb 21 10:11:06 EST 2018 ma-start: running init extensions...
      Wed Feb 21 10:11:06 EST 2018 ma-start: running start extensions...
      Wed Feb 21 10:11:06 EST 2018 ma-start: starting MA
      Wed Feb 21 10:11:06 EST 2018 ma-start: MA started with Process ID 27590
      Tue Feb 27 15:23:55 EST 2018 ma-start: running restart extentions
      Tue Feb 27 15:23:55 EST 2018 ma-start: running start extensions...
      Tue Feb 27 15:23:55 EST 2018 ma-start: starting MA
      Tue Feb 27 15:23:55 EST 2018 ma-start: MA started with Process ID 29655
      Mon Apr 9 12:20:27 EDT 2018 ma-start: running restart extentions
      Mon Apr 9 12:20:27 EDT 2018 ma-start: upgrading core...
      Mon Apr 9 12:20:30 EDT 2018 ma-start: running init extensions...
      Mon Apr 9 12:20:30 EDT 2018 ma-start: running start extensions...
      Mon Apr 9 12:20:30 EDT 2018 ma-start: starting MA
      Mon Apr 9 12:20:30 EDT 2018 ma-start: MA started with Process ID 26103
      Mon Jun 11 16:26:20 EDT 2018 ma-start: running restart extentions
      Mon Jun 11 16:26:20 EDT 2018 ma-start: upgrading core...
      Mon Jun 11 16:26:23 EDT 2018 ma-start: running init extensions...
      Mon Jun 11 16:26:23 EDT 2018 ma-start: running start extensions...
      Mon Jun 11 16:26:23 EDT 2018 ma-start: starting MA
      Mon Jun 11 16:26:23 EDT 2018 ma-start: MA started with Process ID 8810
      Tue Jun 26 09:16:51 EDT 2018 ma-start: running restart extentions
      Tue Jun 26 09:16:51 EDT 2018 ma-start: running start extensions...
      Tue Jun 26 09:16:51 EDT 2018 ma-start: starting MA
      Tue Jun 26 09:16:51 EDT 2018 ma-start: MA started with Process ID 13108
      Wed Jun 27 14:22:41 EDT 2018 ma-start: running stop extensions...
      Wed Jun 27 14:22:41 EDT 2018 ma-stop: stop initiated...
      Wed Jun 27 14:22:41 EDT 2018 ma-start: running init extensions...
      Wed Jun 27 14:22:41 EDT 2018 ma-start: running start extensions...
      Wed Jun 27 14:22:41 EDT 2018 ma-start: MA already running with Process ID: 13108
      Wed Jun 27 14:22:41 EDT 2018 ma-start: MA done
      Wed Jun 27 14:22:49 EDT 2018 ma-start: no restart flag found, not restarting MA
      Wed Jun 27 14:22:49 EDT 2018 ma-start: MA done
      Wed Jun 27 14:47:28 EDT 2018 ma-start: running stop extensions...
      Wed Jun 27 14:47:28 EDT 2018 ma.stop: No PID file found. Java process not stopped...
      Wed Jun 27 14:47:31 EDT 2018 ma-start: running init extensions...
      Wed Jun 27 14:47:31 EDT 2018 ma-start: running start extensions...
      Wed Jun 27 14:47:31 EDT 2018 ma-start: starting MA
      Wed Jun 27 14:47:31 EDT 2018 ma-start: MA started with Process ID 25173
      Mon Aug 27 15:01:50 EDT 2018 ma-start: running restart extentions
      Mon Aug 27 15:01:50 EDT 2018 ma-start: upgrading core...
      Mon Aug 27 15:01:54 EDT 2018 ma-start: running init extensions...
      Mon Aug 27 15:01:54 EDT 2018 ma-start: running start extensions...
      Mon Aug 27 15:01:54 EDT 2018 ma-start: starting MA
      Mon Aug 27 15:01:54 EDT 2018 ma-start: MA started with Process ID 28516
      Mon Oct 15 11:08:09 EDT 2018 ma-start: running restart extentions
      Mon Oct 15 11:08:09 EDT 2018 ma-start: upgrading core...
      Mon Oct 15 11:08:12 EDT 2018 ma-start: running init extensions...
      Mon Oct 15 11:08:12 EDT 2018 ma-start: running start extensions...
      Mon Oct 15 11:08:12 EDT 2018 ma-start: starting MA
      Mon Oct 15 11:08:12 EDT 2018 ma-start: MA started with Process ID 13251
      Mon Oct 15 11:15:49 EDT 2018 ma-start: running restart extentions
      Mon Oct 15 11:15:49 EDT 2018 ma-start: running start extensions...
      Mon Oct 15 11:15:49 EDT 2018 ma-start: starting MA
      Mon Oct 15 11:15:49 EDT 2018 ma-start: MA started with Process ID 13792
      Mon Oct 15 11:31:00 EDT 2018 ma-start: running restart extentions
      Mon Oct 15 11:31:00 EDT 2018 ma-start: running start extensions...
      Mon Oct 15 11:31:00 EDT 2018 ma-start: starting MA
      Mon Oct 15 11:31:00 EDT 2018 ma-start: MA started with Process ID 14702
      Thu Dec 6 09:49:09 EST 2018 ma-start: running restart extentions
      Thu Dec 6 09:49:09 EST 2018 ma-start: upgrading core...
      Thu Dec 6 09:49:14 EST 2018 ma-start: running init extensions...
      Thu Dec 6 09:49:14 EST 2018 ma-start: running start extensions...
      Thu Dec 6 09:49:14 EST 2018 ma-start: starting MA
      Thu Dec 6 09:49:14 EST 2018 ma-start: MA started with Process ID 18535
      Wed Jan 9 17:49:33 EST 2019 ma-start: running restart extentions
      Wed Jan 9 17:49:33 EST 2019 ma-start: running start extensions...
      Wed Jan 9 17:49:33 EST 2019 ma-start: starting MA
      Wed Jan 9 17:49:33 EST 2019 ma-start: MA started with Process ID 27130
      Thu Jan 17 17:20:53 EST 2019 ma-start: running restart extentions
      Thu Jan 17 17:20:53 EST 2019 ma-start: running start extensions...
      Thu Jan 17 17:20:53 EST 2019 ma-start: starting MA
      Thu Jan 17 17:20:53 EST 2019 ma-start: MA started with Process ID 9711
      Wed Jan 23 12:08:03 EST 2019 ma-start: running restart extentions
      Wed Jan 23 12:08:03 EST 2019 ma-start: running start extensions...
      Wed Jan 23 12:08:03 EST 2019 ma-start: starting MA
      Wed Jan 23 12:08:03 EST 2019 ma-start: MA started with Process ID 11469
      Wed Jan 23 17:42:38 EST 2019 ma-start: running restart extentions
      Wed Jan 23 17:42:38 EST 2019 ma-start: running start extensions...
      Wed Jan 23 17:42:38 EST 2019 ma-start: starting MA
      Wed Jan 23 17:42:38 EST 2019 ma-start: MA started with Process ID 28564
      Wed Jan 23 18:18:10 EST 2019 ma-start: running restart extentions
      Wed Jan 23 18:18:10 EST 2019 ma-start: running start extensions...
      Wed Jan 23 18:18:10 EST 2019 ma-start: starting MA
      Wed Jan 23 18:18:10 EST 2019 ma-start: MA started with Process ID 30620
      Wed Jan 23 18:21:53 EST 2019 ma-start: running restart extentions
      Wed Jan 23 18:21:53 EST 2019 ma-start: running start extensions...
      Wed Jan 23 18:21:53 EST 2019 ma-start: starting MA
      Wed Jan 23 18:21:53 EST 2019 ma-start: MA started with Process ID 30896
      Wed Jan 23 18:24:50 EST 2019 ma-start: running restart extentions
      Wed Jan 23 18:24:50 EST 2019 ma-start: running start extensions...
      Wed Jan 23 18:24:50 EST 2019 ma-start: starting MA
      Wed Jan 23 18:24:50 EST 2019 ma-start: MA started with Process ID 31138
      Mon Feb 11 15:14:45 EST 2019 ma-start: running restart extentions
      Mon Feb 11 15:14:45 EST 2019 ma-start: running start extensions...
      Mon Feb 11 15:14:45 EST 2019 ma-start: starting MA
      Mon Feb 11 15:14:45 EST 2019 ma-start: MA started with Process ID 20258
      Wed Feb 20 13:23:44 EST 2019 ma-restart: restart initiated...
      Wed Feb 20 13:23:47 EST 2019 ma-restart: restart initiated...
      Wed Feb 20 13:24:28 EST 2019 ma-start: running restart extentions
      Wed Feb 20 13:24:28 EST 2019 ma-start: running start extensions...
      Wed Feb 20 13:24:28 EST 2019 ma-start: starting MA
      Wed Feb 20 13:24:28 EST 2019 ma-start: MA started with Process ID 15204
      Tue Mar 5 11:37:01 EST 2019 ma-start: running restart extentions
      Tue Mar 5 11:37:01 EST 2019 ma-start: running start extensions...
      Tue Mar 5 11:37:01 EST 2019 ma-start: starting MA
      Tue Mar 5 11:37:01 EST 2019 ma-start: MA started with Process ID 18000
      Fri Mar 8 09:39:00 EST 2019 ma-start: running restart extentions
      Fri Mar 8 09:39:00 EST 2019 ma-start: running start extensions...
      Fri Mar 8 09:39:00 EST 2019 ma-start: starting MA
      Fri Mar 8 09:39:00 EST 2019 ma-start: MA started with Process ID 17263
      Fri Mar 15 12:58:12 EDT 2019 ma-start: running restart extentions
      Fri Mar 15 12:58:12 EDT 2019 ma-start: running start extensions...
      Fri Mar 15 12:58:12 EDT 2019 ma-start: starting MA
      Fri Mar 15 12:58:12 EDT 2019 ma-start: MA started with Process ID 1075
      Sun Mar 17 18:56:34 EDT 2019 ma-start: running restart extentions
      Sun Mar 17 18:56:34 EDT 2019 ma-start: running start extensions...
      Sun Mar 17 18:56:34 EDT 2019 ma-start: starting MA
      Sun Mar 17 18:56:34 EDT 2019 ma-start: MA started with Process ID 17809
      Sun Mar 17 18:59:50 EDT 2019 ma-start: running restart extentions
      Sun Mar 17 18:59:50 EDT 2019 ma-start: running start extensions...
      Sun Mar 17 18:59:50 EDT 2019 ma-start: starting MA
      Sun Mar 17 18:59:50 EDT 2019 ma-start: MA started with Process ID 18066
      Tue Apr 30 11:43:24 EDT 2019 ma-start: running restart extentions
      Tue Apr 30 11:43:24 EDT 2019 ma-start: running start extensions...
      Tue Apr 30 11:43:24 EDT 2019 ma-start: starting MA
      Tue Apr 30 11:43:24 EDT 2019 ma-start: MA started with Process ID 9427
      Tue Apr 30 12:30:27 EDT 2019 ma-start: running restart extentions
      Tue Apr 30 12:30:27 EDT 2019 ma-start: running start extensions...
      Tue Apr 30 12:30:27 EDT 2019 ma-start: starting MA
      Tue Apr 30 12:30:27 EDT 2019 ma-start: MA started with Process ID 12151
      Sun Jun 9 09:02:57 EDT 2019 ma-start: no restart flag found, not restarting MA
      Sun Jun 9 09:02:58 EDT 2019 ma-start: MA done
      Sun Jun 9 17:47:00 EDT 2019 ma-start: running stop extensions...
      Sun Jun 9 17:47:00 EDT 2019 ma.stop: No PID file found. Java process not stopped...
      Sun Jun 9 17:47:22 EDT 2019 ma-start: running init extensions...
      Sun Jun 9 17:47:22 EDT 2019 ma-start: running start extensions...
      Sun Jun 9 17:47:22 EDT 2019 ma-start: starting MA
      Sun Jun 9 17:47:22 EDT 2019 ma-start: MA started with Process ID 8262
      Tue Jun 11 15:37:59 EDT 2019 ma-start: running stop extensions...
      Tue Jun 11 15:37:59 EDT 2019 ma-stop: stop initiated...
      Tue Jun 11 15:38:06 EDT 2019 ma-start: MA explicitly stopped. Exiting restart loop
      Tue Jun 11 15:38:06 EDT 2019 ma-start: MA done
      Tue Jun 11 15:40:48 EDT 2019 ma-start: running init extensions...
      Tue Jun 11 15:40:48 EDT 2019 ma-start: running start extensions...
      Tue Jun 11 15:40:48 EDT 2019 ma-start: starting MA
      Tue Jun 11 15:40:48 EDT 2019 ma-start: MA started with Process ID 1152
      Mon Aug 19 10:25:36 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 10:25:36 EDT 2019 ma-stop: stop initiated...
      Mon Aug 19 10:33:00 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 10:33:00 EDT 2019 ma-start: upgrading core...
      Mon Aug 19 10:33:21 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 10:33:21 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 10:33:21 EDT 2019 ma-start: MA removing pid file for dead pid: 1152
      Mon Aug 19 10:33:21 EDT 2019 ma-start: starting MA
      Mon Aug 19 10:33:21 EDT 2019 ma-start: MA started with Process ID 1334
      Mon Aug 19 10:40:16 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 10:40:16 EDT 2019 ma-stop: stop initiated...
      Mon Aug 19 10:40:20 EDT 2019 ma-start: MA explicitly stopped. Exiting restart loop
      Mon Aug 19 10:40:20 EDT 2019 ma-start: MA done
      Mon Aug 19 10:40:26 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 10:40:26 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 10:40:26 EDT 2019 ma-start: starting MA
      Mon Aug 19 10:40:26 EDT 2019 ma-start: MA started with Process ID 2085
      Mon Aug 19 10:51:15 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 10:51:15 EDT 2019 ma-stop: stop initiated...
      Mon Aug 19 10:51:20 EDT 2019 ma-start: MA explicitly stopped. Exiting restart loop
      Mon Aug 19 10:51:20 EDT 2019 ma-start: MA done
      Mon Aug 19 10:51:48 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 10:51:48 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 10:51:48 EDT 2019 ma-start: starting MA
      Mon Aug 19 10:51:48 EDT 2019 ma-start: MA started with Process ID 2720
      Mon Aug 19 10:59:30 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 10:59:30 EDT 2019 ma-stop: stop initiated...
      Mon Aug 19 10:59:31 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 10:59:31 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 10:59:32 EDT 2019 ma-start: MA removing pid file for dead pid: 2720
      Mon Aug 19 10:59:32 EDT 2019 ma-start: starting MA
      Mon Aug 19 10:59:32 EDT 2019 ma-start: MA started with Process ID 3252
      Mon Aug 19 10:59:32 EDT 2019 ma-start: no restart flag found, not restarting MA
      Mon Aug 19 10:59:32 EDT 2019 ma-start: MA done
      Mon Aug 19 11:05:55 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 11:05:55 EDT 2019 ma.stop: No PID file found. Java process not stopped...
      Mon Aug 19 11:05:55 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 11:05:55 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 11:05:55 EDT 2019 ma-start: starting MA
      Mon Aug 19 11:05:55 EDT 2019 ma-start: MA started with Process ID 3618
      Mon Aug 19 11:06:23 EDT 2019 ma-start: no restart flag found, not restarting MA
      Mon Aug 19 11:06:23 EDT 2019 ma-start: MA done
      Mon Aug 19 11:06:57 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 11:06:57 EDT 2019 ma.stop: No PID file found. Java process not stopped...
      Mon Aug 19 11:06:57 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 11:06:57 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 11:06:57 EDT 2019 ma-start: starting MA
      Mon Aug 19 11:06:57 EDT 2019 ma-start: MA started with Process ID 3747
      Mon Aug 19 11:07:35 EDT 2019 ma-start: no restart flag found, not restarting MA
      Mon Aug 19 11:07:35 EDT 2019 ma-start: MA done
      Mon Aug 19 11:49:11 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 11:49:11 EDT 2019 ma.stop: No PID file found. Java process not stopped...
      Mon Aug 19 11:57:43 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 11:57:43 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 11:57:43 EDT 2019 ma-start: starting MA
      Mon Aug 19 11:57:43 EDT 2019 ma-start: MA started with Process ID 6092
      Mon Aug 19 11:57:46 EDT 2019 ma-start: no restart flag found, not restarting MA
      Mon Aug 19 11:57:47 EDT 2019 ma-start: MA done
      Mon Aug 19 11:58:10 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 11:58:10 EDT 2019 ma.stop: No PID file found. Java process not stopped...
      Mon Aug 19 12:00:03 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 12:00:03 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 12:00:03 EDT 2019 ma-start: starting MA
      Mon Aug 19 12:00:03 EDT 2019 ma-start: MA started with Process ID 6392
      Mon Aug 19 12:00:06 EDT 2019 ma-start: no restart flag found, not restarting MA
      Mon Aug 19 12:00:06 EDT 2019 ma-start: MA done
      Mon Aug 19 12:02:03 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 12:02:03 EDT 2019 ma.stop: No PID file found. Java process not stopped...
      Mon Aug 19 12:02:03 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 12:02:03 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 12:02:03 EDT 2019 ma-start: starting MA
      Mon Aug 19 12:02:03 EDT 2019 ma-start: MA started with Process ID 6528
      Mon Aug 19 12:02:06 EDT 2019 ma-start: no restart flag found, not restarting MA
      Mon Aug 19 12:02:06 EDT 2019 ma-start: MA done
      Mon Aug 19 12:04:38 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 12:04:38 EDT 2019 ma.stop: No PID file found. Java process not stopped...
      Mon Aug 19 12:04:38 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 12:04:38 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 12:04:38 EDT 2019 ma-start: starting MA
      Mon Aug 19 12:04:38 EDT 2019 ma-start: MA started with Process ID 6684
      Mon Aug 19 12:04:41 EDT 2019 ma-start: no restart flag found, not restarting MA
      Mon Aug 19 12:04:41 EDT 2019 ma-start: MA done
      Mon Aug 19 12:04:41 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 12:04:41 EDT 2019 ma.stop: No PID file found. Java process not stopped...
      Mon Aug 19 17:22:38 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 17:22:38 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 17:22:38 EDT 2019 ma-start: starting MA
      Mon Aug 19 17:22:38 EDT 2019 ma-start: MA started with Process ID 20681
      Mon Aug 19 17:22:41 EDT 2019 ma-start: no restart flag found, not restarting MA
      Mon Aug 19 17:22:41 EDT 2019 ma-start: MA done
      Mon Aug 19 17:23:55 EDT 2019 ma-start: running stop extensions...
      Mon Aug 19 17:23:55 EDT 2019 ma.stop: No PID file found. Java process not stopped...
      Mon Aug 19 17:23:55 EDT 2019 ma-start: running init extensions...
      Mon Aug 19 17:23:55 EDT 2019 ma-start: running start extensions...
      Mon Aug 19 17:23:55 EDT 2019 ma-start: starting MA
      Mon Aug 19 17:23:55 EDT 2019 ma-start: MA started with Process ID 20814
      Mon Aug 19 17:23:58 EDT 2019 ma-start: no restart flag found, not restarting MA
      Mon Aug 19 17:23:58 EDT 2019 ma-start: MA done
      

      The ma.log file is too large but I have emailed it to support@infiniteautomation.com

      Please advise. Looks like something may have been deleted?

      posted in User help
      O
      ottawa_admin
    • Unable to restart Cloud Mango

      Hi there,

      I recently inherited a Cloud Mango instance and caused a bit of an issue when installing some new updates (evening of August 17th). Long story short, I was able to restart the Mango but all of the previous data points and scripts were lost.

      I attempted restoring the most recent H2 backup as described in https://forum.infiniteautomation.com/topic/2748/how-to-restore-a-database-backup/2
      This only partially worked. Only the core module remained and none of the previous data points or sources could be seen. I may have been doing something wrong.

      I am now at a point where the Mango cannot restart through command line or the web interface. When restarting through the interface the following error pops up:
      Server error: PreparedStatementCallback; bad SQL grammar [SELECT dp.id,dp.data,dp.xid,dp.dataSourceId,dp.name,dp.deviceName,dp.enabled,dp.pointFolderId,dp.loggingType,dp.intervalLoggingPeriodType,dp.intervalLoggingPeriod,dp.intervalLoggingType,dp.tolerance,dp.purgeOverride,dp.purgeType,dp.purgePeriod,dp.defaultCacheSize,dp.discardExtremeValues,dp.engineeringUnits,dp.readPermission,dp.setPermission,dp.templateId,dp.rollup,dp.dataTypeId,dp.settable,ds.name,ds.xid,ds.dataSourceType,ds.editPermission,template.name,template.xid FROM dataPoints AS dp JOIN dataSources ds ON ds.id = dp.dataSourceId LEFT JOIN templates template ON template.id = dp.templateId ORDER BY dp.deviceName, dp.name OFFSET ? ROWS FETCH NEXT ? ROWS ONLY]; nested exception is org.h2.jdbc.JdbcSQLSyntaxErrorException: Column "DP.SETTABLE" not found; SQL statement: SELECT dp.id,dp.data,dp.xid,dp.dataSourceId,dp.name,dp.deviceName,dp.enabled,dp.pointFolderId,dp.loggingType,dp.intervalLoggingPeriodType,dp.intervalLoggingPeriod,dp.intervalLoggingType,dp.tolerance,dp.purgeOverride,dp.purgeType,dp.purgePeriod,dp.defaultCacheSize,dp.discardExtremeValues,dp.engineeringUnits,dp.readPermission,dp.setPermission,dp.templateId,dp.rollup,dp.dataTypeId,dp.settable,ds.name,ds.xid,ds.dataSourceType,ds.editPermission,template.name,template.xid FROM dataPoints AS dp JOIN dataSources ds ON ds.id = dp.dataSourceId LEFT JOIN templates template ON template.id = dp.templateId ORDER BY dp.deviceName, dp.name OFFSET ? ROWS FETCH NEXT ? ROWS ONLY [42122-199]

      I guess my first question is the following:
      How can I regain the ability to restart, stop and start the Cloud Mango? This way I can start from a blank database and login with admin/admin.

      Once I've got that resolved I'll want to get my backup restored :) One step at a time though.

      Logs can be found here:
      https://drive.google.com/open?id=1Y9h_iw6rC3LiG0nvCL8iWvDBXn049be5

      Thank you so much in advance!

      posted in User help
      O
      ottawa_admin