Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.
Unable to get response IAM from a tridium device
-
Unable to get response IAM from a tridium device.
Attached wirshark file.
Device 2Thanks.[0_1518168687165_jasonscan.pcap](Uploading 100%)
-
@gadi-alaloof said:
Unable to get response IAM from a tridium device.
Attached wirshark file.
Device 2Thanks.[0_1518168687165_jasonscan.pcap](Uploading 100%)
0000 ff ff ff ff ff ff a8 1b 6a 0e 48 7d 08 00 45 00
0010 00 34 45 ee 00 00 40 11 bd 85 ac 18 0f 16 ac 18
0020 0f ff ba c0 ba c0 00 20 05 7b 81 0b 00 18 01 20
0030 ff ff 00 ff 10 00 c4 02 00 00 02 22 01 e0 91 00
0040 21 24 -
Hi gadi.alaloof,
I think this thread might be similar: https://forum.infiniteautomation.com/topic/3121/unable-to-discover-a-bacnet-device-on-my-network/18
The resolution there was found in using a local bind address of
0.0.0.0
and a broadcast address particular to the network, like192.168.1.255
for the192.168.1.0/24
network. BACnet local device settings are on the /system_settings.shtm page