    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    Handling modbus registers in a script

    Scripting general Discussion
    2
    2
    1.0k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • P
      przemom
      last edited by

      Hi,
      How to write a numeric value to modbus register in meta data source script? Thanks for help.

      1 Reply Last reply Reply Quote 0
      • phildunlapP
        phildunlap
        last edited by

        Hi przemom,

        Meta point scripts don't have the .set() function like a scripting data source does. So, your options are either to use a point link from your meta point to your modbus point, or to configure a scripting data source to set the value using varName.set( 12.34 );

        1 Reply Last reply Reply Quote 0