      I am very new to BACnet.
      I need to pass a string through BACnet to NAE ( Johnson Controls) which detects the BACnet objects available in the network.
      I am using the ‘Loop Device’ for the same, running on the default port. Also encoding type in NAE is set to ANSI.
      But ‘Loop device’ is not being detected.
      Please help.
        A few things:
        1. What "string" do you need to pass? Normally to discover other devices on the network you would use a WhoIs request.
        2. You are using a Loop device (it's actually an object called Loop, not a device; a device is another type of object) to detect objects? That doesn't sound right.
        3. Is the encoding type ASCII, rather than ANSI?
        Let me paraphrase to see if i understand what you are trying to do: you have a Loop object on your NAE device that you are trying to detect automatically, and the NAE is on the network using the default port (0xBAC0). If this is the case, you should use BACnet4J to create a LocalDevice on the default port, send a WhoIs, and then upon receipt of an IAm reply introspect the device that sent it to find your Loop object.
        • V Offline
          Vinay
          Sorry may be I didn’t make it clear.
          1. Please check the below details.
          2. No. I am using NAE to detect objects. So I want NAE to detect ‘Loop device’. This is the right approach?
          3. Encoding type as from NAE is ANSI X3.4(US-ASCII)
          No, what I am trying to do is opposite of what you have stated. NAE device is trying to detect the BACnet objects on the network.
          Before BACnet4J I tried the ‘BACnet Server Simulator’ from SCADA Engine (http://www.scadaengine.com/software6.html) and NAE detects that.
          Now I am trying to replace it with ‘Loop Device’ but NAE is not detecting it.
          Please help.
            Can you post the code you are using with BACnet4J?
            • V Offline
              Vinay
              • GNU Lesser General Public License
              • Copyright (C) 2006-2009 Serotonin Software Technologies Inc. http://serotoninsoftware.com
              • @author Matthew Lohbihler
              • This library is free software; you can redistribute it and/or
              • modify it under the terms of the GNU Lesser General Public
              • License as published by the Free Software Foundation; either
              • version 2.1 of the License, or (at your option) any later version.
              • This library is distributed in the hope that it will be useful,
              • but WITHOUT ANY WARRANTY; without even the implied warranty of
              • MERCHANTABILITY or FITNESS FOR A PARTICULAR PURPOSE. See the GNU
              • Lesser General Public License for more details.
              • You should have received a copy of the GNU Lesser General Public
              • License along with this library; if not, write to the Free Software
              • Foundation, Inc., 59 Temple Place, Suite 330, Boston, MA 02111-1307, USA.
                package com.serotonin.bacnet4j.test;
              import com.serotonin.bacnet4j.LocalDevice;
              import com.serotonin.bacnet4j.RemoteDevice;
              import com.serotonin.bacnet4j.RemoteObject;
              import com.serotonin.bacnet4j.event.DeviceEventListener;
              import com.serotonin.bacnet4j.exception.BACnetServiceException;
              import com.serotonin.bacnet4j.obj.BACnetObject;
              import com.serotonin.bacnet4j.type.Encodable;
              import com.serotonin.bacnet4j.type.constructed.Choice;
              import com.serotonin.bacnet4j.type.constructed.PropertyValue;
              import com.serotonin.bacnet4j.type.constructed.SequenceOf;
              import com.serotonin.bacnet4j.type.constructed.TimeStamp;
              import com.serotonin.bacnet4j.type.enumerated.BinaryPV;
              import com.serotonin.bacnet4j.type.enumerated.EngineeringUnits;
              import com.serotonin.bacnet4j.type.enumerated.EventState;
              import com.serotonin.bacnet4j.type.enumerated.EventType;
              import com.serotonin.bacnet4j.type.enumerated.MessagePriority;
              import com.serotonin.bacnet4j.type.enumerated.NotifyType;
              import com.serotonin.bacnet4j.type.enumerated.ObjectType;
              import com.serotonin.bacnet4j.type.enumerated.PropertyIdentifier;
              import com.serotonin.bacnet4j.type.notificationParameters.NotificationParameters;
              import com.serotonin.bacnet4j.type.primitive.Boolean;
              import com.serotonin.bacnet4j.type.primitive.CharacterString;
              import com.serotonin.bacnet4j.type.primitive.ObjectIdentifier;
              import com.serotonin.bacnet4j.type.primitive.Real;
              import com.serotonin.bacnet4j.type.primitive.UnsignedInteger;
              import java.io.IOException;
              • software only device default local loop ;-)
              • @author mlohbihler
              • @author aploese
                public class LoopDevice implements Runnable {
                LoopDevice ld = new LoopDevice("127.0.0.255", LocalDevice.DEFAULT_PORT + 1);
                //LoopDevice ld = new LoopDevice("127.0.0.255", LocalDevice.DEFAULT_PORT );
                Thread.sleep(12000000); // wait 2 min
                ld.doTerminate();
                private boolean terminate;
                private LocalDevice localDevice;
                private BACnetObject ai0;
                private BACnetObject ai1;
                private BACnetObject bi0;
                private BACnetObject bi1;
                private BACnetObject mso0;
                private BACnetObject ao0;
                public LoopDevice(String broadcastAddress, int port) throws BACnetServiceException, IOException {
                localDevice = new LocalDevice(1968, broadcastAddress);
                localDevice.setPort(port);
                localDevice.getEventHandler().addListener(new DeviceEventListener() {
                     public void listenerException(Throwable e) {
                         System.out.println("loopDevice listenerException");
                     public void iAmReceived(RemoteDevice d) {
                         System.out.println("loopDevice iAmReceived");
                     public boolean allowPropertyWrite(BACnetObject obj, PropertyValue pv) {
                         System.out.println("loopDevice allowPropertyWrite");
                         return true;
                     public void propertyWritten(BACnetObject obj, PropertyValue pv) {
                         System.out.println("loopDevice propertyWritten");
                     public void iHaveReceived(RemoteDevice d, RemoteObject o) {
                         System.out.println("loopDevice iHaveReceived");
                     public void covNotificationReceived(UnsignedInteger subscriberProcessIdentifier, RemoteDevice initiatingDevice, ObjectIdentifier monitoredObjectIdentifier, UnsignedInteger timeRemaining, SequenceOf<PropertyValue> listOfValues) {
                         System.out.println("loopDevice covNotificationReceived");
                     public void eventNotificationReceived(UnsignedInteger processIdentifier, RemoteDevice initiatingDevice, ObjectIdentifier eventObjectIdentifier, TimeStamp timeStamp, UnsignedInteger notificationClass, UnsignedInteger priority, EventType eventType, CharacterString messageText, NotifyType notifyType, Boolean ackRequired, EventState fromState, EventState toState, NotificationParameters eventValues) {
                         System.out.println("loopDevice eventNotificationReceived");
                     public void textMessageReceived(RemoteDevice textMessageSourceDevice, Choice messageClass, MessagePriority messagePriority, CharacterString message) {
                         System.out.println("loopDevice textMessageReceived");
                     public void privateTransferReceived(UnsignedInteger vendorId, UnsignedInteger serviceNumber, Encodable serviceParameters) {
                         System.out.println("loopDevice privateTransferReceived");
                 // Set up a few objects.
                 ai0 = new BACnetObject(
                         localDevice, localDevice.getNextInstanceObjectIdentifier(ObjectType.analogInput));
                 ai0.setProperty(PropertyIdentifier.units, EngineeringUnits.centimeters);
                 localDevice.addObject(getAi0());
                 ai1 = new BACnetObject(
                 ai0.setProperty(PropertyIdentifier.units, EngineeringUnits.percentObscurationPerFoot);
                 localDevice.addObject(getAi1());
                 bi0 = new BACnetObject(
                         localDevice, localDevice.getNextInstanceObjectIdentifier(ObjectType.binaryInput));
                 localDevice.addObject(getBi0());
                 bi0.setProperty(PropertyIdentifier.objectName, new CharacterString("Off and on"));
                 bi0.setProperty(PropertyIdentifier.inactiveText, new CharacterString("Off"));
                 bi0.setProperty(PropertyIdentifier.activeText, new CharacterString("On"));
                 bi1 = new BACnetObject(
                 localDevice.addObject(getBi1());
                 bi1.setProperty(PropertyIdentifier.objectName, new CharacterString("Good and bad"));
                 bi1.setProperty(PropertyIdentifier.inactiveText, new CharacterString("Bad"));
                 bi1.setProperty(PropertyIdentifier.activeText, new CharacterString("Good"));
                 mso0 = new BACnetObject(
                         localDevice, localDevice.getNextInstanceObjectIdentifier(ObjectType.multiStateOutput));
                 mso0.setProperty(PropertyIdentifier.objectName, new CharacterString("Vegetable"));
                 mso0.setProperty(PropertyIdentifier.numberOfStates, new UnsignedInteger(4));
                 mso0.setProperty(PropertyIdentifier.stateText, 1, new CharacterString("Tomato"));
                 mso0.setProperty(PropertyIdentifier.stateText, 2, new CharacterString("Potato"));
                 mso0.setProperty(PropertyIdentifier.stateText, 3, new CharacterString("Onion"));
                 mso0.setProperty(PropertyIdentifier.stateText, 4, new CharacterString("Broccoli"));
                 mso0.setProperty(PropertyIdentifier.presentValue, new UnsignedInteger(1));
                 localDevice.addObject(getMso0());
                 ao0 = new BACnetObject(
                         localDevice, localDevice.getNextInstanceObjectIdentifier(ObjectType.analogOutput));
                 ao0.setProperty(PropertyIdentifier.objectName, new CharacterString("Settable analog"));
                 localDevice.addObject(getAo0());
                 // Start the local device.
                 localDevice.initialize();
                 new Thread(this).start();
                public void run() {
                try {
                System.out.println("LoopDevice start changing values" + this);
                     // Let it go...
                     float ai0value = 0;
                     float ai1value = 0;
                     boolean bi0value = false;
                     boolean bi1value = false;
                     getMso0().setProperty(PropertyIdentifier.presentValue, new UnsignedInteger(2));
                     while (!isTerminate()) {
                     //while (true) {
                         System.out.println("Change values of LoopDevice " + this);
                         // Change the values.
                         ai0value += 0.1;
                         ai1value += 0.7;
                         bi0value = !bi0value;
                         bi1value = !bi1value;
                         // Update the values in the objects.
                         ai0.setProperty(PropertyIdentifier.presentValue, new Real(ai0value));
                         ai1.setProperty(PropertyIdentifier.presentValue, new Real(ai1value));
                         bi0.setProperty(PropertyIdentifier.presentValue, bi0value ? BinaryPV.active : BinaryPV.inactive);
                         bi1.setProperty(PropertyIdentifier.presentValue, bi1value ? BinaryPV.active : BinaryPV.inactive);
                System.out.println("end of while");
                synchronized (this) {
                System.out.print("start wait");
                wait(1000); // 1 second or notified (faster exit then stupid wait for 1 second)
                System.out.println("end wait");
                System.out.println("out of wait");
                System.out.println("Close LoopDevive " + this);
                } catch (Exception ex) {
                localDevice.terminate();
                localDevice = null;
                @Override
                protected void finalize() throws Throwable {
                if (localDevice != null) {
                localDevice = null;
                • @return the terminate
                  public boolean isTerminate() {
                  return terminate;
                • @param terminate the terminate to set
                  public void doTerminate() {
                  this.terminate = true;
                  this.notifyAll(); // we may wait for this in run() ...
                • @return the broadcastAddress
                  public String getBroadcastAddress() {
                  return localDevice.getBroadcastAddress();
                • @return the port
                  public int getPort() {
                  return localDevice.getPort();
                • @return the localDevice
                  public LocalDevice getLocalDevice() {
                  return localDevice;
                • @return the ai0
                  public BACnetObject getAi0() {
                  return ai0;
                • @return the ai1
                  public BACnetObject getAi1() {
                  return ai1;
                • @return the bi0
                  public BACnetObject getBi0() {
                  return bi0;
                • @return the bi1
                  public BACnetObject getBi1() {
                  return bi1;
                • @return the mso0
                  public BACnetObject getMso0() {
                  return mso0;
                • @return the ao0
                  public BACnetObject getAo0() {
                  return ao0;
                I think your port number is the problem. I haven't tested your code, so there might be other things as well. Try this:
                Change:
                To:
                LoopDevice ld = new LoopDevice("127.0.0.255", LocalDevice.DEFAULT_PORT);
                Your equipment is probably looking for other devices only on the default port (unless you configured it to work on the other port).
                • V Offline
                  Vinay
                  Sorry, I had tried this too.
                  Is there anything else I can try?
                    Try setting up another BACnet4J device to see if it can discover your loop.
                    • V Offline
                      Vinay
                      DiscoveryTest running in another machine detects the LoopDevice