How to use the new Serial Data Source in Mango Automation 2.1
-
So, in theory, if you sent both messages, the protocol is ambiguous as to which response refers to which question?
The only way I can see that working is using two meta points to buffer the commands and responses for sorting by a script to the appropriate endpoints. Then the serial datasource may have very simple points that catch everything, the meta points addend whatever new message is coming or going, and the script processes the message queues into its own points. You could also write a module for this protocol that hides/accelerates the analysis portion.
It may help to know the serial data source is open source: https://github.com/infiniteautomation/ma-modules-public/tree/master/Serial Data Source
-
Managed that using scripting data source and meta data source.
Thanks again for all the help, Phil. -
Glad it worked :D
Thanks for bringing the escape character issue to our attention!
-
Hi, Philips. Didn't expect to come back so soon myself :)
We start working on a new device with mango 2.4, and I have to use \r\r\n as the message terminator.
Turns out serial data source doesn't accept strings more than one character as the input.
I've checked with the source codes from where you gave, and found that message terminator was of a java.lang.String type.
So is there any chance we get serial data source into accepting characters, other than one character, for the message terminator? -
Hi Marc,
It looks like that restriction was improper. I removed it and tried to read around to validate it, but my serial cables have seemingly grown legs and I can't test as thoroughly as I'd like. Let me know!
Attachment: download link
-
Thanks, Philips. I've tested this version.
First of all, I was wrong about the protocol. It's a "20H 20H 0DH" at the end of the message, not a "0DH 0DH 0AH" as I thought before.
So I tried "\s\s\r" at first, and something about escape was wrong. On saving data source properties, this version lost the first two \ charactors and turned "\s\s\r" into "ss\r". You may want to look into that."[space][space]\r" seems not so well-formed to me, yet it got a correct command message to send.
Then again, the protocol, which is definitely not my favourite, has this response like "0DH 41H xxxxxxx 20H 20H 0DH xxxxxxx 20H 20H 0DH xxxxxxx 20H 20H 0DH"."20H 20H 0DH" is the end of response, but it also shows up in the middle, twice. Is it still OK to use it as the message terminator?
@phildunlap said:Hi Marc,
It looks like that restriction was improper. I removed it and tried to read around to validate it, but my serial cables have seemingly grown legs and I can't test as thoroughly as I'd like. Let me know!
-
The difference from what you'd expect in the resulting terminator using the \s is because Java escape characters are different than regular expression escape characters (spaces are okay with Java). This is unclear, I should probably add that to the documentation.
Unfortunately no, the serial data source wasn't written for protocols that are length dependent or have ambiguous terminators. I think the existing solution is to use the same trick and buffer the serial data into a meta point, then shuffle it to the right point from a script.
-
Thanks, Philips.
Learned more about the response. It's like "0DH [X1] [X2] xxxxxxx 20H 20H 0DH 4CH 32H xxxxxxx 20H 20H 0DH 4CH 33H xxxxxxx 20H 20H 0DH", in which [X1] may be letter 'A','B' or 'C', and [X2] is a single digit.Tryed to split it into 3 parts using 3 data points, each of which ended with "20H 20H 0DH". A sample of the first part is in the screenshot attached.
But "patternMismatch" alarms showed up.
Screenshots of Serial Data Source Configuration, alarm, and event in Mango database are attached.As may not be seen directly in the screeshot, there are two spaces in both message terminator and message regex. Whole strings are written below:
Message Terminator: [space][space]\r
Message Regex: (?s)([A-CL][0-9].*)[space][space]\rEmbbeded flag expression (?s) is used because there are several single '0DH' in the "xxxxxxxx" part of the response. So the ".*" can match them.
I took out the piece of "messageMatcher" java code from SerialDataSourceRT.java, and tested it with sample message and regex above. It was a match. And I got to find the problem elsewhere.
Now it seems to me there is only one space left in the message and the regex, seen from the highlighted parts of the screenshots. Not sure that is a display issue or really a clue.
What do you see, Philips?@phildunlap said:
The difference from what you'd expect in the resulting terminator using the \s is because Java escape characters are different than regular expression escape characters (spaces are okay with Java). This is unclear, I should probably add that to the documentation.
Unfortunately no, the serial data source wasn't written for protocols that are length dependent or have ambiguous terminators. I think the existing solution is to use the same trick and buffer the serial data into a meta point, then shuffle it to the right point from a script.
Attachment: download link
-
Hi Marc,
I modified the serial data source to have a second protocol parsing method: zealous regex. I have updated the help documents, but the short of it is that if the datasource is configured not to use the terminator, it will attempt to match every point's regex with the message as received thusfar and give a value to the first match, popping that match from the input.