Modbus and MySQL Management
-
Hi JJoel Haggar
Mango'm testing on different lines and I have some ideas to improve proguntas handle:-
I have a power meter and voltages Shark 100 with Modbus RTU and want to read your data every second, to take actions based on the values read, but I NOT need to record the data in the MySQL database every second. This overload of data tables. Relevant data should I record in the other table or schema every 15 minutes. How do I do?
-
Mango supports arrays of variables or arrays of data points? for example, I want to load an array as Mem [1 .. 16] with correlation data memory map Modbus registers 1000 to 1032, where data point Mem [1] to Mem [16] are loaded in block.
Best regards.
Erwin Flores
Telemetry - Guatemala -
-
-
On the data point edit page under "logging properties", try "interval" logging.
-
No, Mango does not currently support array or object data types.
-