    Please Note This forum exists for community support for the Mango product family and the Radix IoT Platform. Although Radix IoT employees participate in this forum from time to time, there is no guarantee of a response to anything posted here, nor can Radix IoT, LLC guarantee the accuracy of any information expressed or conveyed. Specific project questions from customers with active support contracts are asked to send requests to support@radixiot.com.

    Radix IoT Website Mango 3 Documentation Website Mango 4 Documentation Website Mango 5 Documentation Website

    Error while reading with EM6436 energy meter using modbus4j.jar

    Modbus4J general discussion
    2
    11
    5.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • P
      piyush
      last edited by

      We are using Mango 1.13 version to perform the reading of Modbus RTU energy meter device EM6436 register value and we are able to read the register values of energy meter device.
      We tried the sample code provided by mango community(RTU example),but we are not getting particular method like

      1. master.getValue(7, RegisterRange.HOLDING_REGISTER, 1000, DataType.FOUR_BYTE_FLOAT_SWAPPED)
      2. ModbusLocator loc = new ModbusLocator(1, RegisterRange.HOLDING_REGISTER, 0, DataType.TWO_BYTE_INT_UNSIGNED);

      Can you suggest some solution for reading register value from Modbus RTU device, since we are using modbus4j.jar for the same and is there any latest seroUtil and modbus jar available which support above mentioned function.

      1 Reply Last reply Reply Quote 0
      • M
        mlohbihler
        last edited by

        Note that Modbus4J uses 0-indexing for registers. I don't recall precisely, but perhaps ModScan uses 1-indexing? So, have you tried reading from register 3900 instead?

        Best regards,
        Matthew

        1 Reply Last reply Reply Quote 0
        • M
          mlohbihler
          last edited by

          We tried the sample code provided by mango community(RTU example),but we are not getting particular method like ...

          That code looks old. Changes to Modbus4J have occurred since then. From your other code samples, it looks like you've figured out the new ways doing things, so i'm not sure what your question in.

          Best regards,
          Matthew

          1 Reply Last reply Reply Quote 0
          • P
            piyush
            last edited by

            Hi mlohbihler,

            Thx for the information.

            The code we posted is used by use and we also tried the RTU sample code.
            The sample code given by mango to read RTU device register there they used one line code to read the value on device i.e
            master.getValue(7, RegisterRange.HOLDING_REGISTER, 1000, DataType.FOUR_BYTE_FLOAT_SWAPPED)

            We tried to use this particular line in our code but we are not getting this method in modbus4j.jar

            In your previous post you mentioned about the register indexing i.e 0 used by modbus4j and 1 by ModScan ,we also tried to read register from 3900,1000,2000 etc...but still we are geting error like

            1. Illegal register address (When register address is 3901)
            2. TimeOut exception (When register address is 3900)

            Similarly we tried to read the register value using ModbusLocater ,this method is also not get imported.
            Sample code for ModbusLocater which we tried is like this:

            // Define the point locator.
            ModbusLocator loc = new ModbusLocator(1, RegisterRange.HOLDING_REGISTER, 0, DataType.TWO_BYTE_INT_UNSIGNED);

            // Set the point value
            master.setValue(loc, 1800);

            // Get the point value
            System.out.println(master.getValue(loc));

            Can you suggest anything on it.

            1 Reply Last reply Reply Quote 0
            • M
              mlohbihler
              last edited by

              Do you have Mango? You could try the discovery tools in there to see what's going on in your device.

              Otherwise, it's hard to troubleshoot something that works in some cases but not in others without being able to test it personally. To deal with your issues with code versions, i suggest you download the latest jars (modbus4J and seroUtils) from the SF CVS.

              Best regards,
              Matthew

              1 Reply Last reply Reply Quote 0
              • P
                piyush
                last edited by

                Hi mlohbihler,

                I got the solution for my problem ,i like to ask one more thing is there any way to convert Modbus response into an float or any way to convert response into an float.
                Since our device support floating value ,there is no problem with the integer and real values.

                Thx..

                Solution is like this:

                 ModbusRequest mreq = new ModbusFactory().createReadRequest(2, 3, 3926, 2);
                 ReadResponse mres = (ReadResponse) master.send(mreq);
                 short[] data = mres.getShortData();
                 int length = 65536 - 3926;
                         for (int i = 0; i < length; i++)
                             System.out.println("Result: "+Integer.toHexString(data*)+" === "+Integer.toString(data*)+" === "+data*);         
                
                1 Reply Last reply Reply Quote 0
                • M
                  mlohbihler
                  last edited by

                  Note that you are using a different register address than before. Does this explain why it was previously not working?

                  Conversion from/to float/double is the point behind locators. The following should be equivalent to what you are trying to do:

                          NumericLocator nl = new NumericLocator(2, RegisterRange.HOLDING_REGISTER, 3926, DataType.FOUR_BYTE_FLOAT);
                          float value = master.getValue(nl).floatValue();
                  
                  

                  Your data type could also be FOUR_BYTE_FLOAT_SWAPPED. Also, locators are stateless, and so can be created once and reused as required.

                  Best regards,
                  Matthew

                  1 Reply Last reply Reply Quote 0
                  • P
                    piyush
                    last edited by

                    Previously we are just creating ModbusRequest and getting the ReadHoldingRegistersResponse now instead of that we are creating ModbusRequest and getting ReadResponse .
                    We tried to convert the values into float with the NumericLocater but it giving us the enumerated output like 5.12345E28
                    Instead of it we like to get the floating values like 12.234.

                    1 Reply Last reply Reply Quote 0
                    • M
                      mlohbihler
                      last edited by

                      Not sure what you mean by this:

                      the enumerated output like 5.12345E28

                      How is your data stored? I.e. what does this print out?

                      System.out.println("Result: "+Integer.toHexString(data*)+" === "+Integer.toString(data*)+" === "+data*);
                      

                      If it is not stored as a float, then you need to use another data type.

                      Best regards,
                      Matthew