<?xml version="1.0" encoding="UTF-8"?><rss xmlns:dc="http://purl.org/dc/elements/1.1/" xmlns:content="http://purl.org/rss/1.0/modules/content/" xmlns:atom="http://www.w3.org/2005/Atom" version="2.0"><channel><title><![CDATA[Wago 750-841 Modbus Fieldbus Coupler]]></title><description><![CDATA[<p dir="auto">Hey guys and gals nice to find this program.  I have a question.  I have a Wago 750-841 Modbus TCP Controller which I am able to talk to with a Java program I and a friend wrote using the Jmod library.  I tried your data source setup and when do a node scan I get 1 thru 240 nodes?!  Correct me if I am wrong but if I have one modbus coupler at one ip should there not be only one node?  What do you think?  Also I have a Mitsubishi City Line System up and configured on Mango just fine.  Bacnet seems to be fine.</p>
<p dir="auto">Let me know,</p>
<p dir="auto">dk</p>
]]></description><link>https://forum.mango-os.com/topic/691/wago-750-841-modbus-fieldbus-coupler</link><generator>RSS for Node</generator><lastBuildDate>Sun, 12 Apr 2026 23:38:37 GMT</lastBuildDate><atom:link href="https://forum.mango-os.com/topic/691.rss" rel="self" type="application/rss+xml"/><pubDate>Tue, 21 Dec 2010 19:43:03 GMT</pubDate><ttl>60</ttl><item><title><![CDATA[Reply to Wago 750-841 Modbus Fieldbus Coupler on Thu, 23 Dec 2010 19:38:37 GMT]]></title><description><![CDATA[<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/zumiani" aria-label="Profile: zumiani">@<bdi>zumiani</bdi></a> said:</p>
<blockquote>
<p dir="auto">You should look at the PLC program.<br />
Maybe a task turn it off after a while..<br />
Surely it isn't due to Mango or Modbus!</p>
</blockquote>
<p dir="auto">Ok finally found the issue!  I had created a binary 0 reset on the program I had wrote and was talking to mango at the same time.  So everytime I had set a point in mango my program was reseting that point after 2 seconds.</p>
<p dir="auto">So now that I finally have it all working I am running a BAC-HD150 bacnet controller for the Mitsubishi City Line system with Bacnet IP of course.  And running custom valve and boiler control for large steam system.  I am controlling that with Wago 750-841 Modbus Field Coupler.  I will update you with my setup once all is done.</p>
<p dir="auto">Thanks and hope this helps others.</p>
<p dir="auto">dk</p>
]]></description><link>https://forum.mango-os.com/post/5152</link><guid isPermaLink="true">https://forum.mango-os.com/post/5152</guid><dc:creator><![CDATA[dkudos]]></dc:creator><pubDate>Thu, 23 Dec 2010 19:38:37 GMT</pubDate></item><item><title><![CDATA[Reply to Wago 750-841 Modbus Fieldbus Coupler on Thu, 23 Dec 2010 08:29:14 GMT]]></title><description><![CDATA[<p dir="auto">You should look at the PLC program.<br />
Maybe a task turn it off after a while..<br />
Surely it isn't due to Mango or Modbus!</p>
]]></description><link>https://forum.mango-os.com/post/5149</link><guid isPermaLink="true">https://forum.mango-os.com/post/5149</guid><dc:creator><![CDATA[zumiani]]></dc:creator><pubDate>Thu, 23 Dec 2010 08:29:14 GMT</pubDate></item><item><title><![CDATA[Reply to Wago 750-841 Modbus Fieldbus Coupler on Wed, 22 Dec 2010 22:02:50 GMT]]></title><description><![CDATA[<p dir="auto"><a class="plugin-mentions-user plugin-mentions-a" href="/user/zumiani" aria-label="Profile: zumiani">@<bdi>zumiani</bdi></a> said:</p>
<blockquote>
<p dir="auto">Modbus TCP device usually answer to all Modbus address.<br />
In fact, as you said, one IP address correspond to one Modbus device and so Modbus address is not so important.</p>
</blockquote>
<p dir="auto">Got it thanks should have read this first.  Still have a problem when setting a bit to the Wago.  It sets fine but about 2 seconds or less it shuts off.  I do not understand why?  Is there something I am missing?</p>
<p dir="auto">dk</p>
]]></description><link>https://forum.mango-os.com/post/5148</link><guid isPermaLink="true">https://forum.mango-os.com/post/5148</guid><dc:creator><![CDATA[dkudos]]></dc:creator><pubDate>Wed, 22 Dec 2010 22:02:50 GMT</pubDate></item><item><title><![CDATA[Reply to Wago 750-841 Modbus Fieldbus Coupler on Wed, 22 Dec 2010 14:00:14 GMT]]></title><description><![CDATA[<p dir="auto">That is great and thank you for the response.  What is bothering me is what function code mabey F7 is being used to scan nodes.  I should see one node right?  Also I can set a point with Mango and turn it on and off now but when I set a Modbus point it turns off after about 2 seconds.  Mango says it is still set but the point on the wago has turned off.  Why would it turn off if I have not told it to turn off?  I have written a java program using Jmod library to do my own scheduling and have no problems with the Wago what do I not understand about Mango that would cause this?  I really like this project and would like to help make it more useful as soon as I understand all of it.</p>
<p dir="auto">Any help would be great thanks,</p>
<p dir="auto">dk</p>
]]></description><link>https://forum.mango-os.com/post/5146</link><guid isPermaLink="true">https://forum.mango-os.com/post/5146</guid><dc:creator><![CDATA[dkudos]]></dc:creator><pubDate>Wed, 22 Dec 2010 14:00:14 GMT</pubDate></item><item><title><![CDATA[Reply to Wago 750-841 Modbus Fieldbus Coupler on Wed, 22 Dec 2010 08:37:59 GMT]]></title><description><![CDATA[<p dir="auto">Modbus TCP device usually answer to all Modbus address.<br />
In fact, as you said, one IP address correspond to one Modbus device and so Modbus address is not so important.</p>
]]></description><link>https://forum.mango-os.com/post/5143</link><guid isPermaLink="true">https://forum.mango-os.com/post/5143</guid><dc:creator><![CDATA[zumiani]]></dc:creator><pubDate>Wed, 22 Dec 2010 08:37:59 GMT</pubDate></item><item><title><![CDATA[Reply to Wago 750-841 Modbus Fieldbus Coupler on Tue, 21 Dec 2010 21:47:17 GMT]]></title><description><![CDATA[<p dir="auto">Ok needed to set the offset to detect proper modbus port.  But when I set a binary value it does not stay set on the wago but is still in mango.  What do you think about that?</p>
<p dir="auto">dk</p>
]]></description><link>https://forum.mango-os.com/post/5142</link><guid isPermaLink="true">https://forum.mango-os.com/post/5142</guid><dc:creator><![CDATA[dkudos]]></dc:creator><pubDate>Tue, 21 Dec 2010 21:47:17 GMT</pubDate></item></channel></rss>